The trouble with DX.....
Last Post 11 Apr 2013 08:51 AM by Brian466. 46 Replies.
|
Sort:
|
|
Prev Next |
You are not authorized to post a reply. |
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 11 Mar 2012 01:04 PM |
|
I have continued to gently (uncommon for me) voice my DX concerns but feel obliged to sum them up given recent rebirth of the topic.
Want a DX system? Ask yourself these questions:
1) Do I want a system that is not recognized by the International Code Council?
It is true, in Michigan for instance if you install a geo-loop system the code requires a hydrostatic test of loop system......show of hands, who wants to run water in a refrigerant circuit hundreds of feet long? How do you get it all out to avoid damage to the compressor?
2) Do I want a system in my home that (often) the same code requires an industrial type machinery room for?
Also true. Though the International Mechanical and Residential Codes apparently haven't heard of Direct Exchange Heat Pumps, they do identify that once over X lbs/ft3 of X refrigerant, one must have a machinery room with ventilation, refrigerant leak alarm etc. Let's say it again, the quantity of refrigerant in your DX system if leaked, could be injurious to the occupants of your home- therefore industrial measures (and related expenses are required).
3) Do I want a system that eliminates an inexpensive circulator pump, simultaneously increasing the workload of an expensive compressor?
While seldom mentioned, don't you think adding (sometimes) 1,000 extra feet to a refrigeration circuit might tax a compressor a little more?
4) Do you want to put geo loops in the yard that very seldom corrode (if proper protocols are followed) or the ones that never do?
I grow weary of water source guys hype of loop corrosion or refrigerant leaks in the ground. A Good DX installer will mitigate the possibility to almost nothing. That said, HDPE fears only impact and sunlight.
5) Do you want a system that is 3% of the market, or 97%?
Seriously if you were buying a car- one to take you to work everyday, are you going to get the one that often costs more, has a smaller dealer/tech/part network just because the salesman says you might save $90 a year in gas (based on laboratory tests not actual driving)?
6) Do you want a system where most manufacturers, license holders etc have not held the product line for 10 + years?
Go ahead check some domain registrations etc. and please don't bring up the sale of FHP to Bosch, I don't think Bosch is in the same catagory as XYZ DX, LLC.
7) Do you want a system where most dealer/installers have spent less than 5 years with the product?
8) Do you want a system that attracts more new guys since they don't have to buy new tools?
Watersource manufacturers aren't particularly better at vetting new dealers, but extra tools and less finicky installations suggest greater financial security and less opportunity for mishap on installation.
9) Do you want a system with 5 times the refrigerant in it?
Things made by people and installed by people do fail. If you get a leak on a your system do you want the one that has less or more- like maybe $800 more to leak out?
10) Do you want the system that tears up more of your lawn?
While DX boasts of smaller foot prints, what they mean is less pipe. Sometimes this is more holes however or longer trenches etc.
11) Do you want the system with less loopfield flexibility?
DX loopfields are refrigeration circuits that ave a prescribed length and pitch- coloring outside those lines may interfere with compressor's oil recovery harming the equipment. Water loops can follow the grade (saving excavation on hilly lots) or be increased where dry soil is present.
Do you have DX in your home now? Do not despair.
Systems in my AO have been up and running more than 20 years.
Efficiency while ultimately hindered by ground thermoconductivity is still quite good.
Everything that has refrigerant in your home is potentially Injurious to the occupants. That a DX system has more suggests no greater risk of leak occurance, and injury is unlikely.
Greater sales today will hopefully keep some of these guys around for parts etc.
Who sells DX? With all this in mind why would anyone want to sell DX equipment? There are essentially 3 types of companies:
A) Tax credit band wagon guy-
Often low bank prefering system with less business start-up costs (i.e. fusion tools, flush carts etc.)
B) Marketing minded guy-
"everyone is selling those systems for X price, if I'm the only one selling this system I can charge a more premium price."
C) Old geo guy trying out new technology, perhaps thinking of a distributorship opportunity down the road.
