Basic questions on Steel SIPs (kinda long)
Last Post 18 Nov 2007 02:59 PM by cmkavala. 12 Replies.
ReadyToRetireUser is Offline
18 Nov 2007 08:31 AM
All,
When I thought of SIPs, I envisioned OSB clad panels.  Having worked with wood, the problems were fairly evident, but they seemed to be significantly outweighed by the advantages.  Thanks to this forum I'm now aware of steel clad SIPs, but I have no experience working with sheetmetal, so problems and solutions are far less obvious.
I've bought and read Morley's book, which discusses OSB/SIP construction.  But I've not found a similar book for Steel/SIP construction.  Is there one?  Has anyone compiled a realistic list comparing OSB and steel skin SIP techniques for residential or small commercial construction?
If it matters, I am considering building in the Eastern half of Virginia where the heat load exceeds the cooling load but without the real cold of the Northern states.  And there are humid summers with rain -- but not to the extent that the South-Eastern states have.  I live in Northern Virginia and have had minor problems with termites, carpenter ants, and carpenter bees, and significant, but not major, problems with humidity based rot in plywood soffits.  So steel has a *real* attraction.
My questions:
Thermal bridging at edge caps:  During the summer, this would be a seemingly minor efficiency issue.  But, during the winter, it could lead to condensation on each door or window penetration similar to that along Aluminum window frames.
Does this limit how far North steel skins are practical?
Is there an accepted solution that's not too unsightly?
Fondation connections:  The construcion technique for OSB SIPs seems to naturally form a layered water barrier -- a 2x plate that is straddled by the skins to form a lap on the outter surface.  My understanding is that the 2x plate is replaced by a steel channel into which the SIPs are placed.
When water gets beyond the siding, it would seem to naturally pool in that channel with no way to dry.  Why is that not a problem?
Do I need a house wrap just for that joint?
Does the channel have an even greater need for a flat and level foundation than a plate?
What fasteners are used and is any unusual tooling required?
Connections between panels:  My understanding is that the steel skinned panels that fit together forming an inner and outer lapped joint at the skins and a tapered, mating joint in the foam.
Is the joint slid together or snapped together?
The joint would seem strong in tension, but how does it do in compression:  Does a steel/SIP wall withstand racking as well as a nailed, spline-joined OSB/SIP would?
OSB skins, with their nailed splines, allow forming door and window openings by inserting partial panels.  Without the nails to hold it in place, what keeps a steel skinned, partial panel from sliding down?
Mounting cabinets:  OSB skins allow an easy to understand solution of scabbing on a 1/2" ply or OSB sheet instead of drywall where the cabinets will mount.  How are cabinets mounted onto steel skins?
Dry walling:  A real side benefit to OSB SIPs seems to be not worrying about hitting studs with DW screws -- you hit OSB no matter where you shoot.  Steel skins seemed to suffer a corresponding problem with having to fir out to allow electrical service because there were no chases in the panels.  But, in a recent thread, Chris Kavala noted that you could mount drywall directly to the steel skin in areas where you didn't need to run wiring.
What screws are necessary to mount DW on a steel skin?
Are they available for a auto feed driver?
Electrical wiring:  A tall base molding with an internal chase and outlets in that molding (and no switches in those wall sections) would seem to eliminate the need to fir out.  But:
How do you wire the doorbell?
Is there an accepted way to mount and wire the internal switches for outside lights?
Can household wiring be run within the door opening and surround?  (Would it meet code?  If so, then I could add a small key shelf with a thicker base, mount the switching and chase in it, and mate it to the door molding.)
How do you mount and wire the exterior, wall mounted lights without a chase?
Sorry if they're dumb questions, but I don't yet understand the process.
Thank you for any comments and for any references that you can recommend.
Very respectfully,
Larry
jmagillUser is Offline
18 Nov 2007 08:46 AM
"Sorry if they're dumb questions, but I don't yet understand the process"
Not dumb! A very well thought out and put together post. Inquiring minds want to know.
I think if the Steel skinned SIP Manufacturers put more of this info on their websites, they would educate the public and increase their sales.
18 Nov 2007 08:47 AM
I'll tag on and ask another possibly naive question. To mount siding or stucco on the exterior, or shingles on the roof, the steel skin is pierced with screws. Wouldn't this leave hundreds of spots for moisture to enter the wall (or roof)?. If the foam inside then acts like a drainage plane, taking the moisture down to the bottom of the panel, then how does it get out?
