Secondary Pump
Last Post 06 Feb 2017 10:36 PM by sailawayrb. 4 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
kitdavisUser is Offline
New Member
New Member
Send Private Message
Posts:9

--
06 Feb 2017 08:26 AM
As the result of some good advice on this forum, I am replacing my current heat source (hot water tanks) with a NextGen boiler system. I have done the math and my flow and head requirements are a bit higher than the built-in pump is capable of delivering. This is not a problem, since there is a relay for a supplementary pump built into the system. However, I am a bit uncertain about how to now calibrate the flow using a second pump. Am I correct that I only need to concern myself with configuring the secondary pump so that it is able to deliver water at the needed flow rate against the system head, and that the primary pump does not enter into the overall flow calculations? Certainly, the number of gallons of water delivered by the pumps can not exceed the capabilities of either pump, but does placing two pumps in series overcome any additional head? Thanks
PARAHOMESUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:199

--
06 Feb 2017 02:09 PM
Where are you finding the best price on the NextGen? As soon as I have some time I'll look at this with you, if nobody else does. Do you have a schematic of your system? "Am I correct that I only need to concern myself with configuring the secondary pump so that it is able to deliver water at the needed flow rate against the system head, and that the primary pump does not enter into the overall flow calculations?" I think this assumption is correct but a diagram & your calcs would help be sure.
sailawayrbUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2283
Avatar

--
06 Feb 2017 09:20 PM
You need to know your system hydraulic friction head at your required flow rate to generate your required heat gain at your outdoor design condition. You can determine that by using the hydronic radiant floor heating design software on our website or some other similar software. Basically, when you place pumps in series, the heads of each pump add. When you place pumps in parallel, the flow rates of each pump add. So what you need to do depends on whether you need to generate more head or more flow rate.Yes, NextGen is a great HR appliance when an electric fuel source makes economic sense.
Borst Engineering & Construction LLC - Competence, Integrity and Professionalism are integral to all that we do!
kitdavisUser is Offline
New Member
New Member
Send Private Message
Posts:9

--
06 Feb 2017 09:39 PM
Thanks for the clear explanation. So, in practical terms, if I have a system that requires 4G/min at 12 feet of head, and I have two pumps each with three speeds . The best the pump can do on speed 3 is 4G/M at 10 feet of head. and on speed 2 it can pump 4G/M at 6 feet of head. Therefore I would put the two pumps in series and rum them both on speed 2, to achieve 4G/M and overcome 12 feet of head? Conversely, if speed 2 could produce 2 G/M at 12 feet of head then I could use both pumps in parallel to achieve the same thing? Additionally, if the pump can produce 4 G/M at only 2 feet of head on speed 1, I could put both pumps in series and run one on speed 1 and one on speed 3?
sailawayrbUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2283
Avatar

--
06 Feb 2017 10:36 PM
Yes, your thinking is indeed correct. You might want to get a couple pumps from NextGen. You could use one as your secondary and the other as a spare. In fact, you can buy a spare parts kit from NextGen that contains several other components in addition to the pump.
Borst Engineering & Construction LLC - Competence, Integrity and Professionalism are integral to all that we do!
You are not authorized to post a reply.

Active Forums 4.1
Membership Membership: Latest New User Latest: croccohvacusa New Today New Today: 0 New Yesterday New Yesterday: 0 User Count Overall: 35027
People Online People Online: Visitors Visitors: 540 Members Members: 0 Total Total: 540
Copyright 2011 by BuildCentral, Inc.   Terms Of Use  Privacy Statement