Or it may be some combination of the 3. My decision after training in 2 different systems (kinda a combination B and C guy)- I made friends in that industry in MN that I trust and would like to support but for now I must wait and see. I have not decided not to ever sell DX. I had to ask myself "why is the biggest dealer of the biggest distributor of X brand, dropping the product in favor of water source?....and why did that same distributor just take on a water source product?" Geo systems are fairly expensive, eating a few lemons can really hurt a small shop.
About your DX dealer you will have to ask yourself: "is he ignorant of the code- following the code- subject to a different code or ignoring the code?" and "why is the aggravation of selling the least popular product worth it to him". There can be very good answers to the questions, but you won't know until you ask.
Then of the manufacturer you have to ask why an organization as big as the International Code Council is not worth approaching to get the equipment recognized and maybe the refrigerant detector waived by exception or at least a reduction of measures required for compliance.
All that said, the best geo heat pump is still "whatever is sold by the best dealer in your town." This does not rule out DX.
There are always exceptions.
I welcome rebuttal from a DX manufacturer.
I think I may contact the ICC myself to see if they have been approached and if there is something new in the pipe line.
Joe Hardin
|
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 11 Mar 2012 02:44 PM |
|
Well said Joe. |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 11 Mar 2012 03:21 PM |
|
Are you going to post this on the GeoExchange forum? I think you should |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 11 Mar 2012 06:43 PM |
|
Could - we get alot of repeat readers so I often wonder im telling the same folks twice. |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 11 Mar 2012 06:45 PM |
|
Or should I say boring the same folks twice? ;) |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
DGF
 New Member
 Posts:10
 |
| 11 Mar 2012 08:51 PM |
|
It's nice that you can be meticulous and retain a genuinely open mind. I appreciate your help. Here's my take 1. ICC endorsement is something I don't really care about much, personally. I was going to write about it myself, but instead I'll just link to someone else who has already summed it up very well: http://www.greenhomebuilding.com/building_codes.htm. Thats just me, though. 2. A significantly larger volume of refrigerant would certainly pose a greater risk in scenarios (whether sensible or silly) in which a leak occurs inside the home. A valid point, one of the most compelling I've come across on the this subject. I'm not exactly certain how much refrigerant is used in either system (just that the DX obviously uses more). What kind of multiple is involved? Ten, one-hundred, one-thousand, times more refrigerant? I'd be interested to know. Just for comparisons sake, lets say that we have the world's most boring, ordinary 2500 SF home. Anyone have a rough estimate of the amount of refrigerant a typical water source system would use, compared to the same for a typical DX system? 3. Good question, one which I was trying to bring up in the other thread. I assumed previously, that adding a water pump would add to the total workload, regardless. Now I'm wondering how a water pump's work-footprint compares with the work added to a compresser by making it cycle an entire ground loop. It all comes down to the electric bill, I imagine. To deliver the same amount of heat, how much electricity would a water pump and a small-loop compresser use, vs singly a large-loop compressor? I think the electric usage for each would clarify that greatly. This doesn't address the issue of having two mechanical systems versus one, and thus having more potential failure points. However, I suppose this may well be trivial; especially if this avoids or rectifies other issues that are of greater significance. 4. I agree with your sentiment. The possibility of corrosion occurring with copper is worth taking note of, but it seems (from what I've read) both rare for for this to be a problem, and easy to determine if it will be in advance. Non-issue if handled appropriately. 5. I do not care if it's only a small percentage of the market, as far as merit is actually concerned. Ad absurdum, geothermal itself only currently represents a small percentage of the overall heating market. This doesn't say much of course - one way, or the other - about an idea's merit. However, this does have a real effect (good or bad) on whether the idea can be implemented in reality, at the time and place you find yourself in. 6 & 7. Experience can be a worthwhile trait, so yes, it is worth considering. Not the end-all-be-it-all, but a meaningful variable. A DX line which has lasted 10 years would indeed be nice. It's hard to say what the lack of this indicates, exactly. Perhaps it proved to be a problematic system, or maybe its just simply the fact that its new, immature, and needs more exploration. Perhaps these businesses were never able to sustainably reach critical mass. Dunno. 8. I honestly don't know enough about this. Might help if you explained this one to me, if you're up for it. 9. Maybe this answers the question I had in up in #1 10. Myself - I'll be looking for a lot of land with, at minimum, 3 acres or more, and doubt I'll have a lawn of any sort. Still, quite a valid, important question for many, I'm sure. 11. Great point I was not aware of before. Ground loop flexibility might very well turn out to be something valuable down the road. I'd like to know more about the "compressor's oil recovery harming the equipment" - not an issue I am currently familiar with. Once again, if you're up for it. I think one of the most disturbing things (deserving or not) I've have heard about, and wasn't brought up yet, is that a DX system is more susceptible to freezing/thawing issues then a typical water source system. Presumably, this is because of a DX's smaller underground footprint, with more heat being taken from every cubic foot of dirt involved then a system with a larger footprint, and where the load is more spread out. This would seem to indicate that a DX will routinely freeze the ground around it, and in turn produce seasonal/variable ground heaving. Can this be avoided in a water loop system? It also sounds as if refrigerant leaks through copper are more problematic, and likely to happen in this scenario, then water/brine leaks through HDPE. Can this be elaborated on? |
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 11 Mar 2012 09:54 PM |
|
Posted By DGF on 11 Mar 2012 08:51 PM It's nice that you can be meticulous and retain a genuinely open mind. I appreciate your help.
