Posted By TechGromit on 04/13/2008 12:27 AM
Posted By engineer on 04/12/2008 10:53 PM
The problem with open loop using a typical well pump is that power consumed by the pump approaches or exceeds that of the compressor. Well pumps are both inefficient and operate at pressure way above that needed by a geo heat exchanger.
Result - really expensive system (compared to air source) with same or greater operating costs compared with air source....why bother?
Complete BS! Geothermal Water source open loop system are way more efficent than air source heat pumps. When the temperature gets too cold an air source heat pump no longer operates and you have to rely on the backup heat only, also the air source heat pump has to go into defrost mode to keep the system from freezing into a block of ice. While the water pump and compressor on an open loop system use a lot of electricity , when compared to an air source heat pump, it's at least 2 times more effiecent. Admitly a DX Closed loop system is the most effiecent system, it's also the most expensive to install.
I found an excellent site that help you figure out how much you will save by switching from one heating system to another.
http://www.energyexperts.org/fuelcalc/default.aspI fully understand the arguments in favor of geothermal vs air source. I stand by my contention that many pump-and-dump systems do not deliver the efficiency improvement owing to well pump power consumption. Two reasons:
1)Geo systems need only a few pounds (or feet of head) across the waterside heat exchanger to produce the required flow, but well pumps provide water at much higher pressure. Pumping water at, say, 40 psi and then throttling it across a valve down to 5 psi or so is a substantial waste pf power
2) Typical well pumps are at best approximately 50% efficient, owing to small size and cheap construction. This effectively doubles the throttling loss in #1 above.
We had a thread awhile back concerning a homeowner with an open loop geo and high power bills and we collectively ascertained that the well pump power use was the culprit.
I happen to have an open loop geo system, but it is connected to an artesian well with sufficient natural pressure to drive water through the heat exchanger. I selected a Waterfurnace Envision unit in part owing to its much lower waterside head loss. It is more efficient than a closed loop system since the open loop water temperature is cooler in summer and warmer in winter than attainable by closed loop.
If an application uses pumped open loop water the best solution is a dedicated smaller pump optimized for the flow and pressure needed by the unit. That is probably not feasible in most applications. Other steps to take:
1) Minimize water flow consistent with unit efficiency, freeze protection, and scaling. My unit is allowed to go as low as 1.5 GPM per ton, which is about where I run it so as to minimize water use.
2) Reduce well pump pressure to minimum tolerable
3) Properly size the well pump - no larger than absolutely necessary.
4) Consider a higher quality, more efficient well pump - I suspect that a brand such as Gould, while more expensive than, say, Flo-Tec, will turn out to be quieter, longer-lasting, and more efficient.
Keep in mind that typical resi well pumps aren't designed to deliver the much greater daily load imposed by a geo system. An open loop geo, depending on time of year, could increase daily water use by a factor of 5 or more.