Posted By billnaegeli on 02/03/2008 8:32 PM
according to the 2003 IRC, ICFs can only go one story above grade w/o additional engineering,
From the 2006 IRC:
R404.4.1 Applicability limits. The provisions of this section
shall apply to the construction of insulating concrete
form foundation walls for buildings not more than 60 feet
(18 288 mm) in plan dimensions, and floors not more than
32 feet (9754 mm) or roofs not more than 40 feet (12 192
mm) in clear span. Buildings shall not exceed two stories in
height above grade with each story not more than 10 feet
(3048 mm) high.
What I have read of the IRC requirements they seem to pretty much copy the Prescriptive Method requirements. I've not done a detailed comparison but I haven't seen any conflicts between them. I don't recall the specifics now but I think Polysteel design requirements are stricter than the Prescriptive Method. I used Polysteel manual for guidance and reference even though I'm using BuildBlock. BuildBlock has adopted the Prescriptive Method. My civil engineer cousin gave me a thumbs up on the footer design, and the BI didn't have any quibbles (except asking about flammability of the XPS covering the footers) when he gave me the Building Permit.
I should have quoted this section:
R611.2 Applicability limits. The provisions of this section
shall apply to the construction of insulating concrete form
walls for buildings not greater than 60 feet (18 288 mm) in plan
dimensions, and floors not greater than 32 feet (9754 mm) or
roofs not greater than 40 feet (12 192 mm) in clear span. Buildings
shall not exceed two stories in height above-grade. ICF
walls shall comply with the requirements in Table R611.2.
Walls constructed in accordance with the provisions of this section
shall be limited to buildings subjected to a maximum
design wind speed of 150 miles per hour (67 m/s), and Seismic
Design Categories A, B, C, D0, D1 and D2. The provisions of
this section shall not apply to the construction of ICF walls for
buildings or portions of buildings considered irregular as
defined in Section R301.2.2.2.2.