Geo Heat Pump Help
Last Post 05 Feb 2010 09:19 PM by gregj. 46 Replies.
Page 1 of 3123 > >>
HeatlessInHarrisburgUser is Offline
31 Jan 2010 02:37 PM
I just got done building a new, single family home/home office/workshop a few weeks ago (I acted as Gen Contractor).  I love our new digs, but HATE the problems I'm having heating system.  You might say after lots of research, I designed the system and had a "contractor" install the mechanical components while I ran the radiant in slab/joist, properly insulated the slab/found walls/f. joists, etc.  The sad part is, if things were properly installed on the generation side, I don't think the design is the problem.  I tried to keep it as simple as I could for what I was doing so as not to confuse both myself and the installer (he mentioned toward the end of my project he was second to last in his HS class...I'm thinking the other guy probably committed suicide).  Sad part is, he wasn't cheap by any means...I paid extra to get him as he has the same system set up at his house, which made me believe he knew what he was doing!  The radiant flooring I designed/put in works great, but heat distribution isn't my problem as it worked great...generation is!  I've included some pictures of my problems:  http://pa-softball.com/junk/geo/Thumbnails.html
My design:
I have a 5 ton Climatemaster Tranquility 27 split for my cooling (forced air) and supplemental heating.  I have a 5 ton Tranquility 27 split w/ heat exchanger for radiant heating.  Radiant is designed to be my primary heating source down to about 10-15 degrees.  Both units have desuperheaters that dump heated water into a 160 gal buffer tank.  The radiant unit solely heats water in the buffer tank.  Each zone has it's own pump/thermostat/manifold and "talks" to a switching relay when it has a call for heat.  The radiant unit/buffer tank "talks" to an outdoor temperature reset and turns the unit on when the buffer tank temp drops below the reset temp.  My thermostats for the radiant "talk" to a switching relay...so there is no direct path between my thermostats and geo unit to tell it when to switch gears (stage 1 to Stage 2)...since I have a buffer tank, the plan was to always run it in stage 2.  Rather than bring another tank into the mix, my DHW is preheated via a 180' soft copper coil in my buffer tank, then goes to a Elec HWH.  I had a manual J done and my house, on the coldest day, would take 8 tons to heat every square inch (basement included as I put radiant everywhere).  I have a 8 ton horizontal, closed-loop field that comes into my mechanical room in a 2" sch 40 PVC, then a 1" supply/return goes to each pump pack for the units.  I only put 8 tons in as  the second unit should never get out of Stage 1 for supplemental heating, which would be running on roughly 3 tons of unit (60% of my 5 tons, give or take)
My problems are as follows:
- It appears that my contractor has both units set up currently to only run in stage 1.  My forced air unit is always right around 15 amps on each leg (220V).  I'm not a electrican, but am pretty such you draw 110V off each leg, so I'm only getting 15 amps of 220V, or roughly 3300W.  I'm thinking a 5 ton in second stage should be closer to double that, about 6000 Watts (which is what the owner's manual seems to suggest as well - ~25.5 amps @ 220V).  The 15 amps jives with the amount of heat I feel is produced.  I estimate my average actual heat loss on a normal day (20-25 deg) to be about 7 BTU/sq foot (roughly 28K for the house), which is roughly 3/5 the capacity of the system, which is what I believe it to be running on (stage 1).  3300W x roughly 10 BTU's per Watt (300% eff.) = 33,000 BTU's.  The radiant unit, when it worked, seemed to also be producing about the same amount of BTU's based on the deltas and flow of my 2 main manifolds (17 loops-6gpm total @ 10 deg Delta) = roughly 30K BTU's.  I would love to be able to get my units running in 2nd stage but his wiring inside the units is suspect.  First, he clipped the end of the second stage jumper off and wire nutted it directly to the "Grey" stat wire...that seems legit since "Grey" is in the "Y2" position on my stats, but the Y2 jumper was never connected to the circuit board.  I'm of the impression the blue, Y2 jumper is to be on the circuit board, so I just unconnected them and placed it on the board where I'm reasonably sure it belongs.  If I'm not mistaken, I also need a jumper between the Y2 on the board, and the Y1 to make it live?  Does this mean I run a connecting wire between the 2 blue stage 1/stage 2 wires?
