Posted By canadageo on 29 Nov 2011 01:11 PM
Depending on where you are.... slinky's may work for you... Go into frigid temperature areas, they don't work very good. You need at least 25-30% more pipe, and a lazy mans way of doing the install. Long term it's harder on the system, they are NOT as efficient, as racetrack. For the most part the "older" guys are the problem. They have learned to do it the way everyone said to do it 20-25 years ago.. Well that's what ruined most people's thoughts on geothermal... most didn't work properly. Most put in too small of systems, then undersized the loops for the undersized units... Now not all are still in this category some of the good old boys have adapted but I still run into it all the time.
Hello youngster.
I would challenge your comments.
I would actually go as far as questioning your expertise and asking you to provide data to support your statements.
We install slinkies in the Buffalo, NY area and monitor many of our systems. Our heating degree days are one of the highest in the US. Here are two systems with slinkies with annual EWT monitoring, and it shows that they perform as they were designed to, namely to bring the EWT into the operating range of the heatpump, and to drop not below 30F even at the peak or at the end of the heating season.
http://welserver.com/WEL0448/
http://welserver.com/WEL0267/
A slinky which does not perform is not a result of the slinky loop, but a flawed loop design in general. While it is true that they need more pipe length than straight pipe, they need significantly lesser excavation and speed up the install process. You call that the "lazy mans way of doing the install" I call that the more efficient way to do the install, which helps to save costs to both the customer and the installer.
May be you can explain to us why they are harder on the system if designed properly, or why they don't work as well long term.
If someone undersizes the system or the loop, that is not a slinky problem. While the industry has learned significantly to improve design material, the "older" guys who have the 20-25 years experience I rarely find problematic. The young guys, who have done a few installs, and then think they know it all are the trouble makers. Some even go on the internet and make misleading statements about design and performance.
One must understand that a greatly designed loop and a good performing loop is the one which brings the EWT within the operating range of the heatpump in the most cost effective way.
If one does not understand that, he or she has not understood the geothermal concept.
If you have any data to substantiate your comments, I am the first to listen. Until then you have to be careful not to mislead people.