In most full-time energy efficient (i.e., well-insulated and well-sealed) residential buildings the goal is to reduce cooling/heating loads and uncontrolled infiltration is typically the biggest driver of these loads in these buildings. In most residential buildings, ERV/HRVs are generally setup in a neutral, equal pressure scheme to provide your ventilation air. Consequently, in most residential buildings using ERV/HRVs for ventilation, uncontrolled infiltration is relatively small and vapor diffusion tends to be the dominant building assembly moisture mechanism in play. As such, doing a Glaser dew point analysis to ensure your residential building assembly performs as desired is entirely appropriate. However, in part-time energy efficient commercial buildings, ERV/HRVs are sometimes intentionally run out of balance to achieve a preferred pressurization scheme. As I mentioned in the other thread, in commercial buildings you could have the exhaust air rate exceed the fresh air rate by about 10% to create a slight negative pressure in the winter. In the summer, you could have the fresh air rate exceed the exhaust air rate by 10% to create a slight positive pressure. These preferential pressurizations are intended to control which way air will flow through the commercial building envelope at different times of the year. In the winter it is often better to encourage dry winter air to pass in through the building envelope as it will not condense on its way in. In the summer, it is often better to encourage dry room air to pass out through the building envelope as it will not condense on its way out. Consequently, in many commercial buildings using ERV/HRVs for ventilation, controlled building assembly infiltration/ventilation may be relatively large and may be the dominant building assembly moisture mechanism in play. As such, a Glaser dew point analysis would likely be invalid/inaccurate because vapor diffusion is the only building assembly moisture transport mechanism considered by this method. Building assembly air infiltration/ventilation, building assembly material moisture capillary transport, direct rain intrusion/wetting, and solar heating moisture transport mechanisms are NOT considered. You would really need to do a much more accurate/complicated building assembly moisture analysis using a transient software model that is capable of considering all of these moisture transport mechanisms as well as the humidity, pressure, and temperature initial conditions. Yes, this preferred pressurization scheme can also be used to good advantage in full-time energy efficient residential buildings too, but you will need to carefully consider and properly address combustion air requirements (e.g., appliances needing combustion air) and makeup air requirements (e.g., appliances such as stove exhaust fans needing makeup air). Of course, you will also need to carefully design a building assembly with this preferred pressurization scheme in mind too. In short, this is an integrated, multi-discipline design/build problem and one really needs to know what they are doing to successfully play this game. The home owner also needs to be fully aware of what is going on to ensure that this integrated building assembly/HVAC system will continue to operate as designed or the consequences may be disastrous. Frankly, we wouldn’t trust very many HVAC pros or home owners to get this right. |