18 Nov 2007 09:52 AM
Posted By ReadyToRetire on 11/18/2007 8:31 AM
All,
I've bought and read Morley's book, which discusses OSB/SIP construction.  But I've not found a similar book for Steel/SIP construction.  Is there one?  Has anyone compiled a realistic list comparing OSB and steel skin SIP techniques for residential or small commercial construction?No one has done one yet, but unlike OSB all steel SIPs are not created equal or generic, they come in a variety of widths 24" to 48" and a vary in available lengths. The interlocks are all different, some companies pay royalties to others for patent infrigements on the interlocks. Some require the seams to be stitch screwed together others are ingineered without joint fastening.
So it would be difficult to make a "standardized" manual when there are so many variables. Most OSB panels are generic, ther a few that have some uniqueness to themselves
My questions:
My rule of thumb is, if you are north of the Mason - Dixon Line then you should start using thermally broken base, top & window/door buck channels
No, ther are no limitations, many steel sips houses have been built in Calgary and other parts of Canada
There is no change in the appearance of the structure
Channels have weep holes to let out any moisture if it gets in
It is not neccessary , you could seal the joints with a self stick tape if you wanted .
No, we get some pretty ugly slabs in Florida, we simply use a self expanding foam under the channel - this will float out any irregularities.
Fasteners:
For plate anchoring - wedge anchors or wedge bolts
For panel to channel attachment - #10 x 3/4" tek screws
For roof attachment  - Trufast HD and LD SIP screws, with washer
Tooling:
A Refrig Panel saw is recommended, blades are cheap about $5.00 each
Magnetic level
cordless and corded drills
magnetic hex driver
If you are building more than one we would reccomend a Muro automatic feed gun with strip screws, It will pay for its self in 2 jobs
That varies with the MFg. ours are a friction fit, others have a snap connection, others are screwed together.
I have not compared the racking test of one against another, I can tell you that with the 3 different steel SIP companies I have used, they all have tested out at triple the strength of wood framed walls, they all can be used as shear walls. We can e-mail you the test data including impact testing
We normally don't insert partial panels, unless the window/door is too large, in that case we would place one screw at the top seam to hold in position until - the next panel is installed and the openig channels installed
A 4" x 18 ga. flat stap - stitch screwed to either steel skin or furring  ( these are available at any metal stud supplier)
Same as a wood drywall screw
Are they available for a auto feed driver?Yes
Electrical wiring:  A tall base molding with an internal chase and outlets in that molding (and no switches in those wall sections) would seem to eliminate the need to fir out. You could do that but, most people like the conventional placement.
But to wire an OSB house, electricians have likened it to doing a remodeling job, needing to use cut-in boxes and fishing wires. This difficulty has driven up the cost of electrical, we have had a few electrical inpectors not like the fact that the wires were concealed
 But:
You are correct, but the chase also provides aconvienent chase for 1/2" water pipes on an exterior wall, that can be problematic with OSB
Isn't is also much easier to fish wire thru a 1-1/2" air space to add a recetacle later than thru a solid OSB wall?
Is there an accepted way to mount and wire the internal switches for outside lights? Use a surface mouted pancake box attached to skin and back feed wires to fixture from interior chase
Could be done that way, but not sure it would meet code. I prefer to do what we know will work
How do you mount and wire the exterior, wall mounted lights without a chase?  You have a chase on the inside and wires are fed to the backside of the fixtures
Very respectfully,
Larry
Larry;
Not dumb questions at all, they were well thought out.
18 Nov 2007 10:00 AM
Posted By Jelly on 11/18/2007 8:47 AM
 Yes, just like nails in a conventional home pierce the barrier and wood, I don't believe that this would allow moiture to get behind the skin, if it did it would be even more catastrophic behind an OSB skin, wouldn't it?
If the foam inside then acts like a drainage plane, taking the moisture down to the bottom of the panel, then how does it get out?The foam is not the drainage plane, the steel skin is , as a precaution, weep holes are put in the base in case moisture would get in somehow
seagladeUser is Offline
18 Nov 2007 10:15 AM
Ready To Retire
I read this SIP forum daily for at least a year before I even built, you can learn a lot from others plus you learn about different Companys that you might not have found on your own.  So I'll pass this one along to you, I used their Steel SIP panels to build my own cottage.
JohnCujieUser is Offline
18 Nov 2007 10:49 AM
I agree that it would be good to have a source, other than the generous Mr. Kavala, to answer basic questions.  I think most questions have to do with interface with the other trades, not solely with the panels.
Some from me.  What depth firring is used for wiring?  Can the skins be pierced for a 2 1/2" deep electrical box? I assume all boxes on the metal are metal.  Is all the wiring in cable?  Regarding exterior stucco:  Can foam for synthetic stucco be stapled on?  If conventional three coat stucco is used, how are paper and wire attached?  I know that interior wood trim can be shot onto light gauge metal studs.  Is this also true for this product?
