New Member
Posts:2
18 Feb 2008 04:26 PM
My house is 3000sq. log 14"diam. lots of windows & open loft. HVAC contractor installed a 3 ton unit. said it would be big enough for this house. We have a ground loop system. It runs most of the time with not much heat production. Would a 4 ton unit heat and cool this house right. In theory without knowing the heat loss factor. or do I need a larger unit. What do you think of the climatemaster units
Palace Geothermal
Veteran Member
Posts:1609
18 Feb 2008 04:42 PM
Before you can tell what size heat pump is needed, you need to know the heat loss of the structure. If you don't know the heat loss, you can only guess. If the heat pump is not keeping the house warm, then either the heat pump is the wrong size or not working properly.
There is no way to know with the little bit of info you have given us.
Climate Master makes good units.
What is the coldest outside temp in your area?
Is your heat pump one or two stage compressor?
Dewayne Dean
<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
csvb
New Member
Posts:2
18 Feb 2008 08:13 PM
Live near Dayton, Oh it gets 10-20 outside. single stage unit. was a 3phase converted to a single phase compressor. I would say our heat loss is avg.
Palace Geothermal
Veteran Member
Posts:1609
18 Feb 2008 09:56 PM
heat loss is given in terms of BTU/h, not average or more or less.
A heat loss report looks like this:
Attachment: with floor insulation.pdf
Dewayne Dean
<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
Palace Geothermal
Veteran Member
Posts:1609
18 Feb 2008 09:57 PM
Once we have a heat loss number, then we can tell you if your heat pump is undersized, but not until.
Dewayne Dean
<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
tuffluckdriller
Advanced Member
Posts:630
21 Feb 2008 01:00 AM
Log homes are always higher heating loads. They have a higher infiltration rate. Just based on the fact that you have a log home and the square footage, I can't imagine that a 3 ton unit would be large enough. However, geodean is exactly right. We have to start with an accurate load calclulation.
Clark Timothy (
[email protected]
)<br>Geothermal Heat Pumps: Heating and Cooling that's Dirt Cheap!<br>www.pinksgeothermal.com
You are not authorized to post a reply.
Green Building Forums
--General Forum - Residential
--General Forum - Commercial
--Green/Energy-Efficient Design and Planning
--Green/Energy-Efficient Building and Construction
Green Building Technologies
--Insulating Concrete Forms (ICFs)
--Structural Insulated Panels (SIPs)
--Radiant Heating
--Geothermal Heat Pumps
--Solar and Wind Power
--Windows/Doors and Interior/Exterior Finish
--Appliances, Lighting and Kitchen/Bath Fixtures
Feedback/Support
--Rules, Instructions and Announcements
--Suggestions/Feedback
--Testing Area
Forums
>
Green Building Technologies
>
Geothermal Heat Pumps
Active Forums 4.1
Membership:
Latest:
croccohvacusa
New Today:
0
New Yesterday:
1
Overall:
35027
People Online:
Visitors:
170
Members:
0
Total:
170