Insulation Recommendations for Post & Beam Barn Conversion
barnrestoration
| 08 Dec 2018 04:29 PM |
Hi all,
Long time reader here but first post. We live in a late 1800s bank barn on a farm in Southeastern Pennsylvania. Our current living area is on part of the second level of the barn and takes up just over 1 out of 4 - 14x40 foot bays starting on the 2nd floor (ground level on bank side of barn) and we have a second story bedroom above. Below the space is fully enclosed area (on three sides by 18" thick stone walls cut into the bank, and insulated walls with doors on the ground level lower side). The lower space is not conditioned and has a 4" concrete slab and is used as a shop. The living space has 9" floor joists w/cellulose insulation on the floor above the shop, and Icynene OCSF sprayed on felt paper and Tyvek attached to the backside of the board and batten siding, in 2x4 framing, with the interior covered in 2 layers of firecode drywall. The space is tight and is very inexpensive to cool but with high ceilings and open ductwork suspended from the 13 foot ceiling between the first and second floor, the floor itself can feel cold in the winter on the first level. We have two ceiling fans that help distribute the heat and use propane to heat at a cost of ~$1200/year. We've loved this space but after 15 years are looking for a little more space to have available especially for visitors.
We're looking at options to create more living space in 2 of the 3 remaining bays on the ground level of the bank side of the barn (this is the 2nd level above lower slabbed shop area) leaving the 4th bay as a work area. The space where we're looking to expand is approximately 1,000 square feet in footprint, and will have a 2nd level over parts of that space. The gable peaks at about 28 feet from the floor but we will be creating a flat ceiling at ~23'. We've pulled the floor to expose the 3x9" joists (TNG board ceiling makes up the current ceiling between shop area and living space attached to bottomside of floor joists) and cleaned out the joist bays to prepare for insulating the floor. Now that spray foam has fire retardant I wan cosnidering that for the floor, and originally I was thinking of spray foam over Tyvek again for the walls but in some recent reading I'm wondering if there are better options for effieciency, cost and eco-freindliness.
There will be minimal windows in the space (several on south side, and some doors at ground level on north side) and we will use a mini split and ideally a masonry heater, but more likely a less expensive wood stove for cozy warmth, possibly with radiant pex run through the flooring tied into the wood stove via heat exchanger to prevent repeating the cold floor issues we have in our existing space.
So in total we're looking at insulating the following:
Floor: ~ 1,000 sq ft
South wall: ~400 sq. ft S. pitched roof: ~350 sq. ft Flat ceiling (below gable): ~800 sq. ft. N wall: ~400 sq. ft N. pitched roof: ~350 sq. ft W. Wall between workspace: 880 Sq. ft.
At this point I have no constraints on framing or wall thickness and just want to create an effiicent, insulated and well sealed envelope at a reasonable cost. The posts are 8x8 so I have plenty of space for whatever framing/insulation combo makes sense from cost and efficiency stand points. Also, I want to be sure to mitigate any moisture concerns with post and beam frame and board/batten siding, since this will basically be insulated from the inside out. I can create a quasi rain screen on back side of the siding but will not be able to get behind the girts the siding is attached too. Maybe I should create an air space between siding and inside framing/covering that insulation is touching?
I'm capable and equiped to handle all of this work myself, but I am on a tight budget and looking for expert opinions on cost effective insulation recommendations and willing for pay for a professional to spray if cost effective. We want a healthy and eco-friendly space!
Thoughts?
