Hello,
I am seeking input from installers who have installed and home owners who have and are using desuperheaters with their geothermal systems. Have you been happy with the performance of desuperheaters and are you seeing energy savings during winter and summer, when the heat pump runs.
I have a Climatemaster Tranquility (2 Stage 64,000 max btu, closed loop) that was installed about 5 months ago. The system came with a desuperheater even though I did not pay for it. Long story. Dealer damaged the original pump during delivery. The contractor, in order to keep with the installation time line, bought another pump which came with a desuperheater. The contractor took the hit on the extra cost.
I would like to pay the contractor for the desuperheater, if I have it hooked up in my house. I would only like to have it hooked up only if there will be significant energy savings.
I live in South East Pennsylvania. I currently have a Bosch tankless water heater that runs off propane. We use about 150 gallons of propane/yr for hot water.
The plan would be to hook the desuperheater to a "non energized" water heater (reservoir), which would feed the tankless water heater.
Any input would be greatly appreciated.
Thanks and best regards,
VK |
|
|
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 29 Mar 2008 07:24 PM |
|
 The attached chart shows the output of the desuperheater on your unit under the HWC column. Basically you get between 1500 and 4000 btuh of hot water heating capacity when your heat pump is running. When you are cooling your home, this is free heat. If you don't put it into your hot water, it goes back into the ground. When you are heating your house, your are getting this heat about 1/4 the cost of heating the water with propane. You could realistically plan on saving at least 50% maybe 75% on your hot water heating bill. Hope this helps |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
tuffluckdriller
 Advanced Member
 Posts:630

 |
| 29 Mar 2008 11:58 PM |
|
How much would you have to pay for the desuperheater? |
|
| Clark Timothy ([email protected])<br>Geothermal Heat Pumps: Heating and Cooling that's Dirt Cheap!<br>www.pinksgeothermal.com |
|
|
jvk
 New Member
 Posts:29
 |
| 30 Mar 2008 04:16 PM |
|
Geodean,
Thanks as always.
What happens when the heat pump is "maxed" out in stage 2 during the coldest days of the year. Will it still output heat to the water reservoir?
Tuffluck,
I believe a total of $750 - $350 for a water heater and $400 for the desuperheater. If the savings is as shown in the Climatemaster data sheet, the cost may pay for itself over the years.
I will look at the data more closely.
Best regards to all,
VK |
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 30 Mar 2008 04:35 PM |
|
Posted By jvk on 03/30/2008 4:16 PM
What happens when the heat pump is "maxed" out in stage 2 during the coldest days of the year. Will it still output heat to the water reservoir?
VK Yes. The function of a desuperheater is to take some heat out of the super heated freon before it goes to the air heat exchanger, hence the name desuperheater. So the water always gets a portion of the heat before the air is heated for the house. So on days when your heat pump runs the longest is when you get the most hot water. If your heat pump is running 24 hours a day trying to keep the house warm, it might make sense to turn of the desuperheater and send the heat into your house instead. How much does propane cost in your area?
|
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
Eric D
 Basic Member
 Posts:104
 |
| 30 Mar 2008 08:00 PM |
|
VK,
Most unit will turn off the desuperheater pump when 2nd stage of the compressor is called for.
You may want to look at the Marathon brand water heaters by Reem. They are low heat loss tanks. With my desuperheater and the Marathon 85 gallon water heater, the electric elements almost never need to turn on during the winter months.
The efficiency of the tank-less systems is a little deceptive in my opinion. They never take into account the air drawn from the inside of your home to use for combustion. This has to be replaced with unheated air from outside. Take into account the btu loss of this replacement outside air into your home is much like leaving a window wide open in the middle of winter. You will see the biggest savings by switching to the desuperheater and a low loss water heater. |
|
| Eric D<br>Southern Michigan |
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 30 Mar 2008 10:02 PM |
|
Posted By Eric D on 03/30/2008 8:00 PM VK,
Most unit will turn off the desuperheater pump when 2nd stage of the compressor is called for.