- My radiant unit recently burnt up a pump that he has between the unit and my buffer tank.  The tank is atmospheric pressure (not pressurized), so to me it seemed critical to mount the pumps below the tank in order to not lose prime.  Well, he didn't do that, stating an "Air Eliminator" would keep out the air.  Needless to say, 2 burnt up pumps later he still hasn't come back to fix the problem or re-mount the pump.  I'm thinking that when the pump burnt up this time it potentially caused damage to the unit as the unit appears to be on lockout.  I assume this based on the fact that when I went down the one day it got cold in the house the pump was burnt up hot, and the area around it looks as though it sustained some serious heat, even melting some of the pipe insulation in the area, baking thermostat wires, and some of the flux seems to have ran down the copper.  Instead of mounting a temp bulb inside the buffer tank, he has a sensor on the copper inside the heat exchanger.  In order to get an accurate temperature reading, I have to run the pump on 24/7.  Needless to say, this seems like a lot of wasted energy as it's a 26-99 (220V) pump (~$25/month!), which seems overkill itself (I was thinking a little 15-58 Grundfos on 110V would do the trick as there should be virtually no head - water is being lifted mere inches and traveling 5-10 feet - which is what I remounted/primed to try and get it back up and running).  He stated the need for a 220V pump as the unit runs on 220V...I asked him why it couldn't just run off 1 leg?  I had a 15-58 around, and replaced it to try and get some heat, but can't get the unit on as I believe it to be in lockout.  When I turned the breaker on after mounting the pump the unit wouldn't do anything.
- I had my return lines frozen solid the other day when I went to my basement to see why I had no heat.  Against my best wishes, there is no flow check (except on the pump, which I don't believe to be water tight) to prevent water from taking the path of least resistance.  Instead of using my loop field, it's simply circulating water from one unit through the other.  I turned the ball valves off on the radiant side (since I couldn't get it to work anyway) between the 1" supply and the pump pack to get it to push through the loop field.  This works for now, but will not allow for the operation of both units in the long run.  Any ideas how this can be rectified?
- My electric bill last month was $650!  I was thinking that it would be closer to $400 for the geo, pumps/air handler included.  Last month was cold, but if my normal bill is less than $100, that's over $550 for heat.  At $0.11/KWH, that's 5000 KWH's, or roughly 50 Million BTU's at roughly a COP of 3...easily obtainable according to Climatemaster charts and around most closed loop applications in this area.  50 Million btu's would be a BTU loss of 67,000/hr or 16.8 a sq'...seems a little high to me.  I'm thinking it could have been the problem with not using the loop field, therefore I was essentially using the compressor as electric resistance heat while only pulling a tiny bit of heat from the loop field (whatever resistance the check valves in the pumps could force through the loop field...COP of 1.  That, and when both units were on <!--[if gte mso 9]> Normal 0 MicrosoftInternetExplorer4 <!-- /* Style Definitions */ p.MsoNormal, li.MsoNormal, div.MsoNormal {mso-style-parent:""; margin:0in; margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:12.0pt; font-family:"Times New Roman"; mso-fareast-font-family:"Times New Roman";} @page Section1 {size:8.5in 11.0in; margin:1.0in 1.25in 1.0in 1.25in; mso-header-margin:.5in; mso-footer-margin:.5in; mso-paper-source:0;} div.Section1 {page:Section1;} --> <!--[if gte mso 10]>
- There are a couple other problems that need fixed (he has 4 of my 7 manifolds mounted above the water line of the tank), but I think I have the solution to those.  Several of those manifolds lose prime and backdrain down into the tank...pump runs dry, pump burns up.  I think remounting the pumps below the water line, or putting an expansion tank above the highest radiant loop, would do the trick.
Thanks in advance for any help anyone can offer.  I'm looking to get this all behind me and be warm for a change (68-70 would be great!)  .  It's been about 57-60 in the house since the radiant unit went down.  I've attached some pictures for your humor/understanding of whats going on, and to give you an idea how not to do things.  That being said, the distribution of the radiant heat seemingly worked great when the unit would run.
Ozark01User is Offline
31 Jan 2010 02:54 PM
The first thing I noticed in your story is that you are moving the wires on the Y terminals. The Y terminals are for cooling and the W terminals are for heat. You may have the A/C running when it is not supposed to be along with the aux heat (if you have any).
31 Jan 2010 03:59 PM
Ozark,
I appreciate your help and that makes sense. I'm thinking that the 2 "C" poles must be 1st/2nd stage of the compressor even though I don't see it written anywhere in the 50 page book that comes with it. He has the one blue jumper hooked to a ground jumper on one of the 2 units, the other "C" spot and blue jumper is not being used. I suspected the blue wire, which I believe to be the 2nd stage wire, might go on the other "C" pole to run the "C"ompressor in 2nd stage?
31 Jan 2010 04:11 PM
My first guess for the C terminal would be it is the common terminal and not related directly to the compressor. It would help if you made a note of the thermostat connections in the unit and the color of the wire on the terminal and do the same in the thermostat. It would also help to know if the thermostat is the same manufacture as the unit. You are correct about the Y terminals. I was thinking of a gas furnace and not a heat pump. Sorry!
31 Jan 2010 04:21 PM
You can see the circuit board in the pictures...on the back side of the thermostat I have the following:
Y2 - Gray
W2 - White
G - Green
W-Orange
C-Blue
Y-Yellow
R-Red
Rc- Bare wire, ground?
The thermostat is a Honeywell TH6220D1002.
It says "Y2 must be wired to solonoid for stage 2 to operate properly".  Could it be while he has the gray/blue jumper wired nutted together, since they aren't on the "C" terminal they are engaging the stage 2 solonoid?  Perhaps just wired nutting them and not putting them on the circuit board is the problem.
