Do you think you have lost any efficiancy by keeping your propane system?
Frank,
The duct work in my home was over sized and works well with the geothermal arangment.
My system is quite different from the norm. The propane system and the geothermal unit are in parallel to the main feed plenum. I have ducting dampers that isolates the unit not in use from the duct work. The design has powered dampers being controlled through relays that only allow one unit at a time to function. The heating unit switch is made by selecting emergency heat from the thermostat. This shuts down the geothermal unit, switches duct dampers and activates the propane furnace only after the dampers are fully open.
After going through this last winter I have found that the geothermal unit keeps up just fine with the heating demands. The current plan is to leave the propane unit though it really isn't needed.
Posted By buymyemu on 04/20/2008 9:50 AM
Did you put the geothermal after the propane burner or on the return side?
On any split system the geothermal must be on the return side of the propane unit. The only other choice is a parallel system where one or the other heating unit is used.
Efficiency could be affected with a split system trying to circulate through the propane unit. This would add a lot of flow restrictions.