I think I was misled
Last Post 08 Dec 2010 09:05 AM by joe.ami. 28 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Page 1 of 212 > >>
Author Messages
foafUser is Offline
New Member
New Member
Send Private Message
Posts:48

--
17 Nov 2010 02:42 AM

I have just had and Earthlinked DX system installed in my home, but I don't think it will do what I wanted. I was very clear with the saleman, who also turned out to be the company owner and foreman.

I told him I wanted a system that would provide me with heating and cooling and that would make hot water all year round, spring and fall, even when the system is not heating or cooling.

I had a quote from a Waterfurnace contractor, who was prepared to install a system like this for me.

I chose the Earthlinked DX system because the guy told me that with the Earthlinked system he could add a desuperheater for $400, and that would give me what I wanted.

The Waterfurnace guy was close in price to the Earthlinked guy for climate control, but was $8000 extra for the hot water, because he had to install a separate box dedicated to hot water.

That made my choice easy, except  my furnace is almost never on this time of year and I find my system is not preheating my hot water. They say they are finished and everything is working. I looked online to see if I could find out why this might be, and learned that the desuperheater does not preheat the hot water all year round. It only works when the air handler is running.

The waterfurnace guy could have added a desuperheater too.

So, now I find myself apparently with the wrong equipment supplied to me, according to my design specifications.

Can this be rectified? Is there any way I can get some sort of add-on to my residential Earthlinked DX system to pre-heat my hot water all year round even when the air handler is not running? 

The Earthlinked web site is not clear about this at all.

Here is what the web site says:

The Earthlinked system has three major components:

1. An earth loop system that circulates a heat transfer refrigerant to exchange heat with the earth.

2. A heat pump that moves heat or cool between the building and the earth via the earth loops.

3. A distribution system to distribute comfort throughout the building.

And two options for water heating:

1. A desuperheater to capture waste heat from the air conditioning cycle and move it to the water heater.

2. A full-demand water heater, where the Earthlinked system supplies all of your hot water needs year-around.


#2 . What does that mean?

Does that mean the whole unit is dedidcated to hot water and does no air handling?

Does it mean, with option 2, I get air handling and year-round hot water?

You would think they would provide more details.

------

update:

The guy is in this morning and he is saying it would cost more in electricity to heat hot water year round using the DX system than using the electric hot water tank, because the DX draws 40 AMPS, and the hot water tank only draws 20 AMPS. He says it only saves money on hot water when you make hot water when the air handler is running. Otherwise it costs more.

Is this correct?





 


joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
17 Nov 2010 07:59 AM
Earthlinked can provide 100% of your hot water and heat/cool the home.
Earthlinked's modular construction makes a DSH or a water heat exchanger field add ons.
Why there was miscommunication between you and your contractor I don't know, but I did have to read your post twice as you said first you wanted a unit that would "make hot water all year round" but later discussed that the system was not "pre-heating your hot water". This describes 2 different functions.
That said your system can still be changed to make all your hot water. It will be more expensive than $400, and you may or may not have enough BTU's available with existing equipment (meaning it may take thousands more).
Depending on your locale perhaps an air source heat pump water heater would be a good comprimise. I wouldn't pay $8,000 (or even 4,000) for domestic hot water the numbers don't add up.
Good Luck,
Joe

Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
foafUser is Offline
New Member
New Member
Send Private Message
Posts:48

--
17 Nov 2010 11:17 AM
Thankyou for your input.

Sorry. I should have mentioned that I have a 4 ton system. They installed an extra water tank that is preheated by a desuperheater only when the air handler is running, which for us would be about six months of the year. For the other six months I am heating my hot water with just the electric element in the hot water tank, and the air handler is not running, so the system is only providing blower air circulation for the HRV, for some of that six months when we don't open windows. The system is not saving me any money or reducing my electrical load for six months of the year.

To clarify a couple things, first I am looking at reducing my daily electrical load year-around, with thoughts of going off the grid. The geothermal system replaces a 5 ton forced air electric furnace, and an air conditioner.

There is an installation cost for power generation, which can be reduced if power draw is reduced. This cost has to be factored in, and indeed, a small generation system may have practical power output limits, that require less load to make them feasible.