I think the second circuit board your looking at is the radiant unit...I am referring to the forced air unit right now trying to get it straight.
31 Jan 2010 04:32 PM
Your pictures did not come through but you probably know that by now.
31 Jan 2010 04:33 PM
Sorry, they are in the link at the end of my top paragraph.
31 Jan 2010 04:36 PM
Posted By Ozark01 on 01/31/2010 2:54 PM
Sorry....but this is bad info.
Y1 starts the compressor in First Stage   heat or cool depending on O
Y2 starts the compressor in Second Stage heat or cool depending on O
O energizes the reversing valve which puts the unit into cooling mode.
W energizes strip heat if installed.
If you want the compressor to run in second stage,  you need to energize both Y1 and Y2.
C is common or ground.
G.O. JoeUser is Offline
31 Jan 2010 04:38 PM
Wow! Where to start. I can't get it all but here are a few points.
In heat pumps contrary to several posts back-
Y1- compressor 1st stage
Y1+Y2- compressor 2nd stage
O- for cooling
Compressor will always start in first stage and will not start without Y1 call.
In your case jumper between Y1 & Y2 for stage 2 runs after start up.
You can't pull 110v off a 220v circuit unless you have a common back to the panel.
You can't specify pumps baseed on what you think. You have to calculate the head loss of the loop (including all components) and size the pump accordingly.
C  C  terminals on circuit board are for the compressor contactor.
C terminal on thermostat terminal is common.
Take a step back. Take a breath and look at the wiring diagram before you start changing things. Also take a picture to document where wires are now.
31 Jan 2010 04:43 PM
I looked at your pictures and don't see a Y2 terminal in the photo. Is there one?
31 Jan 2010 04:45 PM
You are correct. I edited my earlier post to reflect my mistake.
Dean,
He has right now a ground jumper on "C", along with one of 2 blue jumpers that run back to the compressor.  Is the second jumper to go on the "Y" terminal, and how do I make the connection between Y1 and Y2...Y2 is the Grey stat wire from what I can tell.
Ironically I didn't put any strip heat in figuring with already having 2 heat sources I'd be good to go unless something happened in my loop field...I guess my plan was foiled!
31 Jan 2010 04:50 PM
As best I can tell there is nothing labeled "Y2"....I foolishly tried putting them both (yellow and grey, as seen in the photo) in Y1 to no avail...I'm desperate for heat and my contractor has basically walked away from it after he put it in (he said he'd be out next Saturday with the same "expert" he brought last time to check his work)....I'm thinking he doesn't do a whole lot of geo units.
31 Jan 2010 05:00 PM
You only have a single stage unit
31 Jan 2010 05:04 PM
After looking at the pictures The top unit is a TMW water to water unit not a split!
That unit is not 2 Stage.
31 Jan 2010 05:10 PM
Joe/Dean...
You both could be right, but I really hope your wrong! I paid for the Tranquility 27's...they didn't even make the TMW unit then, and were just releasing (but wasn't in stores) the DMW unit, or whatever the high temp hot water unit is called.
The guy that put it in I'm pretty sure blew a circuit board and I'm betting put a different one in? I'm thinking when he blew it he pulled the circuit board from the other unit to get the one he was working on at the time running. As far as I knew it's suppose to be (2) Transquility 27's (TTS) with a heat exchanger for the top unit (radiant unit). None of the indicator lights on the outside have ever worked, but to his credit the radiant unit did work for awhile and kept it comfortable...that was before this last pump episode.
Both units also start their serial #'s TTS064...
31 Jan 2010 05:15 PM
At this point either read and understand the manual before you damage something or hire a pro.
31 Jan 2010 05:23 PM
Don't worry a 3 ton W-W unit costs way more than a 2 stage split.
31 Jan 2010 05:30 PM
Joe,
Actually, I had priced them both out from a local wholesaler when I was designing it, and both a GSW and Tranquility 27 were within a few bucks (for same tonage, then I had to spend some extra bucks for the retrofit kit heat exchanger).  I forget my rationale for going with the Tranquility 27's...I'm thinking it was so they'd both be R-410A and it had a good bit higher COP?
I wasn't really looking to do my own electrical work....trust me, that's why I thought I hired a pro in the first place!
I've been through the 50-page manual numerous times....it's actually forced me to know more about heating/cooling/geo systems than I ever cared to know!  Unfortunately, I feel like I know more about this/care more about getting it right than he does.
I've posted a web link to the Climate Master user manuals if anyone might be able to help figure it out: http://www.climatemaster.com/downloads/97B0047N02.pdf
This manual is newer than the one I have and shows some references to "Y2"...mine doesn't even reference a "Y2"
31 Jan 2010 07:56 PM
Wow  what a mess.
The first thing I would do is get the model and serial number for each unit and get the right board.
If you have a two stage unit and a single stage board, it is no wonder that you have problems.
Is there another pro in your area that can help you out?