09 Aug 2008 12:37 PM
Bill,

Where can I get underground sensors?


Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
09 Aug 2008 12:55 PM

Dewayne, consider using the 'Ruggedized Temperature Probe' from http://www.embeddeddatasystems.com .

"The RTP temperature probe is designed for wide temperature range applications requiring excellent chemical resistant properties and sensor submersion."

"All exposed parts of the RTP are manufactured of either stainless steel, or Teflon based products, resulting in excellent chemical resistance properties to acids, alkalis, ketones, esters, aliphatics, aromatics, and outdoor exposure.  The probe is constructed of 304 Stainless Steel making it both durable and water resistant to 60 PSI.  The cable used on this sensor is Belden’s 7928A CAT 5, which uses Teflon based materials for both the outer jacket and inner conductor insulation.  This cable is particularly suited for harsh environments, and offers excellent resistance to high and low temperatures, oil, gasoline, and sunlight exposure.  The RTP probe is manufactured using a Teflon based heat shrink tubing that creates a water tight seal at the cable’s point of entry into the tube.  This results in a sensor that can be submerged beyond the top of the steel probe."

Downside to these sensors are cost ($50 each on retail basis) and teflon cable length limit is 12 feet.

Hope this helps.

Best regards,

Bill



Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
09 Aug 2008 01:41 PM
Bill, Thanks for the personalized help. How would I connect the teflon cable into the WEL?


Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
09 Aug 2008 04:04 PM

Dewayne, you're going to hook up 1-wire technology sensors to what I call a '1-wire network cable,' regardless of what kind of sensor it is (raw temp sensors, RTP sensors, RH sensors, etc.).

You'll locate your WEL at a place where it's easy to make a network (Ethernet) connection.

From the WEL, you'll have a '1-wire network cable' travel to wherever your sensors are.

Ideally you'll maintain a 'linear topology' - one '1-wire network cable' traveling around to sensor locations, with each sensor 'pigtailed' to the cable, with about at least a foot of distance along the '1-wire network cable' between sensor splices.

(The WEL's 1-wire interface is exceptionally tolerant of cable noise, though, and thus offers good accommodation of a '1-wre network cable' branch.  Make this your second choice, though, if you end up with a lot of sensors, or with long cable distances.)

The actual material for the '1-wire network cable' can range from CAT5 to simply a couple of 'bell wires.'  Generally you're only going to need 2 wires - signal and ground (RH sensors being the exception, where a 3rd wire is needed).  CAT5 cable will offer the best noise immunity - important, though, only in cases where there's a lot of sensors, or where there's a lot of distance to the sensors.  If using CAT5 cable, only 1 of the 4 wire pairs is used (generally).

For the RTP sensors, you'll need to have your '1-wire network cable' within 12 feet proximity.  Simply splice the RTP sensor wires as a 'pigtail' to the '1-wire network cable.'  I use small wirenuts to ensure a solid, mechanical, no-future-problems connection.  This splice connection will need to be someplace environmentally shielded (hence my earlier comment that only getting 12' of teflon cable could be a limiting factor, although you could purchase a spool of the Belden teflon cable to extend out the distance to sensor locations, with waterproof splice connections).

The image below is an example of a sensor connection to my '1-wire network cable.'  It was a first attempt to measure my EWT and LWT.

The gray cable is the CAT5 '1-wire network cable.'  A temp sensor is glued and mechanically fastened to the 2" HDPE pipe, and then is 'pigtailed' to the '1-wire network cable.'  Then, down a foot or so on the '1-wire network cable,' another temp sensor is 'pigtailed' to it.

It's actually more complicated to describe than it is to do it.  It isn't more than a 5 minute job to make the connection.

Best regards,

Bill


Attachment: IMG_10640.jpg

Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
FarmboyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:356

--
10 Aug 2008 12:10 AM
Pardon me for thinking out loud here. Theorectically, if the interior heat exchanger, ductwork, radiant floor system and exterior loop system are designed and installed properly, you should be comfortable and remain so with recommended filter changes and servicing. And the use of sensors would be an optional activity for the detailed or technically oriented homeowner. BUT...

several recent threads have proven the value of keeping tabs on key data to help troubleshoot suspected or outright sytem malfunctions. I suspect a compentent HVAC tech could gather much of this data at some labor rate, but would only be capturing snapshots with which to troubleshoot. How much better is it to have a relatively continuous "video" of the system. SO...

