Posted By rykertest on 09/11/2009 8:49 PM
I think it's a good design but he said the fact that they have 2 walls that are rather long (75') without any breaks in the wall makes it "weaker".
Is this house subject to the IRC2006, or 2009? If so, the building official very well may require you to have the plans stamped by an engineer. The reason being, the IRC specifically limits its provisions to houses that are no longer than 60' in any plan dimension, nor more than 32' floor clear span and not more than 40' roof clear span. I have the 2006 IRC but I can't see that that limitation would have been relaxed in 2009.
R611.2 Applicability limits. The provisions of this section
shall apply to the construction of insulating concrete form
walls for buildings not greater than 60 feet (18 288 mm) in plan
dimensions, and floors not greater than 32 feet (9754 mm) or
roofs not greater than 40 feet (12 192 mm) in clear span. Buildings
shall not exceed two stories in height above-grade. ICF
walls shall comply with the requirements in Table R611.2.
Walls constructed in accordance with the provisions of this section
shall be limited to buildings subjected to a maximum
design wind speed of 150 miles per hour (67 m/s), and Seismic
Design Categories A, B, C, D0, D1 and D2. The provisions of
this section shall not apply to the construction of ICF walls for
buildings or portions of buildings considered irregular as
defined in Section R301.2.2.2.2.