Second I am being told that using my geo-system to make hot water year-around would cost more than just running the electric water heater in the pre-existing hot water tank, because the unit draws 40 AMPS and the hot water tank electric element only draws 20 AMPS.

Even with a $7000 add on unit dedicated to making hot water, I am being told it would cost more for electricity to make all my hotwater that way, than just using my electric water heater. More importantly for off grid, the electrical power consumption would be higher, not lower.

I am being told that many commercial places are installing geothermal hot water systems to go green, but they are actually using more electricity to make the hot water than before, and are not really doing anything green.

Further, I am being told that my unit can do continuous hot water year round without an add-on, by some sort of configuration change, but it is a bad idea because it will use more electricity than the electric element in the hot water heater.

I am being told that I can only save money heating hot water with geothermal, when the air handler is running heating or cooling.

I know enough about many products to know when I am being misled, but I am a geothermal novice, and I really need to know if what I am being told is true. I am relying on my contractor to provide me with accurate information, but I have doubts about what I am being told. Due to the 400% efficiency claims for heat transfer, I would expect that geothermal hot water without the air handler running would use considerably less electricity. Also businesses are usually very thorough about investigating costs, and I can't see them installing an expensive system that increases their costs. Something doesn't seem right.

I am not interested in airing any disputes with my contractor, I just want to get the facts straight so I can make the right choices to reduce my electrical load as much as possible for hot water heating. If I have to add on a separate unit, and it can save me 10kWh a day, I may just do that. But if it is going to increase my electrical load, I would spend a lot of money and make things worse.




cnygeoUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:170

--
17 Nov 2010 12:24 PM
I wouldn'y listen to anything else this guy says - most of this is completely wrong. It is entirely possible to make 100% of your DHW year round with geo, and unless something is really badly screwed up, it will use 60-80% less electricity than a straight electric heater, depending on the system, loop temps, and DHW temp required.

As Joe said, in many cases it does not make financial sense to do this in terms of capital cost, especially when starting with a forced air system, but the energy to run the system will absolutely be significantly lower.

Out of curiosity, what are you using to generate your power? If you are considering PV, keep in mind that for an off-grid application, you would probably come out ahead efficiency wise by using a solar water heater - even if you get an average COP of 3 for the heat pump, the PV is probably only 15% efficient, so you'd only be using 45% of the available solar energy. Most solar water heaters should beat this pretty easily.
foafUser is Offline
New Member
New Member
Send Private Message
Posts:48

--
17 Nov 2010 12:48 PM
Posted By cnygeo on 17 Nov 2010 12:24 PM
I wouldn'y listen to anything else this guy says - most of this is completely wrong. It is entirely possible to make 100% of your DHW year round with geo, and unless something is really badly screwed up, it will use 60-80% less electricity than a straight electric heater, depending on the system, loop temps, and DHW temp required.

As Joe said, in many cases it does not make financial sense to do this in terms of capital cost, especially when starting with a forced air system, but the energy to run the system will absolutely be significantly lower.

Out of curiosity, what are you using to generate your power? If you are considering PV, keep in mind that for an off-grid application, you would probably come out ahead efficiency wise by using a solar water heater - even if you get an average COP of 3 for the heat pump, the PV is probably only 15% efficient, so you'd only be using 45% of the available solar energy. Most solar water heaters should beat this pretty easily.

So, I am being told that the Earthlinked DX system can easily be made to do this with the existing equipment, by reconfiguring something in the compressor box. Is that also wrong?

I did see something on the Earthkinked site that mentions a year-around integrated hot water heating option. Does integrated mean that it is already built into the standard system? The site is clear as mud on this kind of thing. They dont' give you any real facts. It's like watching TV. It's really dumbed down, and uniformative as a result.

I have not decided on power generation yet. I don't like solar PV, or solar in general, nor wind. I have a solar pool heater which works out OK, because it uses the sun in the summer when it provides the most heat. 

I don't like these season/weather/time of day dependent energy sources, otherwise.

I have been investigating using HVAC technology to generate say 3kw 24/7, for 72kWh a day, with batteries to handle surge demand, and startup. Endless Energy Inc has a system that looks interesting. 