What would be the most important data to collect for the interior GSHP eqpt and ductwork, the loop, as well as, radiant floor heating and a desuperheater? A few key data seem to be Entry Water Temp (EWT), Leaving Water Temp (LWT), supply and return air temps and flows. Also is there some data that would require a different method to collect? I'm planning for radiant floor heating (primary), water to air cooling and a desuperheater with a vertical closed loop and am interested in installing sensors and monitoring performance.

Thanks to Bill, Engineer, Joe, Geodean and others for your thoughtful questions and educational responses. I would say several of the recent threads on loop temps, flow rates and related topics have been some of the best in this forum. I think you all should create a video and distribute it.
Dave


engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
10 Aug 2008 10:20 AM
Flows are harder to obtain.

I think another useful bit of info is current - either compressor or the whole system. ECM (variable speed) blower current might be useful to know when to change filters. If WEL had a cheap differential pressure sensor that would be particularly useful to remind of filter changes


Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
10 Aug 2008 11:14 AM

Farmboy, thanks for the comments.  There are many smart people here and I've learned a lot from them.

engineer, water flow is hard as a retrofit because of the effort required to put in a meter into already existing HDPE pipe.  For those that know, in advance of installation, that they'll have some kind of instrumentation system, like a WEL, insertion of a pulse-output flow monitoring device is pretty straight forward.  The WEL can accommodate pulse-output flow meters without difficulty.

As far as planning for optimal use of an instrumentation system, like a WEL, gosh, the 'sky is the limit.'  Take a look at http://welserver.com/ww/ for implementation ideas.  And 5 of the more advanced implementations are listed on the left side of the screen.  All of my implementataions can be seen at http://welserver.com/WEL0043/ .

Climate is the variable that largely affects how much heating/cooling load a residential structure has.  The WEL easily accommodates temp and RH measurement.  And Dew Point and Degree Days are easily calculated.

Heat that has to be added/removed from the home is the response to climate, and is the driver that influences cost of running HVAC equipment.  DeltaT temp across the water-to-gas heat exchanger is easily measured.  With a flow meter hooked up too, that gives you Heat of Rejection or Heat of Extraction on an instantaneous basis (KBTU/hr) or accumulated (KBTU).  (Since many GSHP implementations have a constant water flow, like me, you can accurately measure it by hand, and then use the WEL to do the calculation.)

Power/energy are very straight forward.  Just hook up the monitors where you want them.  Biggest downside to monitoring power is the cost of the monitors.

If you're monitoring HE/HR (above) and you have a power monitor on your GSHP unit, then you have opportunity to have COP in real time.  (I can do this by hand, but, can't do it real-time because I only have one power monitor for both of my GSHP units).

If you're skilled enough with HVAC, you can put in RH and temp sensors in the supply and return air plenums, and determine sensible and latent cooling capacity.

Air flow is straight forward if you have variable speed blower motors - designed to maintain a set cfm as filters, etc. get dirty.  And by measuring DeltaT across the evaporator coil, now you've got Sensible Cooling / Heating Capacities without difficulty with the WEL.

EER is tough to accurately get real-time because you need to know Total Cooling performance.  And this means you need to know the Latent Cooling performance.  I'm not aware of a 1-wire technology wet bulb temp sensor, which is what you'd need.  I do the calculate 'off-line,' and have to assume a Sensible/Total Cooling ratio that I look up in the specs to match up with my EWT.

There are many examples of WEL users monitoring their photovoltaic sensors and thus how much power contribution they're making to/from the grid.

Desuperheater performance monitoring is all quite capable with the WEL.

Putting sensors into the ground to facilitate monitoring water loop performance is straight forward.

WEL1000 is an example of radiant floor monitoring - see http://welserver.com/WEL1000/ .

Hope this helps stimulate some thoughts.

Best regards,

Bill



Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
17 Aug 2008 11:51 AM

Dewayne, congrats!  I see you're up and running with a WEL unit.

Looks like your water temp sensors are located in a conditioned place.

Best regards,

Bill



Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
17 Aug 2008 11:53 AM
Bill,

Could I ask you few questions about the WEL. Call me 801-573-3420 or I will call you if you post your number


Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
17 Aug 2008 06:45 PM
Wow-LATs around 40F - To get that in Florida you'd have to run maybe 150 CFM / Ton, long before which my evap would look like a glacier!

What do your outside air dewpoints run around this time of year?


Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
17 Aug 2008 06:49 PM
Posted By engineer on 08/17/2008 6:45 PM

What do your outside air dewpoints run around this time of year?

Sorry, but I have no idea.  How would I find out?


Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
17 Aug 2008 06:54 PM
Nat'l Weather service reporting points in your area, typically airports.

Here in the southeast, dewpoint is a little-known, but to me, immensely useful indicator of true comfort / discomfort.

Here in Jax it runs 24 / within a couple degrees of 73 for about 4 months per year, our hot humid summers. When it finally drops to 60 or so, this displaced Yankee is finally comfy outside again.


Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
17 Aug 2008 08:20 PM

My Leaving Air Temp for my 3 ton unit Envision WaterFurnace GSHP routinely averages 45°F, when running 1st stage.  Air flow is set at 750 cfm, which would make it 375 cfm/ton.  I believe WF accomplishes this by including in the Envision series a very large evaporator surface area.

Outside Dew Point for the Dallas area, at the moment, is ranging from 60+° lows (recent days) to 74+° highs (a couple of weeks ago, when it was blistering hot).  This is a commonly reported measurement on all of the weather channels.  Simply using http://www.weather.com , for Dewayne's ZIP, I see that at the moment it's 85°, with an RH of 17%, resulting in a DP of 36°.  This is weather we would never see in the Dallas area.

I too pay attention closely to DP, as I run outdoors a lot for exercise.  Many times, when I can, I choose my time of day to go out based on lowest DP.  Not surprisingly, it's in the late morning for me, when temperature is still low (relatively speaking) but RH has already been coming down.  This summer, evening time when the sun was gone, was still at a much higher DP temp than the mornings in spite of the sunshine.

I have DP charted on one of my WEL graphs for the past 20 days.  I'm using my outdoor dry-bulb temperature and outdoor RH sensor, and using the WEL to compute DP based on a formula from Wikipedia.  I'm consistently 5 - 6° higher than what the channel says for my location, but, at least it's consistent.  I don't know why I can't get DP numbers closer to actual.

I agree with engineer's comments on comfort related to DP.  If I had a GSHP that had a blower motor 'slow down port,' and I was an inventor, instead of the thermostat I'd use some kind of a 'Dewpointstat' to turn on/off my HVAC.  I know this is how it's done in commercial and industrial settings.

Best regards,

Bill



Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
18 Aug 2008 01:06 AM
Bill-

My understanding is that large evaporator coils tend to favor SEER at the expense of dehumidification. I learned the hard way not to run continuous blower across my 3 ton Envision's large 28x30 evap - it adds 8% or so to RH.

Dehumidification while the compressor is running is pretty much all dependent upon CFM per ton.

What is your entering air temp (never mind...I'll look at it at WEL...nearly 30 delta T).

I first began wondering a bit when you earlier stated you have RH in the low 40s - pretty low for dewpoints in the upper 60s.

I'm now a bit skeptical of 375 CFM per ton given the 30 deg Delta-T. Your waterside conditions uprate the 3 ton unit to 2.5 tons on low stage. I also wonder if you are really running 650 CFM instead of 750 at low stage - would need to consider fan speed dipswitch settings and whether dehu mode is selected. I know we discussed this before - don't remember details.

I guess another thing to consider is your substantial rest-of-house loads, 42 Kwh / day. Not sure what's causing that, but if most of is ultimately becoming heat in the building envelope then the AC has more load to work against, allowing it longer run time to drive down humidity.


Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
18 Aug 2008 09:50 AM

engineer:

I didn't know that large evaporator coils favor EER at the expense of dehumidification.  Given this, I think another way of saying this is that large evaporator coils increase sensible cooling capacity at the expense of latent cooling capacity - I didn't know this either.

My observation has been that I have pretty short cycling, which would normally be at the expense of dehumidification.  But, I'm able to average an indoor RH of 42% (last 30 days) in spite of this.  I have (perhaps erroneously) been attributing this to a lot of dehumidification in a short period of time due to what's pretty large for an evaporator coil.

Last year I too looked at running the blower continuously, like advertising suggests to do.  It doesn't work for my climate, just as you learned.  Here's a chart of what actually happens to the water in the coil, courtesy of a Lennox study: http://www.pbase.com/neukranz/image/88853062 , showing that the water in the coils becomes a significant latent addition when running the blower without the compressor.  And here's what my coil actually looks like right after a cooling cycle: http://www.pbase.com/neukranz/image/84712917 .  I shot this, thinking that the 'problem' was simply water sitting in the pan.  It's not - the coil is substantially loaded with water.

I didn't know that dehumidification capability is primarily dependent on CFM/ton.  I thought RH removal was also dependent on latent cooling capacity, evaporator coil size, and degree of cycling.

