ICF is simply reinforced concrete and is engineered nearly identical to plain jane panel formed reinforced concrete. It's sorta surprising that engineers don't recognize that. I had a similar build with basement and first floor walls, although we went with conventional framing for the second floor because it soared pretty high. I am in a high seismic zone. Initial indications were 8" or 10" walls at the base, transitioning to 6" on the uppers. Engineering, and adding in some "bumpouts" enabled us to go down to 6" thick concrete for all walls. I also used Insuldeck for the basement/first floor interface which I believe enabled the downsizing as well. Footings were 60" wide by 10" deep with #4 laterals at 10" o.c.and #4 lineals. Footing to wall transitions were #5 "ells" at 8" o.c. Walls are vertical and horizontal #5 bar at 16" spacing. |