Where I live makes this sort of idea more attractive  than other alternatives.  We don't get much sun in the winter when you need power most, and I live in a forest, so shading becomes a problem in winter when the sun is at a low angle.
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
17 Nov 2010 01:32 PM

Second I am being told that using my geo-system to make hot water year-around would cost more than just running the electric water heater in the pre-existing hot water tank, because the unit draws 40 AMPS and the hot water tank electric element only draws 20 AMPS.

Even with a $7000 add on unit dedicated to making hot water, I am being told it would cost more for electricity to make all my hotwater that way, than just using my electric water heater. More importantly for off grid, the electrical power consumption would be higher, not lower.

I am being told that many commercial places are installing geothermal hot water systems to go green, but they are actually using more electricity to make the hot water than before, and are not really doing anything green.






While it might be correct that the whole system running might draw 40 Amps, it will run a much shorter period of time thanks to the overall energy produced (BTW, 40 amps is a lot for a 4 ton system, it should be more in the low 30s). So while your resistance hot water heaters will draw about 20 amps, their output is only about 4500 watts, or 13,500 BTU/hour. However, your 4 ton heatpump should put out about 40.000 BTU/Hour. Unless they have a dedicated hot water generator, I do not see how they can use a desuperheater for all year around use by re-piping. Having said all this, I am not too familiar with the DX product itself, so this is more a general idea about heatpump performance. One thing is constant, a ground sourced heat pump will outperform resistance heat by about 3-4 folds in terms of efficiency.
www.buffalogeothermalheating.com
cnygeoUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:170

--
17 Nov 2010 01:46 PM
Posted By foaf on 17 Nov 2010 12:48 PM

So, I am being told that the Earthlinked DX system can easily be made to do this with the existing equipment, by reconfiguring something in the compressor box. Is that also wrong?

I have been investigating using HVAC technology to generate say 3kw 24/7, for 72kWh a day, with batteries to handle surge demand, and startup. Endless Energy Inc has a system that looks interesting. 


I can't speak for Earthlinked specifically, but in general if you want a dedicated HW system you will need to add a refrigerant-water heat exchanger of sufficient capacity to absorb the entire heat output of the compressor during the shoulder seasons when you might only be making hot water. For a radiant system it is easier since you can do it all on the water side.

Endless Energy looks interesting from the standpoint of being one of the nicer looking SNAKE OIL sites I've come across. Please consult an engineer or physicist before buying!!!
foafUser is Offline
New Member
New Member
Send Private Message
Posts:48

--
17 Nov 2010 04:26 PM

Yes, it would be nice if there were someone on the board who does Earthlinked Geosystems who could provide some answers.

The WEB site has no contact us section that I can find.

WRT Endless Energy, I'm using their system as an example. The concept is fairly flexible and uses HVAC equipment, with a generator that you should be able to purchase separately. I'm sure there are various ways to use heat pumps to create a suitable temperature gradiant to support power generation. They are claiming a realistic 80 F temperature differential which does not allow for very efficient operation, but even low effieciency can be enough for continuous micro generation.

Mid temperature also considered low temperature geothermal generation uses a binary cylce with minimum temperatures around 190 F. This gives a temperature gradient against the environment of about 120 degrees. Efficiency drops with temperature differential. They claim 500% heat transfer efficiency across the gradient between reservoirs. It is the heat differential that is used to run the generator and that is where you lose efficiency with temperature.

Endless Energy is reporting net output of 2-4 kw which is a lot when generated continuously. The generator they are using was designed for use with solar heat collectors to provide the temperature differential, but they are using heat pumps for that, and still producing enough power to run the heat pumps and produce a few kw extra.

This I am hazy on. It's like they are playing some sort of fast shuffle with heat transfer, that smells of a perpetual motion machine.

cnygeoUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:170

--
17 Nov 2010 04:41 PM
The concept is analogous to using an electric motor to drive a generator - it is a perpetual motion machine the way they're using it. If you read the prototyping section, they haven't actually tested a unit that shows a net power generation, they were using an electric motor to pump refrigerant and drive their turbine. So maybe snake oil is too strong a term, it is possible that they honestly think it will work.

