20 Feb 2009 06:12 PM
4 Deg*F is a design day for Mt Pleasant, MI - nearest city I could find. Lansing comes in at 1 Deg so selection of 2 Deg for a temp below which to design for aux strip is solid.

Geofan - thanks for the note on thermostats finishing a call with aux vs auto downstaging.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
wirechiefUser is Offline
New Member
New Member
Send Private Message
Posts:72

--
20 Feb 2009 08:39 PM
Posted By engineer on 02/20/2009 6:12 PM
4 Deg*F is a design day for Mt Pleasant, MI - nearest city I could find. Lansing comes in at 1 Deg so selection of 2 Deg for a temp below which to design for aux strip is solid.

Geofan - thanks for the note on thermostats finishing a call with aux vs auto downstaging.

Interesting, the geo designer gives values for 2 deg and 7 deg and 2 deg was where the Space load first goes greater than the
Geo Btu/h so 4 deg is probabably the design day they used, good information.  thanks Geofan.
1500 sq ft home with 5 ton Geocomfort heat pump<br>desuperheater,3200ft of horz loop. Howard city,MI.
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
20 Feb 2009 10:13 PM
There is no hard and fast rule stating that 'design day' temps must govern temperature for designed switchover to aux heat. It's a starting point, no more. Unit capacities being only available in substantially separated nominal capacities (2.5, 3, 3.5, 4,5,6 tons) means that capacity roundoff, ductwork, loop constraints, and total cost of ownership considerations may suggest a unit capacity specification such that aux heat comes on a bit above 'design day' temps.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
irnivekUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:229

--
08 Mar 2009 08:11 PM
Anyone using warmflo as aux. heat? Jumps up in I think 500w increments as needed...