01 Apr 2009 10:50 PM
Posted By mac31313 on 03/31/2009 9:00 PM
have you done a blower door test to confirm your air exchange?

it is true icf's are "tight", but the other systems (insulation,doors,windows) may not be.
spray foam is very air tight and will maintain indoor air temp well if installed properly.

have you accounted for the "latent heat" created by cooking, fridge, laundry, shower, ect?

location of windows and shading (overhang, e--lass, ect)is very important when using a program to calculate loads, if you desire accurate results.

mac

I'm considering getting a blower door test. I don't have to have it since I can't get an Energy Star rating. Energy Star Northwest has no criteria to assess/approve using a crawl space as a supply plenum, nor the attic as a return plenum, as I have built.

My windows are tight. The doors may not be. It turns out that it's not so easy to get an air tight seal at the door bottom with a low profile threshold. I built my house pretty much ADA compliant.

The Manual J calc for my house did not include the heat of living activities because it's so difficult to estimate accurately. Be careful how you use the term "latent heat." It has a very specific meaning in the a/c world. It's the heat absorbed or released as water is vaporized or vapor is condensed.

The Manual J program used for my house, Wrightsoft, very accurately accounts for window parameters, including shading.



Even a retired engineer can build a house successfully w/ GBT help!
Ken SaganUser is Offline
New Member
New Member
Send Private Message
Posts:3

--
02 Apr 2009 07:28 AM

The HVAC equipment size seems about right. I have a 2,000 sq ft. ICF home -2 levels for a total of 4,000 sq ft and heat it with a 1 1/2 t. Geo in a 5,900 HDD area. I use a sealed combustion fireplace for my back-up on a remote thermostat. I have found that in that Climate Zone that I need the fireplace a few times a year amd did not warrant a larger unit. Air conditioning wise, I need the unit to run maybe 12 days a year. We also have clay walls inside the home that in the early summer will absorb the humidity and act as a "poor mans" air conditioning. We close up the house during the day and air it out at night thus giving up the heat and humidity. I an not a strong supporter of fiberglass, so I used spray foam on the underside of my trusses. This necessitated of course a HRV. I pipe all my bathroom fans back to the HRV and do not directly vent outdoors except the kitchen stove exhaust. I kept my penetrations of the building to a minimum.

Window wise. Since I worked at a University (Building Science) and we conducted window testing I had an opportunity to see all different brands and types. I chose a fiberglass frame window that would expand and contract about the same as the glass, thus the chance of breaking a seal on the thermopane is reduced.

Overhangs is a very important item to consider also and I incorporated a 3 ft overhang on the home and held my window to wall ratio well within 15%. I faced the home due south, thus having the large overhang on the east/ west sides with the less amount of windows on the west wall. I also have skylights on the north roof got light.

As a person working in the construction field ( over 40 Years now), I have seen just about everything and would not build anything other than an ICF home. Love it, love it, love it.



Bruce FreyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:429

--
02 Apr 2009 10:55 AM
Posted By markross on 04/01/2009 7:45 PM

however dont forget the heat of curing is also still adding to your load.

At 5+ months any heat of hydration effect is looooooong gone.  Heat of hydration is not much with 4" or 6" thickness...even with ICF.....and it peaks at day 2 or day 3.  It basically follows the rate of strength gain.

Concrete strength gain and heat of hydration is minimal after 56 days for normal concrete mixes......the curve is quite flat at that point.

Bruce



markrossUser is Offline
New Member
New Member
Send Private Message
Posts:38

--
02 Apr 2009 04:06 PM
Posted By Ken Sagan on 04/02/2009 7:28 AM

The HVAC equipment size seems about right. I have a 2,000 sq ft. ICF home -2 levels for a total of 4,000 sq ft and heat it with a 1 1/2 t. Geo in a 5,900 HDD area. I use a sealed combustion fireplace for my back-up on a remote thermostat. I have found that in that Climate Zone that I need the fireplace a few times a year amd did not warrant a larger unit. Air conditioning wise, I need the unit to run maybe 12 days a year. We also have clay walls inside the home that in the early summer will absorb the humidity and act as a "poor mans" air conditioning. We close up the house during the day and air it out at night thus giving up the heat and humidity. I an not a strong supporter of fiberglass, so I used spray foam on the underside of my trusses. This necessitated of course a HRV. I pipe all my bathroom fans back to the HRV and do not directly vent outdoors except the kitchen stove exhaust. I kept my penetrations of the building to a minimum.

