bru15
New Member
Posts:3
|
25 May 2015 01:15 AM |
|
Building, utilizing SIPs roof and walls. Climate Zone 6 in Idaho.
1) I know we tape the inside seams, but should the exterior seams be taped?
2) For the bottom sill plate..What is the opinion on using (in order) rubber gasket, treated plywood, poly-sealant, then a normal 2x6 as the sill buildup? The Panel would sit on the treated plywood, not the slab.
3) Is a 2x4 on it's 3.5" side adequate for the vented roof or should it be stood on its 1.5" side? Would a 2x3 be enough? |
|
|
|
|
|
Lbear
Veteran Member
Posts:2740
|
25 May 2015 02:36 AM |
|
Posted By bru15 on 25 May 2015 01:15 AM
Building, utilizing SIPs roof and walls. Climate Zone 6 in Idaho.
1) I know we tape the inside seams, but should the exterior seams be taped?
2) For the bottom sill plate..What is the opinion on using (in order) rubber gasket, treated plywood, poly-sealant, then a normal 2x6 as the sill buildup? The Panel would sit on the treated plywood, not the slab.
3) Is a 2x4 on it's 3.5" side adequate for the vented roof or should it be stood on its 1.5" side? Would a 2x3 be enough?
Taping the inside seams is a must. The outside is not as important but if you are a belt a suspender person, then I would invest the time and few bucks to tape the outside. SIGA WigLuv is excellent for exterior SIP seams and Rissan is great for interior seams. A 2x4 laid flat (1.5" in height) is more than adequate for a venting roof channel. Laying it on the 3.5" side is not necessary and would make for a difficult attachment. Just lay it flat and the 1.5" of air space will be more than enough to dry. I would just use a 2x4 since they are plentiful and inexpensive. Are you putting 1/2" or 5/8" OSB over the 2x4 furring strips? |
|
|
|
|
gosolar
Basic Member
Posts:156
|
25 May 2015 07:02 AM |
|
Why treated plywood rather than PT 2x6 etc? What about alum termite shield or poly guard? As to the roof there are many opinions on weather or not that air space is needed rather than a good vapor barrier. I decided against the air space on my build and using a barrier. Seams on the interior are a must, but I wonder if using a good caulking on corner joints like were wall & roof meet would stay in place better than bending tape into the joint. ON the outside the important thing is to get the foam in the joints by drilling holes every 12-18 " and injecting same. Then again a vapor barrier under siding like drainable wrap watch their video on the water gap |
|
|
|
|
bru15
New Member
Posts:3
|
25 May 2015 12:03 PM |
|
Thanks all. Probably will tape outside, it seemed a good idea, but rarely see it mentioned. I have seen a few houses (non SIPs) that built a cold roof and put the 2x4s on the 1.5" end.... supposedly for more air flow. I thought on the flat would be adequate (and easier). What is being used for the screening on the eave portion of this vent (to keep bugs out)? Thinking 5/8" sheathing over, since there are not joists in the SIPs every 2 feet. SIPs roof is 12 1/2". Still out on that one..... Treated Plywood saves a bunch. I have 365 feet of sill plate. My SIPs wall are 6 1/2" thick....I would have to rip 2x8s for the first layer on the sill. The first layer is just to keep the SIPs (OSB) off of the concrete. A EPDM gasket under it. Poly sealant on top, then the 2x6 that the SIPs attaches too. The SIPs manufacturer thought the 3/4" plywood would be fine. I am in Zone 6. Temps can drop to -20, up to 85. We get a lot of summer rain, winter can have 5 feet snow on the ground....leading to a lot of ice dams around. Seems like people get leaks in regular roofs then put up a cold roof and they stop. I want to address this from the beginning. No termites.....too cold all year. No real shield, but I will have a flashing covering about 2" of the SIPs extending down, covering 6" of the foam slab insulation (under the soil fill). Borate spraying the SIPs for the lower 2'. My wall to roof are angle cut so SIPs meet SIPs, no wedges to install. Intended to fur out the wall (3/4") over Tyvek (unless something better), then Cedar T&G 1 1/2" siding. Leaving space on the bottom and top for flow. What is used to screen these areas? As far as the slab....It's a mono pour, R-18 insulated sides and under. |
|
|
|
|
gosolar
Basic Member
Posts:156
|
25 May 2015 12:39 PM |
|
You only need 1mm of space for water to run out, and air to flow, 2by's are over kill, but it's your house.
