Joe,
|
joe.ami
Posted:17 Nov 2010 10:30 PM | Subject: RE: Horizontal loops on small lot
67k????what is the heat load on your house? j |
I appreciate your interest and concern.
The report has this on the front:
Rhvac - Residential & Light Commercial HVAC Loads
Rhvac is an ACCA approved Manual J and Manual D computer program.
Calculations are performed per ACCA Manual J 8th Edition, Version 2, and ACCA Manual D.
Total Heating Required Including Ventilation Air: 45,293
Total Sensible Gain: 29,885
Total Latent Gain: 2,051
Total Cooling Required Including Ventilation Air: 31,936
BTW, google gave me some information to estimate load manually,
and I came in higher than this report....but, I got the square footage right.
He is conditioning only 1/2 the house.
My spreadsheet is summarized:
ft^2 m^2>
|
Heat Load |
2,043.5 |
189.8 |
76,952.5 |
|
BTU Cooling Needed |
|
|
153,905.0 |
|
Tonnage Needed |
|
|
6.4 |
The whole spreadsheet is here: http://www.pachai.net/images/HVAC.xls