Here's my take
1. ICC endorsement is something I don't really care about much, personally. I was going to write about it myself, but instead I'll just link to someone else who has already summed it up very well: http://www.greenhomebuilding.com/building_codes.htm. Thats just me, though. Yes just you. Because I am unaware of a DX system sold to anyone other than a contractor you are suggesting you want to spend thousands with someone who blatantly breaks the rules. What other business rules will they not follow while executing your contract?
2. A significantly larger volume of refrigerant would certainly pose a greater risk in scenarios (whether sensible or silly) in which a leak occurs inside the home. A valid point, one of the most compelling I've come across on the this subject.
Anyone have a rough estimate of the amount of refrigerant a typical water source system would use, compared to the same for a typical DX system?
Loosely 5Xs.
3. Good question, one which I was trying to bring up in the other thread. I assumed previously, that adding a water pump would add to the total workload, regardless. Now I'm wondering how a water pump's work-footprint compares with the work added to a compresser by making it cycle an entire ground loop.
I think the electric usage for each would clarify that greatly. This doesn't address the issue of having two mechanical systems versus one, and thus having more potential failure points. However, I suppose this may well be trivial; especially if this avoids or rectifies other issues that are of greater significance. The significance of design plays a terrific role in op cost here. We know for instance adding one ton in a heating dominated climate may save 50 to 100 bucks/yr though cost thousands extra to install. One of may dealer training courses in DX taught me to load heavy to allow ground thaw (down time) and indeed the trainer appeared hear once and commented that without downtime he would see radial cuts on the loop pipe from frozen earth. So saying it comes down to cost is an oversimplification. Doc is showing performance exceeding the boasts of one manufacturer.
4. I agree with your sentiment. The possibility of corrosion occurring with copper is worth taking note of, but it seems (from what I've read) both rare for for this to be a problem, and easy to determine if it will be in advance. Non-issue if handled appropriately.
You might also agree with part 2 of the sentiment......material where trouble virtually never occurs beats material where trouble occasionally occurs. Let's not forget, many airsource products begin to have trouble after 20 years or so with brazed joints. I am unaware of a socket fusion leak (if done correctly) after 20 years.
5. I do not care if it's only a small percentage of the market, as far as merit is actually concerned. Ad absurdum, geothermal itself only currently represents a small percentage of the overall heating market. This doesn't say much of course - one way, or the other - about an idea's merit. However, this does have a real effect (good or bad) on whether the idea can be implemented in reality, at the time and place you find yourself in. You might care if you find the warranty on your equipment has no backer because the company folded. There is no comparison between the solvency Climatemaster, Bosch or Research products and most any DX manufacturer. 6 & 7. Experience can be a worthwhile trait, so yes, it is worth considering. Not the end-all-be-it-all, but a meaningful variable. A DX line which has lasted 10 years would indeed be nice. It's hard to say what the lack of this indicates, exactly. Perhaps it proved to be a problematic system, or maybe its just simply the fact that its new, immature, and needs more exploration. Perhaps these businesses were never able to sustainably reach critical mass. Dunno. ding ding ding.........