Window wise. Since I worked at a University (Building Science) and we conducted window testing I had an opportunity to see all different brands and types. I chose a fiberglass frame window that would expand and contract about the same as the glass, thus the chance of breaking a seal on the thermopane is reduced.

Overhangs is a very important item to consider also and I incorporated a 3 ft overhang on the home and held my window to wall ratio well within 15%. I faced the home due south, thus having the large overhang on the east/ west sides with the less amount of windows on the west wall. I also have skylights on the north roof got light.

As a person working in the construction field ( over 40 Years now), I have seen just about everything and would not build anything other than an ICF home. Love it, love it, love it.


Cure times are a lot longer in an icf to ultimate strength, and the heat remains higher with a more complete cure.


Mark Ross<br><br>"Le Canuck"
Bruce FreyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:429

--
02 Apr 2009 05:09 PM
Posted By markross on 04/02/2009 4:06 PM

Cure times are a lot longer in an icf to ultimate strength, and the heat remains higher with a more complete cure.


.....and why would this be different than, say, a concrete cylinder from a testing lab's curing room?

Concrete hydration is a chemical reaction (exothermic) and the amount of heat produced by this reaction is mostly a function of the amount and gradation of the cement in the mix.  The insulated forms will keep it warmer for a few days longer.

The curing curves for ICFs and the same concrete in a slab or column will be virtually the same shape (rate of gain), with the ICFs having a slightly higher ultimate strength because of better curing.  This is a small % and should not be factored into the mix design.

One of the potential benefits of ICF (for those who think in terms of decades, scores of years or centuries) is that being encapsulated in styrofoam may prevent or minimize carbonation, which deteriorates concrete over time from the surface inward. 

Bruce


markrossUser is Offline
New Member
New Member
Send Private Message
Posts:38

--
02 Apr 2009 05:45 PM
Posted By Bruce Frey on 04/02/2009 5:09 PM
Posted By markross on 04/02/2009 4:06 PM

Cure times are a lot longer in an icf to ultimate strength, and the heat remains higher with a more complete cure.


.....and why would this be different than, say, a concrete cylinder from a testing lab's curing room?

Concrete hydration is a chemical reaction (exothermic) and the amount of heat produced by this reaction is mostly a function of the amount and gradation of the cement in the mix.  The insulated forms will keep it warmer for a few days longer.

The curing curves for ICFs and the same concrete in a slab or column will be virtually the same shape (rate of gain), with the ICFs having a slightly higher ultimate strength because of better curing.  This is a small % and should not be factored into the mix design.

One of the potential benefits of ICF (for those who think in terms of decades, scores of years or centuries) is that being encapsulated in styrofoam may prevent or minimize carbonation, which deteriorates concrete over time from the surface inward. 

Bruce
Bruce:

Thermocouples proove that during winter (reporting done in North Bay, Ontario, Canada), in an unheated ICF concrete structure, placed in the fall, by mid winter, the temperatures of the core are still upwards of 50 degrees.  Additionally, if concrete "dries" instead of curing, then it will stop hydrating.  A good example of this, is the mass of the Hoover Dam, which still has a very high internal temperature to date and has been monitored from date of construction.



Mark Ross<br><br>"Le Canuck"
mac31313User is Offline
New Member
New Member
Send Private Message
Posts:20

--
02 Apr 2009 07:12 PM
dmaceld,

yes, latent heat is the heat required to be removed to condense water vapor(to get it out of the house)

most people don't realize the amount of water vapor they put in the house.
showering without exhaust fan, boiling water on stove, air drying clothes ,and water form defrost cycle on fridge, ironing(steam), ect

in a dry climate it may not be as important.....but in Florida, we spend a lot of energy to remove water form our homes.

sounds like you are getting a lot of solar gain how much south glass exposed in summer vs winter?
mac


OhioICFUser is Offline
New Member
New Member
Send Private Message
Posts:13

--
02 Apr 2009 08:57 PM
OK... here's some more data. My Nudura block supplier let me try out his Portland Cement Association HVAC sizing software (4.0).

Overall, I found the software very easy to use. It assesses the location, orientation, and geometry of the house, the window placement, window shading, wall construction, amount above/below grade and several other parameters. The only shortcomings that I found were I wish it asked for the type of attic insulation (for thermal mass reasons, as well as air infiltration); I also wish that it did not use a default air infiltration rate based on wall construction... or at least allowed one to select an ERV/HRV option. I believe our "effective" infiltration rate will be less than the default specified by the tool because our fresh air will be going through a heat exchanger. That said; it's a very good tool, and should continue to improve.