Low temperature differential heat engines can work, of course, and I think it's a pretty interesting field. Some of the ocean-based systems might have promise in the right locations (google "OTEC"). In this case, even if they did it right they would be looking at a temperature differential of 30-40F max (and then only in the middle of summer or dead of winter) - THEORETICAL (Carnot) efficiency would be in the 7% range, so in practical terms they might hope to capture 1-2% of the available energy. 3kW would require 1000gpm or so. That's a pretty big pipe. Again, this is best case, more than likely it wouldn't work at all.
foafUser is Offline
New Member
New Member
Send Private Message
Posts:48

--
17 Nov 2010 05:21 PM
Posted By cnygeo on 17 Nov 2010 04:41 PM
The concept is analogous to using an electric motor to drive a generator - it is a perpetual motion machine the way they're using it. If you read the prototyping section, they haven't actually tested a unit that shows a net power generation, they were using an electric motor to pump refrigerant and drive their turbine. So maybe snake oil is too strong a term, it is possible that they honestly think it will work.

Low temperature differential heat engines can work, of course, and I think it's a pretty interesting field. Some of the ocean-based systems might have promise in the right locations (google "OTEC"). In this case, even if they did it right they would be looking at a temperature differential of 30-40F max (and then only in the middle of summer or dead of winter) - THEORETICAL (Carnot) efficiency would be in the 7% range, so in practical terms they might hope to capture 1-2% of the available energy. 3kW would require 1000gpm or so. That's a pretty big pipe. Again, this is best case, more than likely it wouldn't work at all.


I think I am starting to get a picture here. Unless the Earthlinked DX system is somehow special, their year around hot water setup has to use an HWHX box which I don't have, and it can't just be turned on in the compressor box with a configuration change. This I would like to know for certain.

http://www.earthlinked.com/files/downloads/documents/Literature/WaterHeating.pdf

The cost of the HWDX box seems like $7000.

Using hot water as 25% of my electical energy use not considering pool, hot tub, heating and cooling, I get hot water as about 10kWh per day, and I stand to save 60% of that, which works out to 6 kWh per day, for half a year vs a desuperheater, or 182 days, at an average cost of 11 cents per kilowatt.

So that works out to a savings of  $120 a year. It would take more that a lifetime to recover the cost.

So only if I can defer $7000 in energy generation installation costs by needing 6 kWh per day less power, can I justify the expense.

Does that seem about right?

So what I finally need a certain answer about is if I need the HWHX box, or is there some special way the system has of preheating hot water all year around without the HWDX box. Is the HWHX box just for heavy hot water demands like radiant flooring and pool heating, or is it needed for any hot water heating when the air handler is idle?

Who can answer this?

----

Ha! I found their contact us page! I can now go to the manufacturer and get the answers I need. Thanks all.



joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
17 Nov 2010 10:18 PM
"So what I finally need a certain answer about is if I need the HWHX box, or is there some special way the system has of preheating hot water all year around without the HWDX box. Is the HWHX box just for heavy hot water demands like radiant flooring and pool heating, or is it needed for any hot water heating when the air handler is idle?"

Again we confuse "preheating" with finish heating. Most every brand/type of heat pump can "preheat" water for you, but that's not really what you say you want.
A DX to water heat exchanger is not $7000, but if you want it to heat all your DHW it may take more BTU's than your system has available after heating your home. That could require additional equipment that does cost thousands. 
I think you are inadvertantly excluding information which handicaps us in answering your questions.
Joe
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
17 Nov 2010 11:47 PM
foaf,

Send an email to clark at pinksdx.com. He can answer your questions.
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
foafUser is Offline
New Member
New Member
Send Private Message
Posts:48

--
18 Nov 2010 10:42 AM
Posted By joe.ami on 17 Nov 2010 10:18 PM
"So what I finally need a certain answer about is if I need the HWHX box, or is there some special way the system has of preheating hot water all year around without the HWDX box. Is the HWHX box just for heavy hot water demands like radiant flooring and pool heating, or is it needed for any hot water heating when the air handler is idle?"

