A crawlspace can have no more than 4 feet of backfill and be no taller than 5 feet. Never backfill before the floor is installed on top.
Lateral support at top is the floor (TJI's on a sill plate or what have you).
Lateral support at bottom is achieved through dowels. The strip footing provides this resistance. Not the slab.. That's why crawlspaces do not have slabs but gravel..
So... R404.1 tells you that you can use PCA-100 instead. You can use R404.1 but it is obscure and needs a bit of work...
The 2012 edition of PCA-100 says that:
Concrete walls enclosing crawlspaces shall be constructed in accordance with Figure 3.2 and shall be laterally supported at the top and bottom of the wall in accordance with Chapter 6.
in chapter 6 - section 6.2 (still in PCA-100) says:
For buildings assigned to Seismic Design Category A, B, or C
and located where the wind velocity pressure in accordance
with Table 5.1A is less than or equal to 40 psf (1.95 kN/m2),
No. 4 Grade 40 (280 MPa) vertical dowels at a maximum
spacing of 32 inches (813 mm) on center, or No. 5 vertical
dowels at a maximum spacing of 48 inches (1219 mm) on
center shall be installed across the construction joint between
the foundation wall and the footing
PCA100 does not say this but it is a good idea to bend these straight vertical dowels into L's and alternate the feet left to right. The dowels have to reach into the footing by 8" and into the wall by another 8 inches min. So the entire bar would be a minimum of 2 feet (8+8+8) but id go to 36.
The length of the L is typically 8 inches.
There are some more requirements/exceptions but they most likely do not apply to you.
Next time - call the manufacturer