I find it odd that your 5 ton is operating so much better ?
Do you know the reason
The system I was refering to in the begining was a 5 ton DX so all net BTUH measurements where on the air side .
geo fan, I'm not sure I understand your question of what is the reason my 5 ton GSHP is operating so much better. So much better than what?
If the comparison is to a 5 ton DX, I unfortunately don't have any knowledge on DX systems.
I've been very pleased with the performance of the WaterFurnace Envision units I have. While my measured COP and EER performance numbers don't match publish specs, they're either close (close enough to rationalize against laboratory conditions WF probably used), or, I can figure out where my measurement error is.
I just don't have any difficulty pumping out of the earth about 11 KBTU/hr with my 3 ton unit, or 35 KBTU/hr with my 5 ton unit, both in 1st stage only. That's about 46 KBTU/hr available to be processed by the evaporator coils / air handlers and pushed into the structure. Which even in this high 20°F temp outside conditions we have at the moment (cold for Dallas climate), in a non-set back scenario, run time is right around 10 minutes to satisfy the tstat setting (68°).
Best regards,
Bill