My Entering Air Temp averages about 77°F.

Dallas weather at the moment is 72°, 95% RH, and 71% Dew Point.  My indoor RH has varied from about 39 - 44% this cooling season.  It goes up when the GSHP units are not running, and goes down very easily when the units are running.  I don't have a very air tight home, further causing me to think that my Envision units' dehumidification ability is pretty strong.

I'm pretty sure on the blower motor speed setting - I set it to 750 CFM because I wanted to air balance the supply outlets at the highest air velocity, regardless of cooling or heating mode (750 is the minimum for heating). 

My 375 cfm/ton was arrived at by taking 3 tons * 0.67 (1st stage) = 2 tons, and dividing 750 by 2.  If in fact I'm running at 2.5 tons on 1st stage, then my air volume is 300 cfm/ton, further favoring RH removal.

Yes, an avg of 42 KWH per day for misc stuff usage seems pretty extravagant to us.  We were surprised to see how it all adds up.  During the day, when no one is home, and all lights and everything possible is turned off, we can get this down to 800 watts (about 20 KWH / day).  Almost all of this is heat contributing - particularly computers and computing equipment, and refrigerators.  Then add to this microwave, electric oven, entertainment items, etc.  At least we're a 100% CFL home now - that contributed about 12 KWH / day savings when we made this change.

Thanks for the note - interesting subject.  Nice to have a WEL to put numbers to the thoughts.

Best regards,

Bill



Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
BrockUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:599
Avatar

--
18 Aug 2008 12:34 PM
So, are the two of you saying you shouldn't leave your blower on continuously (or all of off peak time anyway)? I have found if I don't run it continuously the south west rooms will warm up and never really catch up cooling wise if the fan shuts off when not cooling.

Also what temp should the air leaving the furnace be? Could you figure out the CFM required that way? For instance with ours if I have the fan speed set to 2 (of 4) the leaving air temps are in the low 40’s with water temps in the mid 30's. If I set it for 3 I see leaving air in the upper 40's with water temps in the low 40's. If I set it on 4 the air temps are in the lower 50's with water temps in mid 40's.

I was told not to run the fan on 4 while cooling because it could cause water to blow off the coils. I never really knew if 2 or 3 would be correct for our system, the default is 3. I do notice more water running out when the fan is on 2 but since it is close to freezing I was worried about it actually icing up. I would think overall the faster the fan runs the more efficient it actually is, within reason.


Green Bay, WI. - 4 ton horizontal goethermal, 16k gallon indoor pool, 3kw solar PV setup, 2 ton air to air HP, 3400 sq ft
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
18 Aug 2008 12:47 PM
Posted By Brock on 08/18/2008 12:34 PM

... you shouldn't leave your blower on continuously



Yes, clearly, you shouldn't leave your blower on continuously, if, you live in climates like mine (DFW), or like engineer's (JAX), where RH can be a significant influencing factor on comfort.  If so, you will definitely add moisture into your conditioned air while the compressor is off.  See the references I provided earlier, above.

Best regards,

Bill


Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
BrockUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:599
Avatar

--
18 Aug 2008 03:13 PM

I did look at those, but if all the pumps are off I would think rather quickly the coil would come up to temp and dry off.  When it is cooling the coil is dripping, almost running water and that doesn't add any humidity to the house since it is water condensing out of the air and on to the coil correct?  Or is it because that water loaded in the coil could otherwise drain off and wouldn't be re absorbed to the home?



Green Bay, WI. - 4 ton horizontal goethermal, 16k gallon indoor pool, 3kw solar PV setup, 2 ton air to air HP, 3400 sq ft
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
18 Aug 2008 03:30 PM
Posted By Brock on 08/18/2008 3:13 PM

... if all the pumps are off I would think rather quickly the coil would come up to temp and dry off.

When it is cooling the coil is dripping, almost running water and that doesn't add any humidity to the house since it is water condensing out of the air and on to the coil correct?   ...


I don't know how long it would take for a coil to dry.  On a day like today, for me, where at the moment it's 78° ambient surrounding the GSHP units, 87% RH outside, and 43% RH inside, I would think it would take a good portion of the day for my coil to dry out, but I don't have any fact or data to support this thought.

Correct.  When the compressor is running, water is being removed, not added, to the air.

Best regards,

Bill


Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
19 Aug 2008 11:03 PM
I installed some sensors at the depth of my ground loop. The lines are just starting to show up on the graphs, but the values are posted on the top of the page in the system png.

I also added an out door air temp sensor. This is the most fun I've had for awhile.


Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system