8. I honestly don't know enough about this. Might help if you explained this one to me, if you're up for it. Aside from the obvious excavation, DX uses tools that any heat/AC tech already owns...so if you want to jump into geo, wouldn't you do it as inexpensively as possible. In fact when a dealer inquires a point is made to let them know they can get in the geo biz on the cheap. 9. Maybe this answers the question I had in up in #1
10. Myself - I'll be looking for a lot of land with, at minimum, 3 acres or more, and doubt I'll have a lawn of any sort. Still, quite a valid, important question for many, I'm sure.
11. Great point I was not aware of before. Ground loop flexibility might very well turn out to be something valuable down the road. I'd like to know more about the "compressor's oil recovery harming the equipment" - not an issue I am currently familiar with. Once again, if you're up for it.
All refrigeration has a maximum reach where oil pumped away from the compressor can not be recoverd by the compressor.
I think one of the most disturbing things (deserving or not) I've have heard about, and wasn't brought up yet, is that a DX system is more susceptible to freezing/thawing issues then a typical water source system. Presumably, this is because of a DX's smaller underground footprint, with more heat being taken from every cubic foot of dirt involved then a system with a larger footprint, and where the load is more spread out. This would seem to indicate that a DX will routinely freeze the ground around it, and in turn produce seasonal/variable ground heaving. Can this be avoided in a water loop system? It also sounds as if refrigerant leaks through copper are more problematic, and likely to happen in this scenario, then water/brine leaks through HDPE. Can this be elaborated on?
see #3 above. water source EWTs have a minimum design temp of 30f (below freezing). ground freeze will occur with either though the HDPE is less concerned with it. It can be designed out in water source with more loops (though it often doesn't pay). One can not simply add loopage to DX. I would not minimize the impact on codes in your world. Insurance companies can refuse to cover equipment not installed to code. Inspectors can order compliance or removal.....etc. A contractor who cheats on the rules would strike me as someone who would cheat on their spouse- you wanna date them 'cause they'll never cheat on you, right? My intent is honest dialogue Your questions are welcome |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
sesmith
 New Member
 Posts:62
 |
| 11 Mar 2012 10:51 PM |
|
Not a geo installer or a residential HVAC guy, but in a previous life I did a lot of automotive AC work. Keeping the refrigerant loop small, and sealed by the factory in the indoor equipment, rather than large, spread underground, and installed at the time of excavation, where contamination with dirt or moisture could easily happen, seems to me like a better way to go. |
|
|
|
|
Looby
 Basic Member
 Posts:401

 |
| 11 Mar 2012 11:27 PM |
|
Posted By DGF on 11 Mar 2012 08:51 PM
I think one of the most disturbing things (deserving or not) I've have heard about, and
wasn't brought up yet, is that a DX system is more susceptible to freezing/thawing
issues then a typical water source system.
Freezing -- in itself -- ain't necessarily a problem. You seem to be ASSUMING that
liquid water is a better thermal conductor than ice. Check the figures, you might be
surprised. And then, there's also "latent heat of fusion" -- check those figures, too.
