Siegenthaler recommends the following MINIMUM R-values: Slab-on-Grade Floors: Rmin = 0.125(Ti - To) Floors over heated spaces: R-11 Floors over partially heated basements: R-19 Floors over unheated spaces (e.g., crawl spaces or unheated basements): R-30 Sounds like you may be closer to being unheated than partially heated... Fiberglass batt is a fairly common way to accomplish Above-Floor or Below-Floor tube & plate system insulation. For a unheated space, you may want consider using a vapor permeable barrier under the batt to prevent trapping condensed moisture. To optimize the insulation economics, you might want to do a floor heat loss analysis with the objective of determining what R-value will keep the downward heat loss just under 10% of the upward heat gain required to meet your building/room heat loss analysis requirements for your climatic design conditions. |