Yes, that would be my recommendation. No, larger tube is more for achieving larger flow rates with less head and less required circulator capacity when you need to move a lot of heat. 1/2" PEX should be more than adequate for your project. Your HR emitter supply temperature will solely be a function of how well your building and your HR emitter perform. Your maximum required HR emitter surface temperature is already locked down and is a direct consequence of how well your building performs given your ACCA Manual J8 heat loss analysis. The only question now is how efficient your HR emitter will be in getting the heat from the PEX to the surface of your floor.
Accomplishing HR via a thin gypcrete slab is usually way cheaper than Warmboard or any other above-floor plate system. Of course, material and labor costs can vary greatly based on locale. I would estimate that Warmboard and a thin gypcrete slab perform about equally well. I don’t have any first-hand experience with Dan’s sandwich system performance, but several folks have reported on this forum that they were happy with it.
We likely do about 90% concrete slab, 5% gypcrete slab and 5% Warmboard. One can usually have a concrete slab HR heating system for less cost than any other heating system option. While HR heating is unquestionably the most comfortable heating system approach bar none (heat at right location, simple, quiet, no drafts), we nevertheless tend to steer folks to mini splits whenever a HR concrete slab isn't an option. However, that's just our mindset/recommendation given that mini splits will significantly out perform any HR heating system that doesn't use a heat pump based heat source. Heat pump based heat sources can get very expensive and can have expensive maintenance issues too. So the lower acquisition cost and lower operational cost of mini splits tend to win that ROI decision for us. |
loghomebuilder
| 11 Nov 2017 05:49 PM |
Posted By sailawayrb on 10 Nov 2017 09:48 PM
hmmm maybe I should look into that again...? Does that add 10 psf to dead load for the floor? |
icfbound
| 12 Nov 2017 12:16 AM |
Figure about 15 psf of additional floor dead load for a 1 1/2” thick gypsum slab. |
CONservative: The first three letters are all you need to know to fully understand this Republican. <br /> <br /> Racist: A person who believes their race is superior to another race. <br /> <br /> Religion: The deception of suckers who fear nonexistence to believe in a nonexistent supreme being and to adhere to false doctrine to control and exploit them. <br /> <br /> Republican: A greedy, racist, sexist person who skillfully uses deception, hate, fear and religion to control and exploit suckers to gain personal wealth and power to benefit themselves while using government to limit the freedoms, safety and pursuit of happiness of others. <br /> <br /> Sexist: A person who assaults, discriminates, intimidates or stereotypes the opposite sex. <br /> <br /> Sucker: A weak minded person who has been brain washed and who usually lacks education and critical thinking skills allowing them to be easily deceived. <a href="https://www.youtube.com/watch?v=vGAqYNFQdZ4">Watch...Don't Be a Sucker!</a> <br /> <br /> Trumpian: A narcissistic and skilled con artist Republican who is highly attractive to suckers and uses Fascist and Nazi tactics and commits traitorous acts to undermine democracy to gain personal wealth and power. |
BuildNewb
| 12 Nov 2017 05:11 AM |
Roth Panels are cheap. A bit over $3 sqf. more responsive than a slab. |
icfbound
| 12 Nov 2017 05:03 PM |
You don’t hear tube expansion noise in gypsum job and it heats good. Any dry system has more noise than gypsum job and doesn't heat as good. Warmboard is best dry system for new construction where it is the subfloor too. It holds tube tight for better heat transfer and less noise than other dry systems. It responds faster too. Roth is good for over concrete but hard to install wood over it. It doesn’t heat as good as Warmboard either. Look at Raupanel too if you don’t care about higher water temps and noise. Sometimes you get what you pay for. Sometimes you don't. |
loghomebuilder
| 17 Nov 2017 04:29 PM |
What about the efficiency drop of staple up with aluminum plates? Are we talking 5% drop? Or like 25%? |
sailawayrb
| 17 Nov 2017 05:17 PM |
According to Siegenthaler, the heat transfer coefficient of a concrete slab HR emitter is 0.882 and the heat transfer coefficient of a below-floor HR emitter is 0.36. That's a difference factor of nearly 2.5. These values are for a 12" PEX tube spacing and a floor finish R-value of 0. As you increase the floor finish R-value, the heat transfer coefficient decreases significantly. This is why we like concrete slab HR emitters and recommend not covering them with wood or carpet... |
loghomebuilder
| 17 Nov 2017 09:07 PM |
Yes I know, but I'm trying to compare a staple up system v. A floor sandwich system. House is half built and I can't replace the first floor with slab on grade |
sailawayrb
| 17 Nov 2017 10:10 PM |
According to Siegenthaler, the heat transfer coefficient of an above-floor HR emitter is 0.55. That's a difference factor of 1.53. I suspect, but I don't have actual data, that Warmboard (and perhaps even Dan's sandwich system) performs nearly as good as a thin-slab HR emitter which, according to Sigenthaler, has a heat transfer coefficient of 0.767 for a difference factor of 2.1. |
loghomebuilder
| 19 Nov 2017 01:33 AM |
OK, I think I understand now. Thanks. |
sailawayrb
| 19 Nov 2017 03:17 AM |
Good deal and happy to help. |