Posted By FBBP on 07 Feb 2014 07:14 PM
Doc - a few observations/comments.
I totally agree that that feeding the DSH the coldest water will be the most efficient. But for the purpose of discussion lets say that the DHW calls for an average of 5 minutes per hour. Does this mean that the DSH is getting the hottest possible water for 55 minutes? Also I don't understand how the 0713, part of the time shows the colder the water entering the DSH the colder the water leaving the DSH and then a goes through a period of the colder the entering water the HOTTER the leaving water???
So even if the geo is not running the DSH pump comes on when there is a DHW call effectively replacing the dip tube during a draw down?
WEL0713 is a variable speed, it pretty much run s all the time at colder temps.What you see that occasionally it shuts off when the hot water safety stops the DSH circulation pump, then the cold water sensor drops because of ambient influence, but you have thermal siphoning with the outgoing water temp getting very hot due to very low flow (coming only from thermal circulation).
It is important to understand that the key to hot water making efficiency is not so much the colder water going into the DSH, but to pass on the hottest water to the second tank, so the electric element turns on as little as possible. You want the hottest water on the top, even if you pull in hotter water into the DSH, rendering the DSH a few degrees less efficient. But that slight loss is nothing compared to fresh water coming in too close to the outgoing port towards the second tank.