The "freezing problem" is more a symptom/warning of a situation in which the DX
loop is in contact with less rock/soil than a well designed HDPE loop -- and so, it's
pulling more BTUs from less soil mass. Also, large delta-Ts (anywhere in a heat
pump system) are not conducive to high efficiency. That's a basic thermo-101 fact. |
|
| One measurement is worth a thousand expert opinions. |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 12 Mar 2012 08:46 PM |
|
DGF, I read your link and have to disagree with the premise. Essentially the author wishes permission to build however he likes without supervision, and a provision for this already exists. It is the agriculture exclusion where the buildings are generally owner financed, not for resale and not for habitation. Your author wishes to use insurance, bank money, habitate the building and presumably sell it someday all while ignoring accepted practices. If you are the future owner of the home are you willing to bank on an unconventional builders engineering? A second way to circumvent the code (which is quite routine) is to have an engineer sign off on the design. Author said he didn't mind spending a little more so he need simply to pay an engineer to sign off on his hay bale house. Finally, to this: "Besides, people who are attracted to be inspectors tend to fit the profile of a bureaucrat. This degree of micro-management can easily squelch innovation in building technologies.innovation which is vital to evolving what I would call sustainable architecture." I find it un true on both counts, as a municipal inspector for more than a decade, I find most inspectors are relatively cavalier with the code within accepted practices. However, since the language that held us harmless was removed you are less likely to get us to carry the liability for your "inovation" not only to you but subsequent ownerS. Nor do we micro manage by authors own admission we tend to follow the book (and then only part of it). Finally; historically, codes are generally a result of disaster and loss of human life. You think there might be a few more rules for building powerplants in Japan? Do you percieve that as squelching innovation? Generally changes are the result of manufacturers communicating with states and getting their product approved by localities and the code council. So to bring this full circle: You don't wonder why DX manufacturers haven't done what everybody else has? Do you want to spend 5 figures with a manufacturer that hasn't? Perhaps that's why NJ doesn't permit them. Not trying to bust chops here, but in that new car scenario, do you wanna buy one from the low bank company that suggests NTSB is squelching their innovation? Maybe fly with "Innovative Airlines" who's new technology is unburdened by the FAA? Or pay $20,000 on a system that after decades is not a blip on the governing agencies radar (DX)? FWIW I have been asking this same question for most of 4 years here without a satisfactory explanation. I did write the ICC to see if anything new is coming along. By the way did you notice this at the bottom of your link?: Disclaimer Of Liability And Warranty I specifically disclaim any warranty, either expressed or implied, concerning the information on these pages. Neither I nor any of the advisor/consultants associated with this site will have liability for loss, damage, or injury, resulting from the use of any information found on this, or any other page at this site. Kelly Hart, Hartworks, Inc.
I don't get to write that on the bottom of a green tag. |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
DGF
 New Member
 Posts:10
 |
| 13 Mar 2012 10:07 PM |
|
A second way to circumvent the code (which is quite routine) is to have an engineer sign off on the design. Author said he didn't mind spending a little more so he need simply to pay an engineer to sign off on his hay bale house. Exactly what I've been doing. |
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 14 Mar 2012 01:16 AM |
|
Posted By DGF on 13 Mar 2012 10:07 PM
A second way to circumvent the code (which is quite routine) is to have an engineer sign off on the design. Author said he didn't mind spending a little more so he need simply to pay an engineer to sign off on his hay bale house.
Exactly what I've been doing. and that's fine.....engineers are paid to design I'm paid to enforce that design. BTW, I was rushed by weather and didn't mean for my post to sound like I was directing venom at you. I slightly amended my last so future readers will know who got my dander up. The short story is inspectors are not the only ones concerned with liability and most are blue collar guys. Many such as myself are contractors and must carry our own insurance, so I get a little testy when called unimaginative by a fella with a liability disclaimer at the end of his page.  I once carried liability on all the sub inspectors in the hometown of Rousch racing and realized if that new paint booth went up my million dollar policy would not cover the retainer for my defense- and I was on the hook for electrical and mechanical inspections..........I spearheaded a move to make all the substitute inspectors part time employees  Any way, back to the point, I recieved a reply from ICC where I was told I could get no interpretations without a member number. I supplied one from one of my client building departments and was told I would be referred to the mechanical guru and little else save the board is soon to meet for the 2015 code very soon. Our state runs 3 years behind so if DX didn't make the 2012 book they are at least 6 years away. To put this in context CSST (corrugated stainless steel pipe commonly known as Ward Flex or Trac Pipe) was introduced around the same time as DX (or a little later) and was recognized in the '96 code. The code council welcomes new technologies, no one wants to pay $200 bucks for books every 3 years if it doesn't have new chapters.  Keep ya posted. |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 14 Mar 2012 10:19 PM |
|
Good luck getting an engineer to sign off on non-code compliant systems, assemblies or alternatives without solid technical backup. The professional fee pales incomparison to the liability exposure if something goes badly wrong.
