Geothermal heat pump sizing
Last Post 24 Jan 2012 09:08 AM by joe.ami. 7 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages Not Resolved
stangaticUser is Offline
New Member
New Member
Send Private Message
Posts:1

--
16 Jan 2012 11:39 AM
I am having a geothermal heat pump ground water open loop system installed.  A load analysis was done on my house showing that the heating load is 46,097 BTU/Hr and the cooling load is 29,953 BTU/Hr.  I am located in Greensboro, NC.  What size heat pump would you recommend based on these loads?


docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
18 Jan 2012 03:26 AM
Sounds like a 3 ton to me if forced air.


www.buffalogeothermalheating.com
SkyHeatingUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:203
Avatar

--
18 Jan 2012 02:08 PM
I don't know your area well but why are you thinking a 3 ton and not a 4 ton doc? If they are beyond the 3 ton limit of the unit for heating using 25% of their system on backup heat it will negate the savings. What indoor and outdoor temperatures did they design for. What are your entering water temperatures from your well? You should have a professional in your area tell you what heat pump and what size. I would go with a two stage unit that way your unit will have close to full heating capacity and in its first stage(most run at 60%) you will still have 28,800 BTU's (assuming 48K cooling of your unit). So your unit will be almost locked into first stage cooling sizing it perfectly.


Visit my Youtube channel for product reviews and customer testimonials http://www.youtube.com/user/skyheating1
http://www.welserver.com/WEL0626/
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
19 Jan 2012 11:39 PM
3 ton.

Size for cooling for best dehumidification and cooling efficiency, save on first cost of the extra ton of system in exchange for somewhat more frequent use of aux heat.

Even better, look hard at the load calc to identify low hanging fruit (infiltration and insulation improvements) for load reduction.


Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
21 Jan 2012 02:59 AM
Posted By SkyHeating on 18 Jan 2012 02:08 PM
I don't know your area well but why are you thinking a 3 ton and not a 4 ton doc? If they are beyond the 3 ton limit of the unit for heating using 25% of their system on backup heat it will negate the savings. What indoor and outdoor temperatures did they design for. What are your entering water temperatures from your well? You should have a professional in your area tell you what heat pump and what size. I would go with a two stage unit that way your unit will have close to full heating capacity and in its first stage(most run at 60%) you will still have 28,800 BTU's (assuming 48K cooling of your unit). So your unit will be almost locked into first stage cooling sizing it perfectly.


See the attached report. A 3 ton unit with DSH will only use $35 of supplement heat in Greensboro, NC climate, with the above design parameters. A 4 ton unit will actually run $17 more per year, give you less comfort since it is running in single stage in A/C, and will cost you usually $3K more upfront. Deep ground temps are 60F, Design temp is 18F for heating in Greensboro, NC. Designing for 1st stage running only is not perfect, it is wrong. Supplement the heating extremes with aux heat, not full heatpump capacity design. The art is to to build the most efficient system for the least amount of upfront money. You in contrast suggest a system which is designed like a conventional system.

Attachment: NC_Forum.pdf

www.buffalogeothermalheating.com
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
21 Jan 2012 11:38 AM
Posted By docjenser on 21 Jan 2012 02:59 AM
Deep ground temps are 60F...
Doc, just curious, and if you get a chance - how do operating cost compare utilizing a horizontal loop (for 3 vs 4 tons)?  Thank you!


Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
23 Jan 2012 02:41 PM
Posted By geome on 21 Jan 2012 11:38 AM
Posted By docjenser on 21 Jan 2012 02:59 AM
Deep ground temps are 60F...
Doc, just curious, and if you get a chance - how do operating cost compare utilizing a horizontal loop (for 3 vs 4 tons)?  Thank you!


They are very much the same. Even if you have warmer ground temps, you are still running the loop down during the heating season. In general, overall performance does not differ between horizontal and vertical loops.


www.buffalogeothermalheating.com
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
24 Jan 2012 09:08 AM
Horizontal loops do not provide as many btus/ft as verticals, so we use more feet. End performance is nearly the same.


Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!