Hello,
Posted here a few time, very helpful.
Anyway, this last weekend our geo guy was attempting to do horizontal bore (5 ton CM, loop, northern Minnesota), the 1st 4-5 feet were clay/loam, no problem. After that was gravel that consists of pea gravel up to large rocks. He said he went down 30-40 feet (trying to get out of the gravel), still gravel and couldn't turn the bit, real hard on his machine. He ended up backing it out, he tried a couple times. He made a call and was told there is another bit that may allow him to pass through the gravel. Waiting on that......
I am not hopeful about this working, looks like vertical loops are in our future at an additional cost of $4000, to total $12000.
How much vertical loop would I need? Does it depend on the water table? I havn't done much research in this area. Excavation is out of the question, would have to take down a lot of trees and the cost would climb because of that.
Any thoughts?
thanks again Steve
|
|
|
|
|
|
|
arkie6
 Veteran Member
 Posts:1453
 |
| 25 Aug 2011 10:33 AM |
|
Around here, you generally need 180'-200' of well per ton of heating/cooling. In this well bore would be inserted a single 3/4" U tube heat exchanger. If your water table is at or near the top of the gravel, then you could likely get by with a little less well depth. Well drilling costs here are ~$5-$7/ft. |
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 26 Aug 2011 08:49 AM |
|
Vertical loops about 3k/ton here. How are you sure you have to take trees down to do horizontal. Trenches don't have to be straight and excavation equipment is in all sizes. j |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
steve_mn
 New Member
 Posts:18
 |
| 26 Aug 2011 01:02 PM |
|
So, for 5 tons 900-1000 feet of well. Can I also get house water out of it? A 3rd pipe should easily fit down the casing. Or does the grout stop that option? Excavation is possible, was thinking slinky, but from what I have seen in videos, the slinky is built next to the trench and then placed inside and filled, doesn't look to narrow to me. We have dense forest.
|
|
|
|
|
arkie6
 Veteran Member
 Posts:1453
 |
| 26 Aug 2011 01:46 PM |
|
You can put a second U tube heat exchanger down a bore hole, and this is done in some cases where the soil has high thermal conductivity; however, usually the soil's thermal conductivity is the limiting factor and just putting more pipe down the same hole gains you little benefit. Any time you cut a large number of a trees roots within its drip line, especially a large tree, you risk killing it. For a 12" diameter oak, the drip line (essentially the farthest reaches of its branches) can easily extend 20'-30' beyond the base of the tree. Most of a trees feeder roots are near the surface, so a trench effectively eliminates those in its path. If you cut a trench within 10' of a moderate sized tree, you will have effectively killed ~25% of its feeder roots. It may not die the first year after - it may take several years and a stressful situation like a drought to kill it, or if it is really healthy and unstressed, there may not be any measurable impact. |
|
|
|
|
arkie6
 Veteran Member
 Posts:1453
 |
| 26 Aug 2011 01:50 PM |
|
Do you really need 5 tons of HVAC? Have you had a Manual J residential load calculation done? |
|
|
|
|
waterpirate
 Basic Member
 Posts:467
 |
| 27 Aug 2011 06:40 AM |
|
Posted By steve_mn on 26 Aug 2011 01:02 PM So, for 5 tons 900-1000 feet of well. Can I also get house water out of it? A 3rd pipe should easily fit down the casing. Or does the grout stop that option? Excavation is possible, was thinking slinky, but from what I have seen in videos, the slinky is built next to the trench and then placed inside and filled, doesn't look to narrow to me. We have dense forest.
There is a huge differance between a closed loop bore hole and a water well. It is a common point of confusion. You can stop by my website for a quick tutorial. Eric |
|
| Eric Sackett<br>www.weberwelldrilling.com<br >Visit our Geothermal Resource Center! |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 27 Aug 2011 07:56 AM |
|
Have you had any geo pros to the project to offer ideas? j |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
lzerarc
 Basic Member
 Posts:423
 |
| 28 Aug 2011 11:05 AM |
|
what about increasing your thermal envelope? Possibly spending an extra few thousand can eliminate a ton or more of required heating. I am in zone 6 (I assume that is the same as you) and for 3400 sqft I only require 2 tons of heating. |
|
|
|
|
steve_mn
 New Member
 Posts:18
 |
| 29 Aug 2011 12:38 PM |
|
Yes, manual J has been done. Grand Rapids MN - very cold, wood backup, need 5 Ton, I have the furnace installed. Gravel - poor heat conductivity. I know the difference betweeen closed and open loop. Super insulated but large vaults and large windows. I know the trees would die.
|
|
|
|
|
jonr
 Senior Member
 Posts:5341
 |
| 29 Aug 2011 01:32 PM |
|
putting more pipe down the same hole gains you little benefit. About 13% per Ground Loop Design. Doesn't seem to change much with soil type. |
|
|
|
|
minihowie
 New Member
 Posts:12
 |
| 30 Sep 2011 11:22 AM |
|
Posted By lzerarc on 28 Aug 2011 11:05 AM what about increasing your thermal envelope? Possibly spending an extra few thousand can eliminate a ton or more of required heating. I am in zone 6 (I assume that is the same as you) and for 3400 sqft I only require 2 tons of heating. Wish we would have put more into the thermal envelope when building, although I do not think we cheaped out either. I'm in zone 5 with about 3000sqft and our contractor did a manual J that said we needed 5 tons of heating. We also tried to do the horizonal boring but ran into rock problems too. Ended up putting in 5 150' wells. |
|
|
|
|