Posted By FBBP on 12 Nov 2014 07:16 PM
BTW: Where is the code regarding gas furnaces requiring pre-heating of the combustion air? (This was news to me, and I couldn't find it in a quick web search.)
Alberta Building Code 2006
9.32.3.4.5) An outdoor air supply duct shall be installed between the outdoors and the furnace return air plenum and shall be connected
a) not less than 3 m upstream of the plenum connection to the furnace, as measured along the length of the duct, or
b) through an acceptable mixing device installed in the return air plenum.
Any chance you might be a little light on the cfm given a 6" chimney, two storey stack and wind induced positive and negative pressures on the intake and stack?
Would the stack/wind driven pressures not be the same wither the stove is at full bore or just smothering?
If you look at the exploded view of the Jotul, do you see anything to prevent the combustion air from bypassing the grate if it is covered with ash/coals and rising right to the top? Yes, it has side baffles etc. but it doesn't look like they are directing the incoming air through the fire. Maybe brushing by the side baffles will rise the temperature enough but that really depends on what the actual volume and velocity of the air is.
Most outside air kits I have worked with in the past are between 3 and 5".
That isn't an outdoor connection to the
combustion air, that's the return plenum of the conditioned space air, which has orders of magnitude higher CFM than the combustion air of a wood stove.
I presume that part is inserted in the code to avoid depressurizing the house relative to the outdoors due to duct imbalance issues, since the intake end of the air handler would be the lowest pressure point on the system. By porting that directly to the outdoors, the air-handler & duct system can't depressurize any part of the house below the outdoor pressure, though it can still positively pressurize parts of the relative to the outdoors.It guarantees where most of the air handler driven infiltration enters the house, but not where it exits. It also guarantees that the air-handler driven infiltration air is heated before it goes into the conditioned space too, rather than, say blowing across a drain or potable plumbing and freezing it up.
It doesn't have anything to do with combustion air though.
I've never seen an outdoor air kit for a wood stove requiring anything bigger than 3" I.D. (7 square inch cross section) even for ~150K BTU/hr wood stoves. I can believe 4 inchers may be necessary for some super-blaster stove, but 5? A 5 incher would have a cross section of 19.6 square inches, which would probably be enough combustion air serve a 500K BTU/hr behemoth. What wood stove out there has a 20 inch cross sectional air intake?
The cfm going up the stack is much larger than the incoming combustion air, due to it's very low density after being heated up by 300-600F, and the conversion of solid or adsorb/liquid materials into gases. The combustion air draw of woodstoves is much lower.
This (not super data-driven not highly referenced) source places it at an average 10-25cfm (see the 3rd to last paragraph),
Martin Holladay seems to think it's 30-50cfm (see first paragraph), but that's not too credible. Good old
Mother Earth News is selling the 10-25cfm story too (would they lie to you!? :-) )
Even a wind gust driven surge of 300cfm (the blast of a pretty good sized range hood exhaust fan) is still be far less than a typical gas furnace air-handler's rate.
At typical forced draft tank type hot water heater runs 50-60 CFM. If your wood stove were sucking even that hard on a 3" intake kit would be quite a breeze, getting into bath exhaust & hair dryer type volumes. With the 3" port on my ~50KBTU/hr woodstove I can't feel the air movement at the intake with a bare hand, but probably could detect it easily with a spider web or hair as a wind vane.
I've never looked closely at a recent model Jøtul but I've looked at several others. Most non-catalyic EPA rated wood stoves have a single operable butterfly valve as the draft control, placed at the input of a manifold that splits the combustion air into multiple paths, one or more of which traverses the fire box to feed superheated combustion air at the top of the stove to light off unburnt gases & particulates. The geometry differs by manufacturer and stove type, but the principle is the same- some air-injection ports near the bottom of the firebox, more up top, usually through ports that are smaller than 1/2" in diameter. Is there a good online diagram of the Jøtul model you can refer me to?
While it's remotely conceivable that Jøtul is concerned about mechanically stressing the casting with large temperature differentials, but cast iron is pretty tough stuff. It's pretty common to have ~1950C flame fronts licking the bottom of a pan while cooking the contents at 100C, an 1800C temperature difference, and you can crank the flame up & down with abandon without stressing the pan. Having combustion air 50C lower outdoor temp than indoor temp on an arctic cold day in Alberta is tame stuff by comparison. If there is a rational engineering explanation, it's probably a different issue.