Climate Master and Hydron do not turn off the desuperheater on 2nd stage. Which units do you know of that do this?
|
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
jvk
 New Member
 Posts:29
 |
| 31 Mar 2008 09:12 PM |
|
Thanks again, Dewayne.
I own my own propane tank and so I get a discount. But the last time I checked prices ( in January 2008) I was being quoted a price of $2.40/gallon.
Eric, Thanks for your input.
I already own a Bosch tankless heater. It currently takes in air from my basement but when I have it set up with the desuperheater, I will make sure that the air for combustion is drawn from the outside. It is not a bid deal in my case because just a few months ago, I used to have a high efficiency propane furnace that was drawing air from the outside. I made sure that geothermal installer left the PVC line available for air intake for the hot water heater. The flue gas from the heater will exit the house via Z-flex lines.
On another forum HVAC installers have been recommending the Marathon water heater as the reservoir to which the desuperheater loop gets connected and the resutling heated water gets fed to a tankless water heater.
Marathon water heaters have a life time warranty, which is great. But the price is a bit much when you are only going to use it as a holding tank.
Best regards to all,
VK |
|
|
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 01 Apr 2008 10:51 PM |
|
The incremental (extra) cost of a Marathon tank over a standard electric water heater tank will likely never be recovered over the lifetime of a typical system. I have a 3 ton Waterfurnace Envision in the process of being piped to an 80 gallon GE 12 year warranty waterheater as a holding tank. I looked at the Marathon 105 gallon units but the additional cost (double +) couldn't be justified.
A 2nd 8- gallon GE water heater will serve as my primary hot water supply.
While comparing fuels beware that a gallon of propane ( ~4 llbs / 92,000 Btu) compares poorly against a gallon of fuel oil ( ~7 lbs / 130,000 Btu). In some localities it even compares badly against a KiloWatthour (3413 Btu), depending on costs of electricity vs Propane.
There's been much ballyhoo regarding tankless water heaters avoiding the standby losses of a standard storage tank water heater, but the reality is that standard electric storage water heaters are or can easily and cheaply made to be 95% or more efficient.
A gallon of propane burned in a conventional center flue domestic water heater (~60% efficiency) is a particularly miserable combination. Tankless units improve the math somewhat, but it is always required to compare fuel cost per unit, Btu content per unit, and heater efficiency to reach an informed decision as to what to choose.
Hot water from a desuperheater is cheap in winter and free (or better) in summer, assuming proper execution with a dedicated preheat tank. Without a dedicated preheat tank a desuperheater is nearly worthless.
By 'free or better' during summer I mean that a properly executed desuperheater can actually slightly reduce summer cooling costs by removing heat from, and thus decreasing head pressure and current drawn by an airconditioning compressor. |
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
Eric D
 Basic Member
 Posts:104
 |
| 03 Apr 2008 09:38 PM |
|
Posted By engineer on 04/01/2008 10:51 PM The incremental (extra) cost of a Marathon tank over a standard electric water heater tank will likely never be recovered over the lifetime of a typical system. I have a 3 ton Waterfurnace Envision in the process of being piped to an 80 gallon GE 12 year warranty waterheater as a holding tank. I looked at the Marathon 105 gallon units but the additional cost (double +) couldn't be justified.
Engineer, The above maybe correct for you, but not for everyone. Some folks have an incredible deal on the Marathon if they check with their utility company. Here is an example. TriCounty Electric CompanyEven without the super deal from the utility some folks can take a credit on their taxes for part of the cost. There are many other advantages to this tank as well. The fact that it doesn't have an anode rod makes it great for use with well water. I'm glad to hear your system is working well for you. Regards, |
|
| Eric D<br>Southern Michigan |
|
|
jvk
 New Member
 Posts:29
 |
| 03 Apr 2008 09:52 PM |
|
Eric,
That is a great rebate from the utility company. With that rebate the Marathon water heater could cost less than what I would have to pay for a standard water heater. I wonder what is the driver for a utility company to offer such a good rebate - what gain could they possible get?
Unfortunately, I live in SE PA and our utility company does not offer such rebates.
Engineer,
Your point is well taken about propane and tankless water heaters. However, I am stuck with propane and that is why I went with a geothermal system.
