Hi, all. I hope I'm not asking a tired question...although my futile search for an answer says I'm not. This is a math story-problem: I'm building a house in New Hampshire, Climate Zone 6. The house will have a "hot roof" (unvented roof) insulated with sprayed polyurethane foam applied to the bottom of the roof deck. The roof area is about 2,500 sqft. I've gotten a pretty good quote from a contractor I trust. He has spec'd R-38 (6") for the roof. For an additional $3,180, he'll increase it to R-51.4 (8"). My question is this: how do I go about evaluating whether or not the extra $3k investment is worth it? If I assume a 10-year payback period (that's as far out as I'm willing to go), then I have to save $318/yr in heating costs. As I'm installing an ultra-efficient Viessmann condensing boiler, it's hard to imagine being able to cut out another $318/yr. Am I right, economists? Any input on how to think about this problem would be greatly appreciated. Thanks in advance!
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
12 Nov 2009 01:38 PM
You'd have to save more than or less than $318/year depending on what assumptions you make on the price of borrowed money vs. the after-tax return you might have expected on it otherwise, as well as the current price & inflation rate of fuel pricing   There are several net-present-value calculators online that can put it in perspective.

Even so, using a very crude insulation upgrade savings calculator, it's hard to say that you'll go NPV+ in 10 years with most reasonable assumptions:


http://www.builditsolar.com/References/Calculators/InsulUpgrd/InsulUpgrade.htm


Southern NH is about a 7000HDD climate, insert your current fuel price and 90% efficiency on the boiler for annual and 10 year (simple, not present-value) savings.

A more cost-effective way to go high-R in that climate would be to do R30 (4.5-5") of foam at the roof deck, and another R30 of wet-spray cellulose under that for a net R60.  Closed cell foam is a premium product at a premium price- great for when you need/want the vapor retardency or high R-per-inch, but it's an expensive way to super-insulate.  If your splitting the R value between cc foam & fiber with the foam on the cold side (exterior) of the fiber, be sure that the foam is at least 50% of the total R in your are (40% is OK if you're in the Portsmouth coastal region).

If it's basically a dead-space/storage-space attic, it's fine to use dry-blown cellulose the attic floor for the fiber, but be sure to air-seal the attic from conditioned space well.  A 2x10 joist filled to the top will yield about R30-R33 in the center between joists, R25-ish overall (due to the thermal short-circuits of the joist.  It'll make the attic space colder, but won't get/stay below the dew point. (You can monitor it for awhile- if the RH stays above 80% all winter you could put in a small dehumidifier to guarantee it never condenses.)

Natural gas, or propane?  (There's a ~300%+ difference in $/BTU between the two in central MA right now, but NG prices are highly variable between utility companies in New England.)
jbirandallUser is Offline
New Member
New Member
Send Private Message
Posts:2

--
12 Nov 2009 05:54 PM
Thanks so much for the quick response! I think you really nailed the answer. The link to the calculator is especially appreciated.