|
|
|
|
|
gosolar
Basic Member
Posts:156
|
25 May 2015 12:51 PM |
|
Posted By bru15 on 25 May 2015 12:03 PM
Treated Plywood saves a bunch. I have 365 feet of sill plate. My SIPs wall are 6 1/2" thick....I would have to rip 2x8s for the first layer on the sill. The first layer is just to keep the SIPs (OSB) off of the concrete. A EPDM gasket under it. Poly sealant on top, then the 2x6 that the SIPs attaches too.
a 4x8 is about $40 so about $7 and change each 8', but you will have more butt joints. A 2x8x16' is $16, it is thicker obviously and you just cut 3/4" off, I think It's easier to cut a 2by than sheet goods into strips |
|
|
|
|
Lbear
Veteran Member
Posts:2740
|
25 May 2015 09:24 PM |
|
Posted By bru15 on 25 May 2015 12:03 PM
Thinking 5/8" sheathing over, since there are not joists in the SIPs every 2 feet. SIPs roof is 12 1/2". Still out on that one..... I am in Zone 6. Temps can drop to -20, up to 85. We get a lot of summer rain, winter can have 5 feet snow on the ground....leading to a lot of ice dams around. Seems like people get leaks in regular roofs then put up a cold roof and they stop. I want to address this from the beginning. Check out 5/8" AdvanTech OSB. It outperforms plywood on many levels. Cold roofs on OSB SIPs is not a bad thing and recommended by the Building Science Corporation and all the top-name building scientists. The cold roof will also act as a "sacrificial layer" to any roof damage. If a roof SIP gets damaged, you are in a world of hurt and expensive fixes. A standard truss roof with OSB sheathing can be replaced and repaired all day long. The same cannot be done with a SIP if it gets water/moisture damage. The 2x4 furring channels will work great in keeping the SIP OSB nice and dry when it gets wet. The 2x4s will also provide a strong and wide area to put down the plywood or OSB and screw it down to. OSB SIPs come in 7/16" thick skins. Typically metal roofs need at least 1/2" or preferably 5/8" thick OSB to provide proper screw retention. Some roof manufacturers will not warranty a roof if it is installed on a 7/16" thick OSB sheathing. It's about the screw pullout in that thickness. If water gets into that area the OSB can swell and the OSB even loses more strength. |
|
|
|
|
gosolar
Basic Member
Posts:156
|
25 May 2015 10:32 PM |
|
Posted By Lbear on 25 May 2015 09:24 PM
Posted By bru15 on 25 May 2015 12:03 PM
Thinking 5/8" sheathing over, since there are not joists in the SIPs every 2 feet. SIPs roof is 12 1/2". Still out on that one..... I am in Zone 6. Temps can drop to -20, up to 85. We get a lot of summer rain, winter can have 5 feet snow on the ground....leading to a lot of ice dams around. Seems like people get leaks in regular roofs then put up a cold roof and they stop. I want to address this from the beginning.
OSB SIPs come in 7/16" thick skins. Typically metal roofs need at least 1/2" or preferably 5/8" thick OSB to provide proper screw retention. Some roof manufacturers will not warranty a roof if it is installed on a 7/16" thick OSB sheathing. It's about the screw pullout in that thickness. If water gets into that area the OSB can swell and the OSB even loses more strength.
I think the pull thru was an issue many years ago when the manufacturers used a different method. can you please name the manufactures that will not warranty the roof? |
|
|
|
|
Lbear
Veteran Member
Posts:2740
|
25 May 2015 11:37 PM |
|
Posted By gosolar on 25 May 2015 10:32 PM
I think the pull thru was an issue many years ago when the manufacturers used a different method.
can you please name the manufactures that will not warranty the roof?