Again we confuse "preheating" with finish heating. Most every brand/type of heat pump can "preheat" water for you, but that's not really what you say you want.
A DX to water heat exchanger is not $7000, but if you want it to heat all your DHW it may take more BTU's than your system has available after heating your home. That could require additional equipment that does cost thousands. 
I think you are inadvertantly excluding information which handicaps us in answering your questions.
Joe
$7000 was an installed price that I was given.

I have a pool, but the pool is heated by solar. I have a Heliocol setup for that. 

I have no radiant flooring at all.

I have all forced air heating and cooling through the air handler.
 
In addition I have a vented HRV, connected to the bathrooms and kitchen.

I have an electric hot water heater. It is 60 gallons.

All I need is preheating of my hot water, I already have the preheating holding tank installed. The preheating holding tank is also 60 gallons. We have four adults living in the house. 

This issue is whether or not the unit can preheat water when the air handler is idle, without a HWHX box, and if it can, does that save on electrical usage, and if so, how much.

My air handler is idle half the year.

geotekUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:154

--
18 Nov 2010 08:33 PM
Preheat hot water, commonly referred to as desuperheater, only works when the unit is running. It works by capturing heat from the compressor, a byproduct of compression. It will save on electricity, how much depends on run time and hot water usage. What you are looking for is on-demand water heating and requires a dedicated unit. I would not do this as an add-on to existing equipment with out determining load requirements. They also make heat pump water heaters which may be an option for you.
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
19 Nov 2010 09:10 AM
"This issue is whether or not the unit can preheat water when the air handler is idle, without a HWHX box, and if it can, does that save on electrical usage, and if so, how much"

No, it can't heat or preheat water when unit is otherwise idle.

I'm not sure if you were "mis-led" or if your bidders did a poor job of clarifying the differences for you. I really can't imagine anyone suggesting that on demand water "pre-heat" was available or even a good idea (in a residential DHW application).
Perhaps we can do that here....

A desuperheater which it sounds like you have, preheats water with "waste" heat from the refrigeration process. Water is generally stored in a buffer tank up stream of finish tank. A DSH will not heat water on demand, geo must be running to heat or cool home. It saves money on electrical usage when used in this configuration.
One could set up a duct zone to "dump" heating or cooling to basement, crawl or outside, to run DSH on demand, but this obviously would add electrical usage.

On demand water heating with geo can be done as well, but it would generally not be done as a "pre-heat", it would replace your finish tank. While it could be done as "pre-heat" it would be the least effective of the scenarios (why finish heating the water with a less efficient method if you've invested in the hot water heat exchanger).
On demand could save energy ($$$) over current configuration, but at what cost?

The configuration you purchased is IMO the most cost effective of your options. No it won't pre-heat water when geo isn't running, but it does save you money without further expense.

j
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
foafUser is Offline
New Member
New Member
Send Private Message
Posts:48

--
19 Nov 2010 11:58 AM
Posted By joe.ami on 19 Nov 2010 09:10 AM
"This issue is whether or not the unit can preheat water when the air handler is idle, without a HWHX box, and if it can, does that save on electrical usage, and if so, how much"

No, it can't heat or preheat water when unit is otherwise idle.

I'm not sure if you were "mis-led" or if your bidders did a poor job of clarifying the differences for you. I really can't imagine anyone suggesting that on demand water "pre-heat" was available or even a good idea (in a residential DHW application).
Perhaps we can do that here....

A desuperheater which it sounds like you have, preheats water with "waste" heat from the refrigeration process. Water is generally stored in a buffer tank up stream of finish tank. A DSH will not heat water on demand, geo must be running to heat or cool home. It saves money on electrical usage when used in this configuration.
One could set up a duct zone to "dump" heating or cooling to basement, crawl or outside, to run DSH on demand, but this obviously would add electrical usage.

On demand water heating with geo can be done as well, but it would generally not be done as a "pre-heat", it would replace your finish tank. While it could be done as "pre-heat" it would be the least effective of the scenarios (why finish heating the water with a less efficient method if you've invested in the hot water heat exchanger).
On demand could save energy ($$$) over current configuration, but at what cost?

