Posted By bobarchitect39 on 22 Jul 2010 10:22 PM
Great thread all. But what about the insulation? What distinguishes "superinsulated" from just normal insulation?
There's no hard definition, but 2x code minimum for clear-wall R values for the location would be a typical starting point. eg: If the code minimum for the area is R19 batts or blown in 2x6" 16" o.c. construction, which has a clear wall value of ~R18, a superinsulated house for that area would have R36 clear-wall values. Slapping an inch or two of foam sheathing on the outside to bring it up to R23-R28 might be good, way better than code, but wouldn't be considered superinsulated by most. If code minimum for the climate is R13 batts in 16" o.c. 2x4, a 24" o.c. 2x6" framing with blown cellulose and an inch of iso on the outside could be considered minimally superinsulated.
Others definitions of "superinsulated" might be "heating & cooling requirements for the structure is less than 1/4 of a code-minimum house", which would involve tweaking aspects beyond simple rated-R, like pressure verification of the air-tightness of the envelope, controlling convective R-losses within the insulation at high delta-T, designing glazing & overhangs/shading for managed solar gain/loss, etc.
Still others consider any clear-wall R value above R30 to be superinsulated, but in my mind it would depend on the climate. R30 walls might be good enough to achieve PassiveHouse spec in some temperate zones in the US when combined with air tightness and a decently insulated foundation/slab relative to local subsoil & seasonal average temps, and well-considered glazing. But R30 wouldn't be as significant an upgrade in ND, MN or the MI-UP, (but still a significant uptick from code-minimums.)