My house, as described in the first few posts in this chain (3600 sqft walkout ranch w/ 6" block and now a R49 cellulose attic), was tested for two different options using 70 degrees as both the heating and cooling setpoints:

1) windows with U=.33, and SHGC=.5
This resulted in requirements of 25,000 BTU/hr heating and 19,000 BTU/hr cooling with 9% of the cooling load being "latent."

2) windows with U=.21, and SHGC=.3
This resulted in requirements of 22,000 BTU/hr heating and 17,000 BTU/hr cooling with 12% of the cooling load being "latent."

I thought this was very interesting... but raises more questions than answers:
--For $4000, are the better windows worth it?
--If not, would a 1.5 ton unit be able to adequately heat an Ohio house with the lesser window selection?
--At what point should one start sizing for heating rather than cooling?
--The program assumed infiltration per ASHRAE standards, how much of this would be temperature corrected by an ERV (lessening the heating/cooling load)?
--How should the condenser be paired with an Air Handler for a 35,000 cubic foot house?... the 1.5 ton blower might not be strong enough... but like dmaceld pointed out earlier, a larger blower might not get the humidity out well enough.

...lot's to think about...
I'd love to hear your thoughts...


mac31313User is Offline
New Member
New Member
Send Private Message
Posts:20

--
02 Apr 2009 09:15 PM
how much wood can you split?
1.5 ton might work "most of the time"

mac


OhioICFUser is Offline
New Member
New Member
Send Private Message
Posts:13

--
02 Apr 2009 09:29 PM
Agreed... Well, that's why we're putting in a woodstove (sort of).

If you need an 8 ton unit, going to a 7.5 or 8.5 ton unit probably wouldn't amount to anything... but switching from a 1.5 to 2 ton is a 25% change. Maybe a 2 ton condenser with a 2 ton variable speed blower is the answer(?).


markrossUser is Offline
New Member
New Member
Send Private Message
Posts:38

--
02 Apr 2009 10:14 PM
6.5 btu/hr/square foot of house in heating sounds very, very low.  I live in Ohio, with a winter design temp of 12 degrees F in cincy. This represents a min of 18.3 btu/hr of straight loss, for every square foot of window area for the windows at the U value you have entered.  With an average 10% window area, this translates to a window loss load of 6,588 BTU without any air infiltration being considered.  Three doors, that are well built, in raw loss translates to another 1,008 Btu, if you have a patio door, you are looking at another 700 Btu per 5' wide slider, with 3 panes of glass.  now the wood burner...thats a standard at best case of very close to 1000 btu/hr.  with your walls, even at 2 Btu/hr, you have to have roughly 2,400 lineal feet at the very lest for 4,800 Btu/hr, and your roof raw loads will be 2 Btu/hr/ft with 1800 square feet at 3,600 Btu/hr for a total of 17,696 Btu/hr raw loads, with no infiltration, lineal footage of crack for openings, other openings, basement slab loads, garages in the building, roof penetrations such as light fixtures, dryer or exhaust vents for bathrooms (they typically rate around 300-400 btu/hr)any missed openings or icf wall foam omitted, rafter edge loss, or leakage through conducted areas.  All of this is assuming you are in cincy area, anywhere north of dayton, and your equipment will be too small, if it is even large enough for the lower part of the state. 

I think you may want to look a little more at the heating and cooling loads, (get a professional HVAC engineer to do it there are many out there that can do proper heat loads for these buildings), because I have yet to see a house with less than 12-14 btu/square foot in Ohio.

If you are as well built as you claim, then your cooling loads would be a lot higher than heating loads.  EG we have a little 2200 square foot in central Michigan (this includes the basement), with a full ICF roof on it, that needs 1.5 tons of cooling, and there are practically no south facing windows in it.  however the two that are there, do overheat the place in the summer.  And the windows...they are the best.  Maybe eldon can post here on this.  Personally, I made the same mistake....twice.

Oh yeah, I forgot about loss from wind, which is actually fairly high.

Mark Ross




Mark Ross<br><br>"Le Canuck"
OhioICFUser is Offline
New Member
New Member
Send Private Message
Posts:13

--
02 Apr 2009 10:40 PM
markross -- awesome post; there is a lot here to think about. Your numbers do make sense to me... The 17,696 BTU/hr sounds about right for the raw loads... appliance and bodies will offset some of the leakage, but it's a little too close for comfort for me... and for that reason, I think I'm giving up on the 1.5 ton idea. It was a nice thought while it lasted... but just doesn't seem feasible anymore.

