neotobeo
 New Member
 Posts:24
 |
| 28 Jun 2010 09:58 PM |
|
Earthlinked is being much more responsive this year -> I received word today that they are preparing an Air Source Desuperheater to be placed between our 5 ton unit and loop field. I am glad to be making progress and having a conditioned space in the near future. Thank you all for your comments - I will keep you updated with our progress. As one would imagine, I spent a great deal of time trying to understand our issue (this forum included) - I came across an interesting study/white paper from the Dept of Energy (Dec 2001) on Hybrid Geothermal Systems (DOE/EE-0258) - discusses challenging geology and other limitations that obligate the use of an auxiliary heat exchanger (like in our case). |
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 28 Jun 2010 11:32 PM |
|
Not the first we've heard of this. Sounds like a reasonable plan. A system unable to employ larger/deeper loop systems can still benefit from an air cooled coil. Hope it works for you, keep us posted. Joe |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 29 Jun 2010 12:17 AM |
|
I should say, now that max length is installed, you have little choice. I did not like the plan without first increasing loop size. jr- perhaps you know something about earthlinked that their designers do not. they say 150'/ton max, not me. you should offer them your wisdom. meanwhile us real world installers will follow manufacturers' installation instructions. it is a code/warranty thing....you wouldn't understand. joe |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
neotobeo
 New Member
 Posts:24
 |
| 28 Jul 2010 06:07 PM |
|
As promised -> follow up on our 5 Ton Earthlinked System, now with Earthlinked supplied air source desuperheater in-line (vapor) - works well! The liquid line returning from the loop field is warm at best, not scalding as it was up to the minute the desuperheater was put in service. I will provide follow up after it has been running for a few weeks in the heat (around 105 where the unit is sitting and ambient is at 100 right now - house is cool).
Thanks to Earthlinked for responding to this customer's concern. |
Attachment: IMG956807.jpg
|
|
|
|
jonr
 Senior Member
 Posts:5341
 |
| 28 Jul 2010 06:18 PM |
|
> they say 150'/ton max, not me - you wouldn't understand No Joe, you claimed a reason for this, and that's where you were not understanding. But hey, never miss an opportunity for a snide and incorrect remark. |
|
|
|
|
JackH
 New Member
 Posts:37
 |
| 28 Jul 2010 06:54 PM |
|
I am glad things are working better. But i was positive Earthlinked would solve the problem. And try and keep that thing in the shade.. LOL |
|
| |
|
|