barnrestoration
| 08 Dec 2018 04:41 PM |
pic of space - this is the south wall of area we're considering expanding into and insulating. |
Dilettante
| 10 Dec 2018 08:07 PM |
Depends on what you mean by "efficiency". Unfortunately, foam is, generally, about the most efficient insulator on a straight-up "per inch" basis. There's nothing stopping you from building non-load-bearing interior walls and filling the cavity with whatever insulation you want. Rockwool Fiberglass (batts or blown-in) Cellulose Spray foam Whatever. That's probably the ideal method, as it allows you to run wiring chases ahead of time... |
| 11 Dec 2018 09:07 PM |
In barns the siding is usually the sheathing. To keep it all from rotting out there needs to be an air gap between the siding & insulation. Best bang/buck is often installing girts spanning between posts to maintain the air gap, onto which you can mount reclaimed roofing foam boards, which can be cheaper than batts per square foot at a given R value, and easier to make air tight. A layer of housewrap on the interior side of the foam detailed as an air barrier can also help the long-term air tightness prospects. A continuous layer of 3" roofing polyiso (R16-R17) would beat current code minimums for SE PA if it also insulated the posts. Installing 2" foam (any type) onto the girts and a 2x4/R13 framed wall tight to the foam would also beat code min with margin. There are several vendors of used foam in your area. Run these searches every few days and you may find a few more: https://philadelphia.craigslist.org/search/sss?query=rigid+insulation https://lancaster.craigslist.org/search/sss?query=rigid+insulation https://allentown.craigslist.org/search/sss?query=rigid+insulation
barnrestoration
| 12 Dec 2018 03:13 PM |
In barns the siding is usually the sheathing. To keep it all from rotting out there needs to be an air gap between the siding & insulation. In this case the siding is actually vertical 1x12 board and batten and its in good shape so I want to leave these intact and tackle this from the inside. Best bang/buck is often installing girts spanning between posts to maintain the air gap So what is a good air gap to shoot for between the foam board and the inside of the siding? I plan to run the girts from post to post so siding boards could be removed if ever needed without disturbing the insulation. In other words, should I use 1x or 2x, or even 3x material for the girts, and can they be flush against the backside of the siding or should the girts have an space as well? Should the foam board seams be foamed or is tape sufficient? Installing 2" foam (any type) onto the girts and a 2x4/R13 framed wall tight to the foam would also beat code min with margin. Are you suggesting to use regular batts for the 2x4 wall with this approach? How necessary is adding a layer of foam inside of the 8x8 posts? I had envisioned making the framing flush with the inside of the posts and then covering the framing, insulation and house wrap with T&G boards. Adding foam inside of the 8x8 posts will make for a much thicker wall, which is ok I guess but then there would be a larger air gap between the backside of the siding boards and where the foam board insulation starts, maybe 5-6". My gut tells me that that seems like a large air space to have and could lead to moist air getting trapped behind the siding. Maybe I can keep foam boards, girts and framing flush with inside of posts, then cover with house wrap to a super thin layer of foam stapled to posts as a thermal break? Thoughts? Finally, as far as the house wrap goes, I had envisioned tacking it up to the inside of the girts against siding before applying the foam board, but you recommend applying inside the foam board between the insulation and interior wall cladding. Can you explain which is better? My thought was that wrap on backside (between siding and girts), would keep moisture from entering the seams on the back side of the foam board which cannot be sealed, but maybe the moisture is more likley to come from inside the house and that is why you recommend applying wrap inside the foam boards? I'm also considering using foam board as suggested and then a DIY spray foam to seal the seams. What is the recommended air gap between the foam insulation and the interior wall cladding? Thank you! |
newbostonconst
| 12 Dec 2018 03:55 PM |
Nuclear.....yep |
| "Never argue with an idiot. They will only bring you down to their level and beat you with experience." George Carlins |
barnrestoration
| 12 Dec 2018 05:38 PM |
Posted By newbostonconst on 12 Dec 2018 03:55 PM
Nuclear.....yep
LOL. Just looking for sound advice and opinions as this isn't a typical approach to construction. |
| 12 Dec 2018 07:53 PM |
A 1/4" air gap is a sufficient thermal break for tighter siding but the amount of wind-driven bulk water potential getting by well-aged board & batten the 1.5" depth of a 2x4 girt isn't a terrible idea and gives you something firmer to hang the foam board on, but 3/4" is fine. Contact between the girts & siding is not a problem. Moist air simply can't get "trapped" by board & batten siding unless you sprayed the exterior with a heavy coat of sprayed roofing material or something. The bigger the air gap, the better the capillary break, but the benefits diminish after 3/4". In rainy western British Columbia they only demand 10mm (~3/8"), but it's easier to go with twice that using 1x lumber to establish the gap. The posts themselves are a thermal bridge through the insulation layer, which means you'd need somewhat thicker insulation to achieve the average performance needed to hit code minimum. With foil facers on the foam board a temperature rated aluminum tape would be sufficient. If asphalted paper or fiberglass, housewrap tape overlaid with troweled-on duct mastic works. Spray foam doesn't have sufficient adhesion to form a reliable air seal on the seams unless applied fairly thickly. Tape & seal the foam to the posts too, and put a bead of caulk between the end stud and post when installing the studwall. DIY foam kits use high environmental impact blowing agents and should be used only sparingly. Caulking the non-structural framed wall to the foam facers with polyurethane caulk the full perimeter of each stud bay and using rock wool batts is both more fireproof and more environmentally friendly, and surprisingly comparable in thermal performance despite the lower center-cavity R. (The thermal bridging of the studs robs higher R/inch goods of their potential performance.) A 2" layer of foam board is sufficient dew point control for a 2x6 /R23 rock wool wall, which would be 7.5" actual depth, 8" if including wallboard. At 2" rigid polyiso has has a huge amount of margin on a 2x4/R15 wall (6" actual depth with half-inch wallboard), which what you'd probably be building. If the 2x8 posts are full dimension 8.0" nominal that would be plenty of room for 1.5" thick girts. If they're milled 2x8s with 7.25" nominal depth, drop back to 1x4s for the girts. At center cavity with a 2x4/R15 + 2" reclaimed polyiso wall you'd be at R26-ish at center-cavity, and would beat code minimum performance by quite a bit if the framing fraction of the posts & beams are less than 10% of the total face area of the wall, which it probably is. (It might be about 5%.) The location of the housewrap depends on where you set the window depth & flashing. With "outie" windows the glass is roughly co-planar with the siding the housewrap would go between the girts & foam. If the glass is set just slightly proud of the exterior stud edges (which is a bit more common) it's an "innie" mount and the window flashing and housewrap is on the interior facing side of the foam board. When there is no sheathing layer between the foam board and studwall it's probably better to go outie on the windows, and drain into the gap established by the girts.
