Posted By flyboy on 02 Oct 2010 09:10 PM
I don't need a very large pump since I don't want the water to flow
too fast so it has time to transfer the heat from the ground ...
Low flow rate will reduce heat transfer, not enhance it. Fuggeddabout
temperature, it's BTUs that count -- and any heat exchanger will move
more BTUs at high flow rates than at low.
Also, independent of the above, you want the flow rate high enough
to achieve turbulent flow. At low flow rates (laminar flow), the fluid
in the loop forms a static "boundary layer" against the pipe walls,
and this retards heat transfer.
As engineer cautioned, low voltage does not equate to low power --
ignore the volts, pay attention to the watts.
Sorry to say, I must agree with geodean on your chance of success.
600 feet of pipe won't deliver much heat, especially with such low
delta-Ts across both the source and load heat exchangers.