First point is that code minimum in most areas is 1/2" minimum on the roof sheathing. In my area it states that the roof sheathing must be "1/2" minimum roof sheathing" and areas with higher snow loads it states, "5/8" minimum roof sheathing". I would advise one to check with their local code and see what the minimum sheathing thickness is for the roof. Can an inspector tell the difference between 7/16" and 1/2"? Most likely not but the code is what the code states. If it's 5/8" minimum sheathing then they surely will tell the difference between 5/8" and 7/16" OSB. As far as roofing manufacturers go. I would contact whichever roof manufacturer you are using and ask them if 7/16" OSB is sufficient for their attachment. If they are OK with it and will warranty it, then have them put it in writing. Metal roofing companies prefer 5/8" sheathing to attach their screws & clips into but will tolerate 1/2". With 7/16" you will get sketchy answers regarding the warranty. Can you find a metal roof manufacturer that will warranty the roof being installed and attached using 7/16" OSB? If so, get it in writing because all the ones I talked to will not warranty it. The problem is that 7/16" OSB does not have much holding strength in it. The metal roof screws and clips rely on the holding strength to prevent the panels from sliding off in snow events or lifting off in high winds. A good 12" of snow or a 60mph wind will pull a metal panel off of a roof if it is not secured properly. Best read this from the JLC: Metal Roofing and 7/16" OSB |
|
|
|
|
gosolar
Basic Member
Posts:156
|
26 May 2015 07:42 AM |
|
As far as the code goes and sheathing thickness, sips are approved nationwide with 7/16", including S Fl hurricane zones. Besides the argument can be made that the roof is not 7/16" but double that with two layers. I think you're mixing up the facts of sheathing thickness over rafter support spacing and metal attachment. https://www.disastersafety.org/hail/metal-roofs/ states 7/16" Firestone 7/16" Texas Dept of insurance 7/16 Now unless you can show otherwise can we agree sips 7/16 is good to go, to say nothing of thousands of installs out there. |
|
|
|
|
Lbear
Veteran Member
Posts:2740
|
26 May 2015 03:19 PM |
|
GoSolar,
Every building code dept is different and every roof manufacturer has different requirements. Once again, 7/16" OSB is a sub-standard attachment area for a metal roof. There is not much grip in 7/16" OSB to hold down a metal roof that might experience heavy snow loads and high winds.
There is no one-size fits all application here. One will have to call the roof manufacturer that they plan on using and find out if they will OK and warranty their metal roof being attached to 7/16" OSB. If they say, "yes", then you are good to go. If they say, "no", then you will have to find another manufacturer or just install a cold roof with 5/8" sheathing and kill two birds with one stone (venting of SIP and proper sheathing thickness for metal roof attachment).
|
|
|
|
|
bru15
New Member
Posts:3
|
26 May 2015 06:05 PM |
|
Good info. A couple items...
Roof will be asphalt not metal.
3/4" furring on walls...can't find anything to use that is smaller thickness or would consider. |
|
|
|
|
gosolar
Basic Member
Posts:156
|
26 May 2015 10:37 PM |
|
Posted By Lbear on 26 May 2015 03:19 PM
GoSolar,
Every building code dept is different and every roof manufacturer has different requirements. Once again, 7/16" OSB is a sub-standard attachment area for a metal roof. There is not much grip in 7/16" OSB to hold down a metal roof that might experience heavy snow loads and high winds.
There is no one-size fits all application here. One will have to call the roof manufacturer that they plan on using and find out if they will OK and warranty their metal roof being attached to 7/16" OSB. If they say, "yes", then you are good to go. If they say, "no", then you will have to find another manufacturer or just install a cold roof with 5/8" sheathing and kill two birds with one stone (venting of SIP and proper sheathing thickness for metal roof attachment).
Just came across this engineering test report on 7/16" OSB LBear still think it doesn't work? |
|
|
|
|
Lbear
Veteran Member
Posts:2740
|
27 May 2015 03:01 AM |
|
Posted By gosolar on 26 May 2015 10:37 PM
LBear still think it doesn't work?
