Posted By ColdInNY on 20 Dec 2011 10:28 AM
...
Thinking about investing in welserver software so I will have data incase I need it. What are others thoughts?
In a recent thread (above), ColdInNY asked if using the Web Energy Logger (WEL) is helpful to diagnose possibly being short of water loop pipe length. Rather than respond to that thread directly and possibly take it off course, I thought I’d start a new thread here to address how the WEL is ideally suited to monitoring the ‘health’ of a geothermal Ground Source Heat Pump (GSHP) system.
Entering Water Temperature (EWT) is a very easy measurement to record over time to show how well the water loop is performing. For example, here’s a 13 month chart showing the ‘health’ of my vertical closed-loop system:

Here we see that my water loop gets to about 85° (F) max in the summer, and to about 61° in the winter. Keep in mind my GSHP system is in Dallas, a very warm season climate. Thus loop design is focused on keeping the summer EWT as cool as possible, versus in a cold season climate where keeping the winter EWT as warm as possible is the goal.
Watching this chart every once in a while provides reassurance that the loop is performing properly. If my loop was not designed properly, it would be easy to see, as summertime EWTs would be much higher than shown (and at the expense of significant A/C SEER degradation).
Another concern is long term, over many years change in the soil temperature where the loop is, making the loop eventually no longer able to perform. In a warm season climate this would be loop field heating – in a cool season climate this would be loop field cooling.
Here’s an example of EWT for the past 3 years:

Here we see that the maximum EWT has risen at about a 1° per year rate – 82° in 2009, 83° in 2010, and 84° this year (2011). More time (years) will be needed to determine if this is due simply to warmer summers for the past 2 years, or if indeed loop field heating is occurring to the point where in 10 plus years significant SEER degradation occurs during summer A/C.
A second temperature measurement that is excellent at monitoring the health of GSHP equipment is maximum daily compressor discharge refrigerant temperature. Here’s a 13 month example:

This is the temperature of the copper pipe near the GSHP’s compressor that contains the refrigerant coming out of the compressor. This is the maximum daily temperature, something that’s easy for the WEL to produce.
Here we see it well behaved and normal. In the summer compressor discharge refrigerant temp rises and falls slowly in line with EWT. The same behavior occurs in the winter although it’s a little harder to see.
The key value to this chart is that over time it can tell you when a problem’s coming. This gives you time to react in a controlled manner, avoiding unnecessary emergency expenses.
For example, twice I got alerted by the above chart that something was wrong with my 3 ton GSHP unit well in advance of an equipment lock out condition. We can see these two situations summarized with the same chart over a 3 year period:

In both cases circled, a refrigerant leak had developed in the evaporator coil.
As refrigerant slowly leaked out, compressor discharge refrigerant pressure slowly dropped and its temperature comparably increased. Left unfixed, at some point the GSHP’s low pressure monitor would have enabled, turning off the unit hopefully before compressor damage occured.
Here the chart showed well in advance that something was wrong, and that at some point the compressor was going to overload and lock out. Seeing the problem developing slowly, it was possible to initiate repair (evaporator coil replacement) at a time when it didn't have to be done as an emergency action.
The cost for doing this monitoring with a WEL unit, including the provided WEL web site and lifetime data collection, both with no monthly fees, and with no required s/w installation on anything, is about $410 for the WEL unit, and about $15 for each of the two temp sensors (EWT and compressor discharge). The monitoring scenario above is probably one of the easiest to implement with a WEL: nail the WEL to the wall, plug in its transformer power supply, make a LAN connection, string a CAT5 cable to where EWT and compressor discharge can be measured, connect up a couple of temp sensors to the cable, and you’re basically done.
The expense here is certainly more than simply measuring occasionally, manually with a thermometer, EWT, or compressor discharge temp. But if you want something that’s no fuss / no mess and runs continuously forever, giving you an exceptionally reliable and very good picture of the ‘health’ of your GSHP unit, I know of no other better ‘bang for the buck’ capability.
I’m at WEL0043 – please feel free to ask me any questions that I can be helpful with.
Hope this is helpful.
Best regards,
Bill