Posted By ECO-HAMMER on 12/04/2009 11:25 PM
I believe you have to put a conector on the end of the conduit and strip the outer jacket from the romex where it goes thru the conduit.
Cheers,
Joey
Nope on both counts. The NEC allows you to run Romex thru conduit up to 5', I think, maybe 8'. I'd have to check but the length limit is reasonably generous. No clamp is required but the romex will have to be fastened within 6" of the end of the conduit. You're not permitted to strip the outer sheath off the romex, nor can you use wired stripped from romex cable as regular conduit wire. The reason is identification. The individual wires in a romex cable do not carry size, type, etc., info on them. It's all on the outer sheath. All wires must have visible identifying info on them, which individual strands made for conduit use have.