John
I e-mailed Metals, USA with some basic questions about their product SIPbloc since their website had no mention of it.  One question was could they supply it to my area.  Got a reply from a marketing rep that they would have to research and get back to me.  Doesn't give you much confidence. Do they even manufacture it, or just sell someone else's product?
DonaldsonUser is Offline
18 Nov 2007 11:06 AM
RTW,
I had the same questions as you have and none are dumb. I am not a builder but a DYIer and can only give what we did. CK did my shell for me and what I learned watching and helping, ( or getting in the way) was more than valuable information. I don't have an answer for the thermal bridging, What I do know is that here in Central Florida although brief we do get temp in the freezing range for a couple of weeks long enough for my heat to run and keep the house a toasty 75. This would seem to be long enough for the condition to at least show itself and I have had no evidence of such. My wife is Canadian and I do know that they use steel sips in Canada.
Foundation connection: Yes the panel is fit into a channel that is in my case bolted to the concrete slab. This is a very tight fit and a little 50 year caulking goes a long way. You can also use 10 year tape, (what goes around your window on the outside) to cover that joint if you feel the need. If your siding is attached properly this isn't an issue.
The plate channel depending on code in you area is attached with 1/4" or 1/2" cement crews or red heads. Our Duplex used a 1/2 in screw that was five inches long with a big 3/4 hex head. Drill the appropriate hole and with a simple power driver screw it in every 2' . Simple enough. The panels are attached with #8 self taping screws. You should be able to completely tool up for steel sips for under $500.
Joints are slid, snapped, pushed what ever you want to say. WE just pushed the one panel into the next panels on the duplex (see previous post) and then using a 2 X 4 and a small sledge gave a little tap at the top and bottom to make sure of snug fit then move on to the next wall section section. Basically with two guys screwing the panel to the tract. by the time we screwed the panel all the way across the next panel was in place on the long wall runs. Four or five guys can put up a long wall very quickly.
E-mail Chris Kavala and he can give you the technical engineering on the racking and compression strengths.
When you come to a partial panel or say a header panel that fits over a window we put one screw in the top at the joint to hold it in place, then snap the next panel in to it. It will hold fine until you put the cap on across the top. In the case of my two story house where a window opening was on the first floor and then a 15' panel went above it you can make a simple brace out of channel about ten inches long cutting across the flanges in the middle and bending into a 90 degree angle. This would fit at the top of the window opening in the corner and screw to the panel hanging above and the one next to it. That is all the hanger you need. When you screw the top plate across you can even remove the hanger and the panel will hang there as you line the inside of the window opening with channel to complete the window opening process.
I mounted my cabinets to my sip wall very simply. between the high hat furring strip I screwed 2 X 4 to the panel along the line that my cabinet maker said was his screw line. He then had a solid line of 2 X4 or firring strip. I have the extra tall cabinets that are very heavy, all 5/8 solid plywood, no plastic or press board.
Dry wallers have been using a self taping DW screw for years to go into the metal framing studs, it is the same screw. My DW crew didn't have any problems putting up 350 boards of 12 ft DW in two and half days hitting the firring strips.
All electrical can then be ran behind the drywall clipped screwed to the skin. For the door bell or out side lighting the electrical is ran behind the drywall and then drill a hole to take the wire outside at the appropriate spot. My door bell, front door lights Spot lights around the roof line all have a little hole to the outside, I ran the wire through a piece of old garden hose to protect from the edges of the metal skin and then spray can foam the hole to fill in any space. You have to check the code in your area to see if the baseboard molding can be used, it is not acceptable where I live.
Jelly, If moisture is getting to the screws of the roof panel or siding then it was done improperly. I used a Gearard roofing shingle that is gal metal impregnated with stone. This has a 50 year unlimited non pro-rated warranty on it. The screws are hidden and covered in an unbelievable effective way so much that at a hip and valley test they used a fire hose for one hour with no moisture penetration. The fire hose did chew away the facial board though, it was on CC. A friend of mine did one thing better to his roof. He used 90 lb self stick roofing as his under-layment beneath his steel roof and the sip skin. Any screw is automatically sealed by the self stick as it goes into the steel skin. The roofing I used was about twice the cost of the best asphalt shingle, but I figured that I would roof once in my life time and never have to again.
I can't answer about siding as I just painted my outer skin with elastomeric paint designed for that purpose. One day I hope to hardi-plank the house but I am short on $ right now.
