Forums > Green Building Technologies > Radiant Heating > Subject: Radiant Circuit Pump Question

You are not authorized to post a reply.   
Prev Next
Author Messages
ergnutUser is Offline
Registered Users
New Member
New Member
Send a message
Posts:18


10/22/2008 9:50 PM  
When the air temp in my house rises to the target for the radiant system, the 'mix target' temperature for the water drops low, but the circulating pumps still run.   Is this OK?  It seems like the circulating pump runs all the time, regardless of whether heat is being added to the radiant circuits.  It's a viega basic heating control, and a grundfos pump.



Thanks

quailrunnerUser is Offline
Registered Users
New Member
New Member
Send a message
Posts:14


10/27/2008 7:36 PM  
What's the set-up?  More detail needed; is there a slab w. a sensor?
BadgerBoilerMNUser is Offline
Registered Users
Basic Member
Basic Member
Send a message
Posts:122


10/27/2008 8:59 PM  
Sounds like it is working on outdoor reset and yes the pump may run part or all of the time. A question for your designer I think.

MA
www.badgerboilerservice.com
ergnutUser is Offline
Registered Users
New Member
New Member
Send a message
Posts:18


10/28/2008 9:17 AM  
There are air temperature sensors in the basement and 1st & 2nd floors - no slab sensors.