barnrestoration
| 22 Dec 2018 11:54 PM |
Very helpful information Dana thank you. I picked up 30 sheets of 1.5" XPS and another 30 sheets of 1.5" paper backed polyiso insulation today for next to nothing to get started. Based on your advice so far I'm thinking I can use 2 layers of rigid foam for the walls with no additional insulation and perform reasonably well in SE PA. Correct? Would you recommend a layer of XPS attached directly to the girts, then a layer of polyiso inside of that or vice versa? Should each layer be sealed at the seams or only the innermost layer's joints? Vapor barrier required or no? Interior cladding will be either drywall or tng 1x.
For the ceiling/roof, part sloped and part flat, I'm thinking of a similar approach but then adding batts to acheive required r value. It sounds like the air sealing at the roof level will be most important, especially since the existing roofing is metal over purlins with no tar paper or ice & water shield and condensation inside the metal roofing could be likely if any air leaks through. So what would be the best approach at the ceiling/roof given the foam board I now have?
Thanks!
| 24 Dec 2018 06:13 PM |
Posted By barnrestoration on 22 Dec 2018 11:54 PM
Thanks!
A nearly continuous 3" of foam (any type) will pretty much meet IRC code-minimum in your stackup.
If alternating layers of polystyrene and polyisocyanurate, the polystyrene goes on the cold in winter side of the assembly. As the average temperature through the layer drops, the performance of polystyrene increases monotonically. Most paper faced roofing polyiso increases in performance until the mean temp through the layer hits the high 40s or low 50s F, the falls. With 1.5"/ R6.3-R7.5 polystyrene on the exterior, the R8.5-ish polyiso will always be warm enough to meet or exceed it's rated R value, but would have to be derated a bit if on the exterior.
Per the FTC the labeled nominal R-value is required to be it's performance at a 75F mean temperature, at a 50F temperature difference. (50F on the cold side, 100F on the hot side.) That tends to exaggerate the cold weather performance of most polyiso. The only vendor who has beaten that is Dow's Thermax wall sheathing polyiso, which like polystrene increases monotonically with falling temperature (at temperatures that matter for building insulation purposes, at lease.)
Tape the seams of both layers. There is no such thing as "too tight".
At 1.5" XPS is a Class II vapor retarder, all paper faced polyiso sold in the US is also a Class II vapor retarder. With an air gap between the board & batten and the foam there is no way that vapor diffusion through the foam would cause a moisture problem for the sheathing- even air leaks would not be a moisture problem in this stackup. In short, don't install a vapor barrier- it's not necessary, and you already have one (the foam), from a practical standpoint. Make it air tight, but don't worry about water vapor diffusion here. |
barnrestoration
| 09 Jul 2019 05:34 PM |
Dana,
Thank you again for your thoughts on this. What would you advise for insulation on the underside of the roof/ceiling in this scenario?
Basically we have a 3rd floor that has a knee wall extending up from the 2nd floor wall below that will be likely insulated as you describe above with 2 layers of 1.5" rigid foam. From the knee wall, the ceiling will slope up the bottom of the rafters to 10' high, then be attached to the bottom of rafter ties that hang 6-7 feet below the ridge. The roof is galvalume corrugated metal roofing panels, screwed directly to purlins with no roof decking.
My thought is to add a spacer along the rafter edges, attached directly below the purlins to create an air gap from the vented soffit to the vented ridge. Then attach rigid foam cut to fill the rafter bays, taped and sealed. Then to the underside of this, attach additional continuous layers of rigid foam board to reach R30+ and finally clad the whole underside in either 1x t&g pine or sheetrock. Thoughts?
Thanks!
229 |
229 |