Several years ago I invested in a tankless water heater. Now all I have to do is buy a storage tank for my desuperheater.
Best regards to all,
VK |
|
|
|
|
Eric D
 Basic Member
 Posts:104
 |
| 04 Apr 2008 06:52 AM |
|
VK,
I don't know all the details, but I have been told that a lot of these savings are government mandates to the utility companies to promote energy savings initiatives.
On a different subject a friend was telling me that here in Michigan, the state government has put in place a buyback of power from the utility companies of electricity at nearly four times the cost, if you supply them from a wind powered generator system. Again, I don't know all the details, but I'm planning on checking this out. Hey, maybe I'll be putting up a wind generator!
Regards, |
|
| Eric D<br>Southern Michigan |
|
|
bmwphd
 New Member
 Posts:7
 |
| 13 Jul 2008 09:25 AM |
|
Posted By engineer on 04/01/2008 10:51 PM
Hot water from a desuperheater is cheap in winter and free (or better) in summer, assuming proper execution with a dedicated preheat tank. Without a dedicated preheat tank a desuperheater is nearly worthless.
By 'free or better' during summer I mean that a properly executed desuperheater can actually slightly reduce summer cooling costs by removing heat from, and thus decreasing head pressure and current drawn by an airconditioning compressor. Engineer, Could you please help me understand how a preheat tank helps with the desuperheater? Thank you.
|
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 13 Jul 2008 10:41 AM |
|
Posted By bmwphd on 07/13/2008 9:25 AM Engineer,
Could you please help me understand how a preheat tank helps with the desuperheater?
Thank you.
This has been explained several times on this board. Do a search for desuperheater and you can read all about it. |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 13 Jul 2008 11:20 AM |
|
I 2nd the motion. |
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
bmwphd
 New Member
 Posts:7
 |
| 13 Jul 2008 12:50 PM |
|
Engineer,
You mentioned having two 80-gallon tanks after the desuperheater. What is the capacity of your GHP?
I am considering a three-ton dual-stage Envision and I wold like to use my existing 66-gallon heater as a storage tank. How should the powered tank be sized relative to the storage tank?
Thank you.
|
|
|
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 14 Jul 2008 12:19 AM |
|
My Envision is an 038 2 stage (nominal 3 ton), though so far I've kept stage 2 locked out and meet cooling setpoints on days as high as 94 Deg F, which are 'design' days. I probably could have gotten by with the 2.5 ton, but my builder urged me to oversize by 1/2 ton in case I ever lose my open loop artesian well water (enters at 70 deg F) and have to resort to a closed loop system whose entering water temps would be in the 90s, substantially reducing unit capacity. I took his advice. The 3 ton unit is the most efficient size, and the thermal mass of my ICF house increases runtime in the wee hours of sultry nights, substantially improving dehumidification without true 2 stage operation.
Powered tank should be no larger than necessary to meet household needs at peak time of use, typically when multiple showers are taken at around the same time. My 80 gallon powered tank may be too large, but it was cheap ($400 with a 12 year warranty) and I wanted to be able to accommodate house guests and a future 3rd bathroom, big master bath soaking tub and future teenagers taking long showers.
Oversizing the powered tank incurs slight penalties in efficiency - energy factor in the low point 90s rather than mid point 90s owing to larger surface area losing more heat.
Powered tank can instead be a tankless unit. I don't particularly favor them for reasons I've described in other posts, but they have their advantages of small size and efficiency.
Preheat tank should be as large as feasible, but ideally at least as large as needed to hold a day's use of hot water. The reason for this is to fully connect periods of heat recovery (late afternoon during summer, late at night in winter) with next day's periods of peak hot water use. In other words, I don't want inlet water to the powered tank to have missed out on the previous day's desuperheat whether it be during a hot summer afternoon or a cool winter night. Undersizing the preheat tank will cause some inlet water to the powered tank to not be preheated, somewhat defeating the purpose of the system.
66 gallon is probably a reasonable size for preheat on a 3 ton. The Cadillac tank would be a Marathon 105 gallon tank, but payback time for one would likely be decades, if ever. |
|
Curt Kinder <br><br>