Posted By bi0hazard on 17 Oct 2011 11:59 PM
Thanks for all responses.
I have noticed a few ridge vents around here. If anyone has new vents (other than the standard), it is usually the turbine. 4/5 companies recommended turbines, and only one wanted to the the ridge vent. The ridge vent's design is seems counterintuitive as far as exhaust is concerned, but I am not a professional. It looks better than a turbine, but it is more expensive (quote $900 for my roof, instead of~ $600 for 4 new turbines). Also, it is very windy in DFW, so I think turbines may actually work It makes sense with foil type radiant barrier, that the heat collected between the roof deck and foil must get out, so I see why I need more ventilation, since I only have about 300 sq in of exhaust for ~3000 sq ft roof area.
My AC and ducts are in the attic, standard here. Only 1/5 companies wanted to mastic seal the ducts ( expensive = $300 for 3 units). Others said the ducts appear OK. I don't know how to know for sure who's right. One company actually took temp readings from my ducts and the guy said it leaks just a tiny amount more than it should but overall it looked good.
As far as insulation goes, nobody does cellulose from the companies I called. They use fiberglass. On person said cellulose is garbage that gets degraded to dust over time and they don't want to install it. What really gets me is that companies are split on whether I need insulation or not. Some say I am at R26 the others R38. How can I figure this out? People charge $600 to add insulation, which is more than I want to pay if I don't need it.
Dana, the solar windows you recommend are popular. My neighbors have them but they are super overpriced and they look awful.
Thanks again for everyone's input.
Very windy + turbine== depressurized attic. Unless you have the worlds-best air-barrier and the tightest house in Texas a turbine is going to suck conditioned space air up into the attic, and hot humid air in wherever it can. DON'T DO IT!! It's an energy-loser.
With rafter mounted RB the heat isn't collected- it's reflected back to the roof deck and keeps it from radiating on your ducts & joist tops, insulation, etc. While this raises the temp of the roof deck & shingles, the higher temp on the exterior allows more of that heat to be radiated back at the sky for a net reduction in collected heat. Using a more solar-reflective but still highly emmissive
CRRC rated roofing material is more effective than interior RB, but I'm assuming you have a lot of life left in whatever is up there.
$300 of duct sealing is CHEAP compared to blowing away 20% off your air-conditioning energy and risking ruining your indoor air quality with fiberglass dust in the process, are you kidding? If you're not going to seal the ducts, at least seal the attic, to keep the pressure differences driven by the duct leakage all within the pressure boundary of the house.
You can't tell how much leakage you have by looking- you have to pressure test it and MEASURE the duct leakage. Visual inspections and temp measurements can sometimes tell when you have a total disaster on your hands, but not much more than that. Find a specialist with a duct-blaster test setup who can do the job right and verify the result.
Cellulose will only degrade over time via
excessive moisture cycling. There are houses with 90 year old cellulose in the walls and attics that are doing just fine. In high dew-point climates going with an air-tight attic (even if you don't put the insulation at the roof deck) will put the cellulose inside the pressure boundary of the building, and the air-conditioning will keep it from taking on humidity during the cooling season.
In DFW there's no good rationale for a vented attic. The summertime dew points are high enough that higher attic ventilation rates creates higher accumulation of moisture in the structural wood, and more risk of condensation & mold from outdoor air coming in contact with the air conditioned surfaces. Cellulose crumbing to dust just doesn't happen if applied at proper density and reasonable depths, even under high humidity cycling, but it will settle considerably under humidity cycling. But given that it's more effective during the cooling season at equivalent R than low-density fiberglass, and the fact that it's downright CHEAP, even if you have to top it off with another 6" in 2 decades time, it will have more than paid for itself. But seriously, if the ducts are in the attic consider adding 6" of open cell foam to the roof deck & rafters, sealing all of the venting at the same time (and VERYIFY the soffit sealing!) Between the air-sealing and additional R the load to the AC will drop, and by containing the duct losses within the pressure boundary of the building the net-efficiency of the system will improve.
The Oak Ridge Nat'l Labs data is unequivocal about the effectiveness & economic value of more insulation than R26 (which doesn't even meet current code-min). And you're looking for the most cost-effective route to COMFORT, not mere net-present-value on energy savings. Going to R50 using cellulose or high-density Optima or Spider on the attic floor would be a huge improvement in comfort, as would 6" of open cell at the roof deck and sealing the attic. See the table on pages 5 & 6:
http://www.ornl.gov/sci/ees/etsd/bt...et2010.pdfDFW's cooling season is somewhere between Austin's and Atlanta's, you're only going to get big dollar savings out of RB if your ducts are un-insulated and located in the attic. If you're at code-min on the insulation it'll save some, but the money is better spent on improving the ducts. If the ducts are insulated or located inside of conditioned space, RB buys you squat. But going 1.5-2x code min on the insulation isn't hugely more expensive than bringing your R26ish up to R30-R38 you'll be able to feel the difference, at least as much as with rafter mounted RB, and with higher net annual savings. Open cell foam on the roof + air sealing will be more expensive than a cellulose blast or RB, but it will be the better performer, particularly if the ducts are in the attic.
To figure out your nomimal R value, get up there with a tape measure and measure the depth of the (presumably blown-fiberglass) insulation, and multiply inches by 3.2. If it's only ~8", that's R26. IIRC dode min in DFW is R30, which is more like 10". But if it's not covering the joist tops/truss chords by at least 3" you're getting a huge amount of thermal bridging through the timbers, so any retrofit insulation needs to be at less joist-depth + 3". If those are 2x10s (9.25"), topping the joists by 3" would mean 14-15", or R45-50. But those last 3" add quite a bit more performance than would be accounted for by center-bay R, since it's raising the R-value of the ~R8 thermal bridge of the joists to ~R20. If you insulate right up to the joist tops with 9.25" of blown fiber you'll meet your R30 code min, but with R8 joists most of the heat transfer is being conducted through the joists. With a 10% framing fraction (it's probably more), you end up at ~ R26-R27 for whole-assembly performance. But for 3" more the center-bay value becomes ~R40 but the whole assembly R rises to ~R38- a 50% performance improvement for 33% more material. Even if you do it with low-performance fiberglass, insulate over the joist tops.
Exterior shades are a trade-off between comfort and visual aesthetics, and not everyone will make the same choices, eh?