Am I being dumb ? - ICF floors, UFH and thermal bridging
Last Post 14 Nov 2022 01:25 PM by newbostonconst. 3 Replies.
Author Messages
cliftonarmsUser is Offline
New Member
New Member
Send Private Message
Posts:3

--
03 Nov 2022 08:30 PM
Almost all ICF suppliers have a concrete flooring beam product that attaches to the wall. All normally show UFH embedded in these floors.

Am I being a bit dumb in suggesting that this is a huge thermal bridge / dump of 30'C floor heat into the 10-15'C concrete wall core. And hence a big waste of floor heating energy into the wall core.

Am I missing something?

I'm looking to design in wet UFH floors for basement, ground and first floor, but dont see how ICF decks can be used on the ground and first floors without thermal bridging to the walls, ( basement will be insulated slab )

Someone please tell me I am being stupid !!!

Attachment: Capture.GIF

smartwallUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1197
Avatar

--
04 Nov 2022 02:24 PM
You are not being dumb, you have found the problem with the use of eps floor system. The only way to lessen the impact is to beef up the exterior wall insulation. I see by your rendering that you may be using Quad Lock. They allow you to increase the thickness of the exterior insulation. This is one reason I don't use this product in my area. Chasing the toasty floor has it's cost.


newbostonconstUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:736

--
14 Nov 2022 01:25 PM
...


"Never argue with an idiot. They will only bring you down to their level and beat you with experience." George Carlins
newbostonconstUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:736

--
14 Nov 2022 01:25 PM
cliftonarms I agree with you.....do a wood truss floor with an inch and a half of concrete on top if you want heated floors.


"Never argue with an idiot. They will only bring you down to their level and beat you with experience." George Carlins


---