Posted By decafdrinker on 21 Feb 2011 08:01 AM
My R ends up being only 1400 ???? .... Or is my formula off?
That Re looks about right, according to the tables in WF's p-drop
calculation manual -- but I can't vouch for the formula you posted
without some reverse-engineering of the units.
http://waterfurnace.ca/Engineer/Misc%20References/Pressure%20Drop%20Calculation%20Instructions.pdf
Anyhoo, a major source of headaches with p-glycol is that its viscosity
increases very rapidly with falling temperatures, so you get a Reynolds#
"double whammy" at low brine temps. Calculations for p-glycol at 30F
are of little use at 25F.
As far as "needing" a higher Re, I can agree with the turbulence-deniers at
least to the extent that if your measured coax and air handler delta-Ts are
reasonably close to manufacturers' specs, it's unlikely that loop mods or
antifreeze tweaking will improve system efficiency by very much.