Hi all,
Great forum here!

This is a question about further improvement to an already well-functioning GSHP system. The question is will adding an outdoor reset system help out much more in the following scenario. Don't have the KW usage at hand but our electric- for-heating portion of the bill runs between approximately $40-$90 month during the colder parts of the winter (includes well-pump power).
Setup:
4200sf in 1st/2nd living space plus 1500sf garage/workshop
(living space is tubing in gypcrete/garage is tubing in slab).
All exceptionally well insulated and sealed (w/dual-core HRV).
We keep the living space @ 73degF day/night/winter/summer and the garage/shop @ 58degF during the winter.
Location: Montana (northern) climate

Design temp -35degF+20mph wind.
GSHP is
one Econair GW471 (4 ton) w/DSH takeoff for DHW assist. Buffer tank is 50 gal. water heater with heating elements as backup (never needed/powered off). It does have cooling capacity through forced-air cooling coils that are in-use not more than 2-3 months of the year. Duty cycle at -25degF is approx 60% on.
System is groundwater sourced with 1 supply & 1 recharge well. Groundwater temp is constant 60degF. Fortunately, there are no water fouling/scaling problems to speak of with a LSI index of -0.1 (no nasty water chemistry for the core either).
Hydronic hi (buffer tank) temp is 92degF which is plenty for worst condtions encountered so far (-25degF/25mph wind). I found that when it is warmer outside (say 50degF) we can run the tank at 77degF. I don't think we could go much lower as the room temp is set at 73degF.
Which leads to the main question: With such a limited range between the required high and minimum low buffer tank temps will an outdoor reset unit be worth it? There are no direct numbers in the Econair engineering chart to work with so we have to interpolate. For example our EWT is beyond their chart for heating but I think the COP would improve to some extent (using Econair's 50degF EWT chart entry should increase COP from 5.5 to 7.3 for at least some of the heating season).
I was looking at the Tekmar 256 unit as it provides all the functions required during heating season but am concerned that it might not operate quite right within the limited buffer tank working range (using auto or fixed differential) and the pre-programmed curve may not be optimal as it appears to be primarily designed for boiler systems. I did read somewhere there was a firmware change in 2010 to the Tekmar 256 unit to better accomodate heat pumps but I cannot verify this. Also I wasn't thinking of using an outdoor reset on the cooling side as the season is so short.
Any thoughts are welcome,
Thump