I think you are missing the point. As I stated before, as long as your local code inspector approves it and the roofing manufacturer approves it, you are good to go. So if the two agencies OK the 7/16" then you are good. Judging from the report you referenced it appears to be a Florida application. There are no snow loads in Florida. That is why the 7/16" is passable for that manufacturer. With that being said, any roofer knows that 7/16" is NOT a good screwing base for metal roofs. Can it be used? Apparently so but it is not ideal. 1/2" roof sheathing is the bare minimum but 5/8" is ideal |
|
|
|
|
cmkavala
Veteran Member
Posts:4324
|
27 May 2015 06:38 AM |
|
Posted By gosolar on 26 May 2015 10:37 PM
Posted By Lbear on 26 May 2015 03:19 PM
GoSolar,
Every building code dept is different and every roof manufacturer has different requirements. Once again, 7/16" OSB is a sub-standard attachment area for a metal roof. There is not much grip in 7/16" OSB to hold down a metal roof that might experience heavy snow loads and high winds.
There is no one-size fits all application here. One will have to call the roof manufacturer that they plan on using and find out if they will OK and warranty their metal roof being attached to 7/16" OSB. If they say, "yes", then you are good to go. If they say, "no", then you will have to find another manufacturer or just install a cold roof with 5/8" sheathing and kill two birds with one stone (venting of SIP and proper sheathing thickness for metal roof attachment).
Just came across this engineering test report on 7/16" OSB
LBear still think it doesn't work?
gosolar, the ultrarib roofing in the test report is not a typical home installation, the exposed fastener roofing is more typical in agricultural or commercial installation |
|
Chris Kavala<br>[email protected]<br>1-877-321-SIPS<br /> |
|
|
cmkavala
Veteran Member
Posts:4324
|
27 May 2015 06:48 AM |
|
Posted By Lbear on 27 May 2015 03:01 AM
Posted By gosolar on 26 May 2015 10:37 PM
LBear still think it doesn't work?
I think you are missing the point. As I stated before, as long as your local code inspector approves it and the roofing manufacturer approves it, you are good to go. So if the two agencies OK the 7/16" then you are good.
Judging from the report you referenced it appears to be a Florida application. There are no snow loads in Florida. That is why the 7/16" is passable for that manufacturer.
With that being said, any roofer knows that 7/16" is NOT a good screwing base for metal roofs. Can it be used? Apparently so but it is not ideal. 1/2" roof sheathing is the bare minimum but 5/8" is ideal
Lbear, there a are no snow loads in Florida , but there are hurricane codes and wind design criteria that affect screw pull out values much more than snow load, |
|
Chris Kavala<br>[email protected]<br>1-877-321-SIPS<br /> |
|
|
cmkavala
Veteran Member
Posts:4324
|
27 May 2015 06:55 AM |
|
Posted By bru15 on 25 May 2015 01:15 AM
Building, utilizing SIPs roof and walls. Climate Zone 6 in Idaho.
1) I know we tape the inside seams, but should the exterior seams be taped?
2) For the bottom sill plate..What is the opinion on using (in order) rubber gasket, treated plywood, poly-sealant, then a normal 2x6 as the sill buildup? The Panel would sit on the treated plywood, not the slab.
3) Is a 2x4 on it's 3.5" side adequate for the vented roof or should it be stood on its 1.5" side? Would a 2x3 be enough?
