Why don't you get an HVAC guy to calculate the cooling load through your roof choice and then through the R19 insulation and see how many BTU's you're actually chasing at that point?
Your local building inspector may accept R19 instead of code required R30 based on performance values. Usually, the spray foam MFR has a document of some sort that states that R19 of his product is just as good as R30 fiberglass. Most inspectors accept that around where I live, it's probably the same where you live. That doesn't mean it's the thing to do, just that it does get done that way.
IF the resulting cooling load through the roof is, say, 6000 BTU's on a design day, you might be better off to upgrade your air conditioner to a more efficient unit and add better windows or add additional shading or something rather than spend more money on insulation.
On the other hand, if the resulting load is 18000 BTU's, add more insulation.
|