I hope this helps answer some questions. I would be glad to send via e-mail pictures as I can't seem to get my pic's small enough to post.
18 Nov 2007 11:48 AM
Posted By JohnCujie on 11/18/2007 10:49 AM
1-1/2"
They can be, but by using the 1-1/2" strips you can fasten a standard 4" square x 1-1/2" box with a 1/2" plaster ring directly to the skin
metal is a better for grounding  but plastic is perfectly acceptable and avialable as well in the 4 sq. box
it can be, but romex meets the code, even in commercial work
No, but screw attachment is common
Waver head screws are used and is code accepted
That correct, a standard pnuematic trim nailer will pierce light gage framing
John
RE: Metals USA, it is my understanding Metals Usa is no longer producing their panels for  residential use.It is also my understanding that they have scaled back production to just aluminum skin panels for patio use only
18 Nov 2007 12:15 PM
Thank you for your typically useful answers.
I viewed OSB SIPs as interchangeable units from vendors of varying quality and support; I'd misapplied that simple model to steel SIPs.  And it's good to know that thermal breaks are available -- that would solve the issue on the edge caps.
Having been bitten more than once, I've become a believer in the KISS principle -- which is one of the advantages that I see in SIPs:  they markedly simplify the shell structure.  So it would be nice to avoid the complexity (as well as the material and labor costs) to build out the chase over the entire surface; but I can understand that it is a trade-off for increased labor and materials in wiring along the external shell.  My wife and I have seen and like the looks of bases with outlets in them, so, for us, that's not a problem.  I can see that the OSB approach with set horizontal and vertical chases might not translate well to steel skins.  But:
Are internal chases available as an option -- for example for switches by entry doors?
Are there reasons NOT to cut a chase into the core of a steel-skinned SIP?
Would there be a structural or durability issue with cutting a vertical chase into the core, cutting a horizontal chase to the edge and across the header section, installing penetrations from the outside to those chases, cutting an opening the size of a switch box (assuming that it's 5-6 inches from the door opening), and fishing that short stretch?  (It sounds like a lot of cutting, but it would all be internal except for the penitrations at the lamps (which are needed anyway) and the hole for the switch box.)
VERY respectfully,
Larry
18 Nov 2007 02:27 PM
Posted By cmkavala on 11/18/2007 9:52 AM
I guess that would depend on the type(manufacturer) of SIP. The manufacturer that we use has both a horizontal and vertical chase in each panel, and at their junction a prerouted box hole is placed. Just knock it out with a hammer.
It would be hard to imagine that using this system would take an electrician any longer than the standard of having to drill a hole through every stud and pull the wire. In fact some electricians have told us that the system is easy to wire. And, if we need a custom chase, we just ask for it.
18 Nov 2007 02:45 PM
Posted By ReadyToRetire on 11/18/2007 12:15 PMI viewed OSB SIPs as interchangeable units from vendors of varying quality and support; I'd misapplied that simple model to steel SIPs.
Larry,
Unfortunately that 'simple model' does not apply to OSB based SIPS either. There are differences, and one of the most important is the connection between panels(How easy is it to obtain an air tight seal?). They are not all equal.
Having been bitten more than once, I've become a believer in the KISS principle -- which is one of the advantages that I see in SIPs:  they markedly simplify the shell structure.  So it would be nice to avoid the complexity (as well as the material and labor costs) to build out the chase over the entire surface; but I can understand that it is a trade-off for increased labor and materials in wiring along the external shell.  My wife and I have seen and like the looks of bases with outlets in them, so, for us, that's not a problem. There is no depth behind the base for the outlet or wire? I can see that the OSB approach with set horizontal and vertical chases might not translate well to steel skins.  But:
Are internal chases available as an option -- for example for switches by entry doors?No they are not available on anything I have used
Are there reasons NOT to cut a chase into the core of a steel-skinned SIP? The manufacturing process with steel is different and not practical to do that
Would there be a structural or durability issue with cutting a vertical chase into the core,No
 cutting a horizontal chase to the edge and across the header section,Yes, your header wether steel or OSB would be compromise if you were cutting the skin to put in the chase installing penetrations from the outside to those chases, cutting an opening the size of a switch box (assuming that it's 5-6 inches from the door opening), and fishing that short stretch?  (It sounds like a lot of cutting, but it would all be internal except for the penitrations at the lamps (which are needed anyway) and the hole for the switch box.)There is no problem with cutting in as many boxes as you want, even close to the door
VERY respectfully,
Larry
People Online People Online: Visitors Visitors: 166 Members Members: 0 Total Total: 166