bru15, sorry to see your thread get hijacked , but as you will find out on this forum if you hang around it long enough is: the opinions by some are by those that have no real life experience in construction, but have strong opinions based on their research, sometimes based on faulty information, just like a computer ----- garbage in / garbage out |
|
Chris Kavala<br>[email protected]<br>1-877-321-SIPS<br /> |
|
|
acobb
New Member
Posts:30
|
27 May 2015 10:36 AM |
|
Speaking of garbage in-garbage out: The recommendation to put a vapor barrier on the outside (cold side) of a SIP structure in climate zone 6 is ludicrous. Don't do it! As a SIP professional with 25+ years of experience I can assure you that is bad advice. The consulting work I do nationwide often involves forensic investigation of SIP projects gone bad. It is not uncommon to find an exterior VB installed in cold climates which leads to trapped moisture. You are better served by installing back ventilation in both walls and roofs then wasting money on taping your exterior joints. I'd be happy to walk you through the process and other details if you contact me via private message. good luck Al Cobb |
|
|
|
|
gosolar
Basic Member
Posts:156
|
27 May 2015 11:02 AM |
|
www.premiersips.com disagrees, they recommend for example http://www.cosella-dorken.com/bvf-ca-en/products/roof/underlayments_metal/products/trela.php Vapor permeable underlayment with structured separation and drainage
layer for ventilated and non-ventilated pitched roofs and facades with
metal cladding. |
|
|
|
|
acobb
New Member
Posts:30
|
27 May 2015 05:15 PM |
|
Gosolar, Please explain how they disagree. If, in fact, they recommend the underlayment suggested, it is in complete agreement with my recommendation. The Delta underlayment is not a vapor barrier and, it does aid in back-ventilation. Look at the perm rating and you will see that it, much like the Benjemin Obdyke material you suggested earlier are not vapor barriers. I stand by my recommendation as one that is endorsed by Premier, BSC, SIPA, the IRC, and basic building science 101. Regards, Al Cobb |
|
|
|
|
Lbear
Veteran Member
Posts:2740
|
27 May 2015 05:25 PM |
|
I believe GoSolar is confusing vapor permeable with vapor impermeable membranes and is viewing them as the same, vapor barrier.
Posted By acobb on 27 May 2015 10:36 AM
Speaking of garbage in-garbage out: The recommendation to put a vapor
barrier on the outside (cold side) of a SIP structure in climate zone 6
is ludicrous. Don't do it! As a SIP professional with 25+ years of
experience I can assure you that is bad advice. The consulting work I do
nationwide often involves forensic investigation of SIP projects gone
bad. It is not uncommon to find an exterior VB installed in cold
climates which leads to trapped moisture. good luck Al Cobb
I agree that vapor impermeable membranes should not be used on top of OSB roof SIPs. That is a recipe for eventual disaster. Lot of confusing info out there but I have concluded that it is not the best practice. A vapor permeable membrane should be used and a venting channel above the SIP should be utilized. Any trapped moisture can pass through the vapor permeable membrane and the drying channel will allow for proper airflow to dry it out. |
|
|
|
|
gosolar
Basic Member
Posts:156
|
27 May 2015 06:00 PM |
|
not confused at all, I agree on this rare occasion with you about the membrane just n ot the air space with old fashioned belt & suspenders approuh on batten systems |
|
|
|
|
vb
New Member
Posts:88
|
29 May 2015 10:54 AM |
|
Read Structural Insulated Panels (SIPs) by Joe Lstiburek. It is highly informative and is a must read for anyone building with OSB SIPS. Having said that, I used 2x4's for spacing on my own cold roof after much deliberation. It only took a couple extra days the cost was minimal and I sleep much better with the added protection and "sacrificial layer". I furred out my Hardie siding with 1/4" strips and feel better about that as well. My house is only 5 years old now but so far no issues. By the way, I only taped the inside seams not the outside and I taped them all, even though my detail only required taping the roof seams. |
|
|
|
|
Lbear
Veteran Member
Posts:2740
|
29 May 2015 03:43 PM |
|
Posted By vb on 29 May 2015 10:54 AM
Read Structural Insulated Panels (SIPs) by Joe Lstiburek. It is highly informative and is a must read for anyone building with OSB SIPS. Having said that, I used 2x4's for spacing on my own cold roof after much deliberation. It only took a couple extra days the cost was minimal and I sleep much better with the added protection and "sacrificial layer". I furred out my Hardie siding with 1/4" strips and feel better about that as well. Joe Lsitburek also wrote the Building Science Corporation study and article on SIPs. Physics are a law of nature and they cannot be changed. Moisture will eventually get its way into wood substrates like SIPs and one cannot prevent that from happening. All one can do is allow a proper and expedient drying path and capability for that moisture and let the SIP OSB skin dry to prevent damage, rot and eventually failure. |
|
|
|
|