flushing a new loop
Last Post 17 Nov 2011 04:06 PM by geodean. 26 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Page 2 of 2 << < 12
Author Messages
geo pupUser is Offline
New Member
New Member
Send Private Message
Posts:14

--
17 Nov 2011 12:59 PM
4 trenches straight out ,300 foot long , 2 circuits in each trench , total of 8 circuits . 4800 ft of 3/4 piping , 214 ft of 1 1/4 header supply and return . System is piped in parallel. Headers are balanced headers from geothermal supply company . Circuits are piped in first out last in
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
17 Nov 2011 01:21 PM
so do you have 214 of header pipe each way for a total of 428 of 1.25 pipe?

what program are you using to calculate head loss?
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
geo pupUser is Offline
New Member
New Member
Send Private Message
Posts:14

--
17 Nov 2011 01:24 PM
No 107 each way , And I hooked up my pool pump and I'm getting air out now
geo pupUser is Offline
New Member
New Member
Send Private Message
Posts:14

--
17 Nov 2011 01:34 PM
Climate master pressure drop calculator
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
17 Nov 2011 02:04 PM
Posted By geo pup on 17 Nov 2011 01:24 PM
  And I hooked up my pool pump and I'm getting air out now

Good to hear.    The WF pressure drop program says you need  32 GPM @ 71' of head.   Not  sure why the difference.
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
geo pupUser is Offline
New Member
New Member
Send Private Message
Posts:14

--
17 Nov 2011 02:15 PM
I think the air maybe out . Would you disconnect the second pump before you did your final check and added antifreeze
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
17 Nov 2011 04:06 PM
Once the air is out, one pump will do what you need.
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system