|
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 16 Mar 2012 12:33 AM |
|
.....and there it is. Inspectors should sign off on non compliant stuff (at their peril) but they just stand in the way of progress......yeah-no. RE my original post, I could see an engineer signing off on DX before adobe or hay bales, but the whole point is: why do DX manufactures fail to put themselves in the code book and why do their dealers and customers forgive it? |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 16 Mar 2012 02:19 AM |
|
CC my email to a DX manufacturer...... To Whom it may concern, I have trained in 2 different DX products and consider yours the front runner but have not pulled the trigger based on reservations I have itemized on blogs at both greenbuildingtalk.com geoforums and geoexchangeforums. I sell 100s of thousands in geo each year and am confused by the DX industry as a whole in not legitimizing the product. Among the most pressing of my questions is why the industry has not found it necessary to present the product for recognition with the ICC. How DX manufacturers intend to compete when ICC inspectors enforce the requirement by current code that the product be placed in an industrial type machinery room due to lbs/refrigerent/cuft. How ICC inspectors not require hydrostatic tests of ground loops etc. Please respond on the forums or privately (though I will share your replies). Respectfully, Joe Hardin President AMI Contracting President Doityourselfgeothermal.com Michigan Mechanical Contractor Michigan Mechanical Inspector Michigan Boiler Installer IGSHPA Certified Installer |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 24 Mar 2012 08:40 AM |
|
Well at this point: No response from a DX manufacturer or installer. Did get a response from the ICC to tell me that someone has been assigned my question. 1 week later (on my follow-up) I was told a reminder was sent to the person assigned. Not pleased with the ICC. Stunned at the DX crowd. Tell me I am mistaken. Tell me you are in BOCA or some book I'm not a student of. Tell me your proponents are meeting with the ICC........... Perhaps contacting a Canadian manufacturer of both technologies will yield some answers. |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 01 Apr 2012 02:01 AM |
|
FWIW- ICC responded this week. I was referred to the latest "Green Code" for testing loop efficiency. I replied that my concern was with the "hydrostatic" pressure test required by the IRC and was told they'd get back to me................72 hours ago. Still no response from DX manufacturers.....or installers. What say you Paul? Not trying to bust anyones chops but for cryin' out loud, does no one care enough about the product to make it mainstream? |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 03 Apr 2012 09:51 AM |
|
Just recieved reply yesterday from ICC. Apparently my question about hydrostatically testing loops was misconstrued as I was reffered to the table below (which identifies how to test loop efficiency).
This answers one question: The ICC does recognize DX equipment (just not in the building codes).
This clearly raises the follow up question "why-not"? My follow up question is posted below the table.
Reference: 2012 International Green Construction Code (IgCC)
Table 606.2.2.1 of the IgCC
Energy-Efficient Criteria for Ground Source Heat Pumps
|
PRODUCT TYPE |
MINIMUM EER |
MINIMUM COP |
TEST PROCEDURE |
|
Water-to-Air Closed Loop |
14.1 |
3.3 |
ISO 13256-1 |
|
Water-to-Air Open Loop |
16.2 |
3.6 |
ISO 13256-1 |
|
Water-to-Water Closed Loop |
15.1 |
3.0 |
ISO 13256-1 |
|
Water-to-Water Open Loop |
19.1 |
3.4 |
ISO 13256-1 |
|
Direct Expansion (DX) or Direct GeoExchange (DGX) |
15.0 |
3.5 |
AHRI 870 |
The AHRI 870-2005 can be obtained on the internet under AHRI as it is a free download. This standard has information on the test procedure and pressures etc. you are requesting.
This is my reply:
My question regarding "testing loops" again has to do with the 2009 IRC which makes mention of "ground source heat pump system loop piping" in chapter 20- 2105 (hydronic piping). Here it calls for a "hydrostatic test" which would seem to be damaging to refrigeration loops yet no distinction is made between water and DX loops.
If the IRC does recognize the technology of direct exchange (expansion) geo systems why is a pressure (leak) test not outlined for them as there is for water source? Clearly an air-test is indicated.
The second part of my question had to do with the quantity of refrigerant in a DX system that seems to require a machinery room according to the IMC. Is there a provision that waives this requirement for residential applications to avoid requiring expensive measures of a homeowner (i.e. refrigerant detector......).
Thank you for your attention thus far.
