EWT/LWT values for slinky loops?
Last Post 16 Nov 2010 10:13 PM by davewick. 3 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
davewickUser is Offline
New Member
New Member
Send Private Message
Posts:13

--
16 Nov 2010 10:34 AM
Last week I fired up my 4 ton Tranquility 27 system and after 5 days of collecting data I wanted to check with folks about the delta T I'm seeing on the enter and leaving temperatures of the loops. I'm located in Western Massachusetts, the loops are ~7' down and are 3200'. When running in heating mode I'm consistently seeing a 4.2 degree difference. Is this OK? I've looked at a number of folks's WEL graphs online (http://www.welserver.com/) and 4.2 looks consistent with others, but being a new-bee I'm kinda curious what I should expect to see. Thanks -David
LoobyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:401
Avatar

--
16 Nov 2010 11:31 AM
Delta-T is mainly a function of heating load (i.e. stage1 versus stage2)
and flow rate (GPM); it has very little to do with the loop field itself.
If you're concerned with loop field performance, pay attention to EWT
alone. If it doesn't get too low (during heating season) the loop is
doing its job.

FWIW, a 4.2 F delta-T sounds about right for a closed loop Tranquility 27
system running in stage1 within the CM-recommended flow rate range.


One measurement is worth a thousand expert opinions.
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
16 Nov 2010 09:11 PM
Sounds good, perhaps even low, to me as well. What is the EWT?
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
davewickUser is Offline
New Member
New Member
Send Private Message
Posts:13

--
16 Nov 2010 10:13 PM

Thanks for the feedback already received. 

Update:  I changed the position of my temp sensors tonight and the delta T is now 6.3 rather than 4.2.  So, this is entirely within the range recommended by Climate Master for this heat pump.  The issue appears to have been related to trying to measure temps through the plastic pipe, once I put the sensors on the metal fittings used to couple the pipes to the circulation pumps I got what seems to be a more accurate reading.