The good thing about this is even if we fall short slightly with a 2 ton unit, we can still light a gas or wood fire to supplement the heat pump. 99% of the time, we should be covered just fine.

...and we are right by Dayton. Small world.


markrossUser is Offline
New Member
New Member
Send Private Message
Posts:38

--
02 Apr 2009 11:38 PM
Posted By OhioICF on 04/02/2009 10:40 PM
markross -- awesome post; there is a lot here to think about. Your numbers do make sense to me... The 17,696 BTU/hr sounds about right for the raw loads... appliance and bodies will offset some of the leakage, but it's a little too close for comfort for me... and for that reason, I think I'm giving up on the 1.5 ton idea. It was a nice thought while it lasted... but just doesn't seem feasible anymore.

The good thing about this is even if we fall short slightly with a 2 ton unit, we can still light a gas or wood fire to supplement the heat pump. 99% of the time, we should be covered just fine.

...and we are right by Dayton. Small world.

I am not saying my reply is the answer, nor is it right, I have done a few heat loss's and work in wright soft for my own projects only now.  I just have found, that if you break it all down, its easier to understand, however you need the information to start with.

Dayton gets a lot more snow than we do here, its funny what a 40min drive will do for weather.

BTW I am originally from Northern Canada, I just live down here now.  However, it is a small world.

Nice texting "ya-all"


Mark Ross<br><br>"Le Canuck"
dmaceldUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1465
Avatar

--
03 Apr 2009 12:04 AM
Posted By mac31313 on 04/02/2009 7:12 PM

sounds like you are getting a lot of solar gain how much south glass exposed in summer vs winter?
mac

The house is at 45 to the world so there's no directly south facing glass. I've got two 6/4 x 6/0 windows facing SW that are pretty much 100% exposed to the sun in mid winter, and about 30% exposed in mid summer. I've got a pretty good overhang above them, a bedroom wing to the SE of them, and a porch to the NW of them. There's two 5/0 x 6/0 windows on the SW wall shaded by the porch. They have 0 sun in the summer and about 30% sun in the winter. Two bedroom windows face SW with no shade but they're only 2/8 x 5/0.

I can't remember, and I'm too tired to look, if window sizes are normally stated H x W, or W x H. The above are W x H.



Even a retired engineer can build a house successfully w/ GBT help!
Bruce FreyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:429

--
03 Apr 2009 04:35 AM
Posted By markross on 04/02/2009 5:45 PM

Thermocouples proove that during winter (reporting done in North Bay, Ontario, Canada), in an unheated ICF concrete structure, placed in the fall, by mid winter, the temperatures of the core are still upwards of 50 degrees.  Additionally, if concrete "dries" instead of curing, then it will stop hydrating.  A good example of this, is the mass of the Hoover Dam, which still has a very high internal temperature to date and has been monitored from date of construction.


Do you have a link to the study?  I would like to see the temperature curves.

It is clear that hydration will continue as long as there is availble moisture and silicates. There is enough microscopic water in a good mix to allow it to gain strength almost indefinitely (the curve gets really flat), even more so if it is not subject to surface drying.

One of my projects in the past had a 16,000cy, 10' thick mat and pumped concrete 1000' vertically, so that got me very interested in concrete technology.  After almost 30 years, they tell me that the mat is still a bit warm, too.

If you like concrete stuff, you might find this link interesting:
<http://www.cement.org/tech/pdfs/pl972.pdf>

Bruce
(sorry for hijacking the HVAC, Window and insulation thread)


dmaceldUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1465
Avatar

--
03 Apr 2009 08:35 AM
Posted By Bruce Frey on 04/03/2009 4:35 AM

There is enough microscopic water in a good mix to allow it to gain strength almost indefinitely (the curve gets really flat), even more so if it is not subject to surface drying.

One of my projects in the past had a 16,000cy, 10' thick mat and pumped concrete 1000' vertically, so that got me very interested in concrete technology.  After almost 30 years, they tell me that the mat is still a bit warm, too.


I have been told that concrete has something like a 100 year lifetime, 50 yrs getting stronger and then 50 yrs getting weaker and deteriorating. This is probably more likely in thin structures such as walls and slabs than in huge masses like dams.