Sincerely,
Joe Hardin
|
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 13 Apr 2012 10:33 AM |
|
RE: my request for clarification with ICC "Section M2105.1 was intended to address traditional water loop heat exchange piping. DX loops were not anticipated when this was put into the code." Direct quote- DX loops were not anticipated (after about 3 decades in existence).... so the DXers paid their money to get AHRI certification ('cause that's how you qualify for tax credits) but have not persued code recognition. The employee of ICC who responded obviously thinks this is new technology. Regarding refrigerant leak detectors and machinery rooms the response was a little more fuzzy....paraphrased; a refrigerant leak detector is required if quantity v CF is identified in excess of the table, but also mentions that there is no such table in the residential code and dwellings covered by the residential code are not governed by the IMC. The trouble with this however is the IMC governs lots of things not covered by the IRC in residential inspections and uses the word residential repeatedly.......so in political doublespeak we have our answer. Yes and No. I sent this follow-up question: Thank you for your responses. One point I wish to clarify. In MI I was trained to refer to the IMC whenever the IRC didn't cover certain things and the IMC uses the term residential and addresses residential occupancy repeatedly. Are you saying that at no time should the IMC be applied to a single family home? No DXers or manufacturers as of yet have felt my inquiries were worthy of response.
|
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 15 Apr 2012 01:20 PM |
|
"Are you saying that at no time should the IMC be applied to a single family home?" To this question a different engineer at the ICC replied: "Joe, This is a complicated subject. We addressed this is great detail in the IRC 2012 commentary for section P2601.1. There is no “yes or no” answer to your question, but the fundamental rule is that the IMC would apply to a single family dwellings of 3 story and less, only when the IRC failed to address a particular subject that is encountered in that dwelling. If the general subject is covered in some manner in the IRC, then it is assumed that the IRC has all of the coverage that it was intended to have." Inspectors are tasked with enforcing "the intent of the code" where clarification is not available. As a mechanical inspector I would suggest that the "intent" of the code in the case of DX is not to cause harm with hydrostatic testing (especially since that particular requirement is in the chapter on hydronic piping). Therefore I could yield to manufacturers' installation instructions on testing the ground loops. I can only speak to areas governed by the ICC. In those areas as a code official I also conclude the following: Since DX technology is scarcely recognized by the code (seemingly accidently by reference to an AHRI table) I would be able to yield to manufacturers' installation instructions as the Code itself once I established ASME, UL or some other testing agency approval on the particular assembly. If one were to dig deep they may find some of the DX products were not approved for use in every application advertised i.e. hydronic heating etc. I would add little to the manufacturers' installation requirements except compliance with machinery room standards where pounds of refrigerant exceed that allowed per cuft of dwelling according to the IMC and temperature/pressure relief valves where hot water is created and isolation valves are installed (which is neglected by every manufacturer to my knowledge water source or DX). The code further requires compliance even if enforcement doesn't. That means that simply because an inspector is ignorant or cavalier to the code, the installer still must comply and can be subject to action even if an inspector approved the installation (particularly if a tragedy occurs). As a code official it is my opinion that inspectors in ICC governed areas could be subject to charges of negligence by not enforcing machinary room rules where indicated (particularly if a tragedy occurs). These are my opinions and interpretations. They were not asserted by any of the respondents of the ICC. Other ICC inspectors may interpret the code differently and their opinion is no more or less valid than mine. So to bring this full circle with my original post, if you are in an area governed by the ICC and you wish to purchase a DX system, is you installer ignorant of the code or indifferent to it? Or have they included a machinary room and refrigerant detector in your estimate or indicate that it is not required based on #refrigerent/cuft? If you don't know, you better ask. If the answer doesn't ring true, you may wanna rethink spending thousands with that individual. Finally I want to re-iterate that if you already have a DX system, I'm not suggesting you are in peril. Most likely leak would be outdoors as the lions share of piping is. Further leaking into the home does not automatically mean danger. Unlike a gas leak, the quantity is finite-therefore folks with gas furnaces have a far greater risk of disaster. So what's my point if as I say I'm not against the technology? The point is DX manufacturers' have not taken care of business. They continue to operate on the fringe of the code and cry foul when they are implied to be a second class technology and risky investment. I encourage the manufacturers' to approach code councils and bring their product from the wild west into the mainstream HVAC technologies. Only then might I again consider offering it to my customers.
|
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|