The configuration you purchased is IMO the most cost effective of your options. No it won't pre-heat water when geo isn't running, but it does save you money without further expense.

j

Thanks to all for clarifying all this.

Right now, I did a test by turning up the thermostat 5 degrees C, so the furnace ran continous for fifteen or twenty minutes.

I could not feel any heat being generated at either of the water pipes going in or out of the compressor box. I understand that the unit is supposed to preheat water in both the cooling and heating cycles, so with the furnace running a long time, shouldn't I feel some water being heated?

About that. If the desuperheater is running off the compressor during the heating cycle, would it be possible to bypass the air handler when it is not needed and just run the compressor for the desuperheater, or does the desuperheater need some sort of preceeding heat exchange besides the ground loops?



decafdrinkerUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:420

--
19 Nov 2010 12:29 PM
The desuperheater on most units only takes a small percentage of the actual heat the unit is generating...it's a very small heat exchanger compared to the main exchanger used for ultimately heating the ducted air. I've read on the order of 5 to 15%. In cooling mode, 5% to 15% of the heat pulled out of the house can be dumped into the hot water generator (desuperheater) and rest of the heat is "sent" to the ground loops. In heating mode (when running, of course), 5% to 15% of the heat pulled out of the ground is sent to the hot water generator. The rest goes to heat the ducted air for the house. When the compressor is running, in either heating or cooling, certain other conditions have to be met in order for the actual desuperheater components to operate. The temperatures of the incoming desuperheater water, the amount of "excess" heat coming from the home (cooling mode) or loops (heating mode).

Trying to run the desuperheater exchanger system without running the actual air handler would, most likely, be highly ineffective.
foafUser is Offline
New Member
New Member
Send Private Message
Posts:48

--
19 Nov 2010 04:15 PM
Posted By stuart.wyss on 19 Nov 2010 12:29 PM
The desuperheater on most units only takes a small percentage of the actual heat the unit is generating...it's a very small heat exchanger compared to the main exchanger used for ultimately heating the ducted air. I've read on the order of 5 to 15%. In cooling mode, 5% to 15% of the heat pulled out of the house can be dumped into the hot water generator (desuperheater) and rest of the heat is "sent" to the ground loops. In heating mode (when running, of course), 5% to 15% of the heat pulled out of the ground is sent to the hot water generator. The rest goes to heat the ducted air for the house. When the compressor is running, in either heating or cooling, certain other conditions have to be met in order for the actual desuperheater components to operate. The temperatures of the incoming desuperheater water, the amount of "excess" heat coming from the home (cooling mode) or loops (heating mode).

Trying to run the desuperheater exchanger system without running the actual air handler would, most likely, be highly ineffective.

Thanks for the knowledgeable information. I think that wraps it up. If the system can't run the desuperheater on its own economocally it means a dedicated hot water heat exchange box or the desuperheater operating when the air handler is running are the only two options.

If the desuperheater cannot tap into 100% of the compressor output and efficiently preheat hot water, when the air handler is idle, then there are no other options.

I thought it might be as simple as a couple valves bypassing the airhandler and pushing all the refrigerant from the compressor through the desuperheater, governed by a water tank thermostat, when the air handler is idle. I don't know enough about how these things work and where they are connected.

Cheers

engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
19 Nov 2010 10:52 PM
Nope - desuperheater heat exchanger is way too small to accept and transfer anywhere near the compressor's full output. This is by design.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
foafUser is Offline
New Member
New Member
Send Private Message
Posts:48

--
29 Nov 2010 09:52 AM
Posted By engineer on 19 Nov 2010 10:52 PM
Nope - desuperheater heat exchanger is way too small to accept and transfer anywhere near the compressor's full output. This is by design.

More no can do attitude.

Good thing the engineer at Earthlinked has more imagination.

I sent them an email and asked them. They are doing a PI, and sending me a custom control module, to do hot water preheating with the desuperheater all year around. I think they liked the idea. My guess is that they will probably market it and even do retrofits for existing installations. I asked how they did it. Brilliantly simple, just like the suggestion. 

You just have to beleive it can be done and you can usually find a way.