When I visited Grand Coulee dam in Washington during a college field trip, ala 1966, we were told that the piping for running cooling water through the dam had been removed only a few years before that. I don't remember when the dam was built but I think it was the '30s.




Even a retired engineer can build a house successfully w/ GBT help!
OhioICFUser is Offline
New Member
New Member
Send Private Message
Posts:13

--
08 Apr 2009 04:39 PM
As I stated in my previous posts, we've got a 3600 sqft house (1 story ranch w/ walkout basement) built w/ ICFs all the way up to R-49 cellulose in the attic w/ raised heel trusses. We're using an ERV for ventilation. Most of our windows face North (due to the lot topology).

I ran the portland cement HVAC sizer for ICF houses: it says I need 1.5 tons cooling, 2 tons heating.
I consulted my local HVAC installers that used Wrightsoft: it says I need 1.5 tons cooling, 4 tons heating.

Bottom line: we selected a 2 ton condenser w/ 2 ton variable-speed blower. When it gets really cold, we won't want the heat pump running anyway; we'll be using resistance heaters. This works out to about 6.5 BTU/sqft. Let the experiment begin...

We're also putting in a direct vent fireplace and a woodstove for emergencies. I'll be sure to let you all know how this system performs.


Bruce FreyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:429

--
19 Jul 2009 03:31 AM
Posted By dmaceld on 03/30/2009 12:35 AM
One aspect of a well insulated air tight house that I haven't seen much discussion of, and is causing me to have some questions, is the heat generated by bodies and normal living activity. I'm about same as finished with my 2000 sf ICF house. I used 6" Buildblock forms, have an insulated crawl space including XPS under the rat slab, have about R 35 to 40 spray foam on the underside of the roof, and Andersen 400 casement windows. My heat load calculated at about 20,000 Btuh at 20° outside, and 36,000 at 9° outside. I installed a 3 ton Daikin heat pump.

Here's my problem, or potential problem. We're not living in the house yet, but have been working in it all winter. What I have noticed is when the outdoor temp is about 40°+ the body heat from 4 workers, and the power tools and lights we used, along with solar through the front windows, would raise the indoor temp from about 70° to 73° during the day with the heating system not kicking in at all. The windows still have the factory plastic film on them so they aren't totally clear.

What I'm beginning to wonder is if I may have traded a reduced heating bill for an increased air conditioning bill. I may have to run the a/c at a lot lower outdoor temp than one would normally expect to have to to get rid of the normal heat generated by life activities. I haven't made much use yet of the Econo Cool mode of the Ultimate Air ERV so I don't know yet how effective that will be in cooling the house.

Be aware that as you super insulate your house, and get the required heating system size down to a very minimum, you may be holding naturally created heat inside to such a great extent that you will need cooling from March to November!!!

Like I said, there hasn't been much discussion about this, that I've read anyway, and I don't have a long enough history yet to define the issue better, but I really think it's a subject we need to keep in mind. The real kicker is that heat generated by breathing, walking, talking, cooking, watching TV, surfing the 'net, etc., is such a variable it will be hard to place a reliable number on it.


Now that it is summer and I assume you are living in your house, how is your system performing?

Bruce


OhioICFUser is Offline
New Member
New Member
Send Private Message
Posts:13

--
19 Jul 2009 08:02 AM
Bruce,

Unfortunately we're not in yet (probably 6 months out)... the banking process was slower than expected. I will certainly post what I observe though.

Cheers!


ClarkUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:248

--
19 Jul 2009 11:50 AM

Another option to consider as a means to reduce thermal gain/loss through windows is to install rolling shutters.  Our ICF house has several SW facing windows which get 100% sun exposure in the late afternoon.   The shutters can be lowered to block the sun as needed.  Since rolling shutters are on the exterior side of the window, they are much more effective than interior shades for blocking solar radiation.  In winter, they provide an insulated barrier from wind and, thereby, increase the R-value of the window.

 

Although they can be installed as an afterthought on most homes, we didn’t like the aesthetics of the exterior take-up box above each window.  Instead, the 12-1/2” thick ICF walls made it possible to hide the shutter box inside the wall (the picture in an interior view of the shutter with the insulated access cover removed.)  Rolling shutters are not inexpensive, but cheaper than upgrading to high R-value fiberglass windows.  We coupled them with Pella Designer Series casement windows (U=0.25.)  When you consider the other benefits of rolling shutters (privacy, security, storm protection), they’re worth at look.


Attachment: INT0005.JPG