Posted By j.e. on 08/30/2007 11:07 AM
Kinda like what a stickler for details you are...
Planned anatomy of floor in basement over (existing) dirt:
1. gravel (or Item 4 crushed stone)
2. foam board insulation (will probably opt for 4")
3. vapor barrier
4. rebar
5. radiant tubing
6. 4" slab
Thanks, again.
Thanks for the info. You'll want the vapor under the insulation. Consider using fiber reinforced concrete and do away with the rebar. It's easier, cheaper, and plenty strong enough. Fasten the pex tubing to the foam board with special staples or holders that screw into the foam. I don't recall the names of them but you should be able to find them. One place for info is ZurnPex.com.
Poughkeepsie, NY is somewhere near the border of climate zones 5 & 6 in the moist region of the country. In other words, you're in a cold, damp climate when it comes to heating.
Now, the exposed brick. Maybe you already have done this, but think really, really, hard about leaving the brick exposed. The single biggest reason you shouldn't leave it exposed is heat loss. Those brick walls will be cold in the winter. Since you're using hydronic you surely must have a good understanding about the radiation part of radiant heating. Well, it applies to cold also. Those cold walls will suck heat right out of the floor, the furniture, the interior walls, and especially you and your family. I had a house just south of Pittsburgh in the early 70's. The first floor was clay tile construction with stucco on the outside and plaster on the inside. In the winter you could just feel the heat radiating from your body to the cold walls. I think there are two possibilities that may make it feasible to leave the brick exposed. If you have, or can apply, a good insulated siding system on the outside and/or if you can fill the air gap between the layers of brick with foam you may be able to cut the heat loss down to a manageable level. But to have a really good energy efficient home you should consider a stud wall inside the brick wall sealed tight and stuffed full of insulation.
Another thing to consider. If you have a high heat loss your hydronic system needs to pump out that heat. You may run into a problem with having to either have your tubes close together, like maybe 6" or closer, in order to keep the temperature and water flow rates reasonable, or you may end up with uncomfortably hot floors as the system tries to pump out the heat necessary with higher temperature water. Another option for keeping the brick is forget the in-floor heat and
place radiators or baseboard heaters on the outside wall. That way you
can really crank the heat up and warm up the air that sweeps down along
the wall.
Seal the dickens out of the house. Since you have the interior exposed now is the time to look for every crack and hole where outside air can come in, and seal it. Consider foam insulation on the underside of the roof. The heat loss through an insulated roof and sealed and conditioned attic is about the same, or less, than through an insulated ceiling under a vented attic. When you seal the house really tight, you will need to add a mechanical ventilator. A heat recovery ventilator will keep you from pumping too much heat outdoors.
Have you done, or had done, a heat load calculation for your house? If not, you really need to do it. A good HVAC contractor can do it for you and give a listing of heat losses by floor and room. If you want to do it yourself get HVAC-Calc. You can use it for 2 months for $49.95. I've used it and it's pretty good but doesn't provide nearly as much detail in the output. But you can input different scenarios for wall construction and insulation and get a real good idea of how much heat you'll lose with inadequate insulation. You then need to convert the heat load room by room into the tubing layout. Tubing layout requires considering spacing, tube diameter, water flow rate, and water temperatue. There's a limit to each one.
If you do end up changing out your boiler, and have yard space available, consider going to a geosource heat pump. That way you can cut the cost of heating in terms of Btus of energy you buy, to about 1/3 to 1/4 of the total heat load.
Whatever you do, try to stay away from electric heat, including electric radiant mats. Electricity is just about the most expensive energy source there is, unless you run a heat pump with it.
That's enough for now. If any of this is old hat and you've already thought it all out, please say so and forgive me for going overboard. You did ask for advice, and my approach is to make sure the cake has been baked properly before we start discussing the icing! :-)
For more info go to BuildingScience.com. There's a lot of good info about building for cold climates there.