Wiring well pump in Open Loop system
Last Post 19 May 2009 10:21 AM by joe.ami. 1 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
eisensmsUser is Offline
New Member
New Member
Send Private Message
Posts:18

--
19 May 2009 09:26 AM
Normally, I see a pressure switch used to control the submersible well pump, to turn it on and off.
Would it be possible to just have the well pump controlled by the heat pump, such that when the
heat pump turns on, it activates the well pump, and when the heat pump turns off, it deactivates
the well pump.  This would eliminate the need for a pressure switch, right?
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
19 May 2009 10:21 AM
With the right pump you could do as you describe. Pressure switches and tanks were an attempt to keep pressures fairly static without short cycling pumps in low use situs (i.e. washing your hands).
With the relatively low pressure requirements of geo, low pressure or vari pumps have the advantage of low noise from flow raters.
J
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!