 Hi,

 Northern Minnesota (Grand Rapids), new CM T27, 5 ton, well loops filled this
winter with food grade glycol (not my 1st choice), just applied power this past
weekend. JW3-FP1 jumper is cut. This has been 'do it yourself' as much as I can.
The entire loop is 8 feet below grade, the basement was at freezing temp,
so the part of the loop entering the house was pretty cold.

 Power on, all leds green, fan slow, 4-5 minutes later the fan speeds up twice, 7
minutes from power on the compressor and flow controller turn on, the heating coil
is warm, after 3 minutes, then lockout.  FP1 Fault code 4.

 Found Technical Bulletin TBJ005 (2007) about bad thermistors.

Since the Technical Bulletin is from 2007, I would think I should be covered.
Should I just replace the thermistor or do the test on it (mentioned in theTSB).
Should I look elsewhere?
 I won't get a chance to work on it for a couple weeks, so would like to get my ducks in a row.

 I havn't taken any measurements as far as flow or temperature.

 The system was filled and purged by supposedly experienced folks (they sell Waterfurnace).
 Can anyone recommend a good place (on the web) to purchase p/t gauges?

 Searching the website I found mention of the bad thermistor and new design, not sure what I have.

 Thanks alot.

joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
12 Mar 2012 08:43 AM
had bad thermistors, bad switches etc. neeed way more info.
pressure gauges are as easy as a basket ball inflation needle and a gauge.
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
12 Mar 2012 09:11 AM


Can anyone recommend a good place (on the web) to purchase p/t gauges?

Geothermal Supply Company



Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
12 Mar 2012 10:02 AM
Posted By geodean on 12 Mar 2012 09:11 AM

Can anyone recommend a good place (on the web) to purchase p/t gauges?
www.flowcenterproducts.com/accessories.php
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
steve_mnUser is Offline
New Member
New Member
Send Private Message
Posts:18

--
13 Mar 2012 05:20 AM
Gauges on the way - may be fixed or will have more info on Monday.
steve_mnUser is Offline
New Member
New Member
Send Private Message
Posts:18

--
19 Mar 2012 12:34 PM
Fixed - there was air in the loop. When they initially filled the loop and purged the air, there was no power to the flow controller (Geo-Pulse - no pressure type, so pressure gauge is useless).
This past Friday, the HVAC guy wired the flow controller direct to 220v and it started pushing water and air in a few minutes, displaced about 1 gallon of water/glycol.
He mentioned that the 5 wells are not in series, but rather in parallel, there is a manifold for in/out under the ground.
How is all the water in each well used then?
How can I be sure each well is used equally, purged of air and that I am getting all the btu's out of the wells I should be?
BTW - 38.3 degrees EWT and 33.3 degrees LWT - matches spec of the furnace.
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
19 Mar 2012 02:21 PM
Glad it is working for you. I'm a little suprised installer did not properly flush system- that is the only way to know all the air is out.
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
ChrisJUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:277

--
19 Mar 2012 02:26 PM
Posted By steve_mn on 19 Mar 2012 12:34 PM
He mentioned that the 5 wells are not in series, but rather in parallel, there is a manifold for in/out under the ground.
How is all the water in each well used then?
How can I be sure each well is used equally, purged of air and that I am getting all the btu's out of the wells I should be?
The manifold sends equal amounts of fluid to each well provided the air has been purged from all wells. Usually the installer uses a high flow purge cart to push all the air out.

EWT of 38*F after only a few days of use, may mean not all wells are purged, maybe not, I am not a pro, just a homeowner w/GSHP, and don't know what kind of load has been put on the HP (cold weather out there?)

ChrisJ RI
steve_mnUser is Offline
New Member
New Member
Send Private Message
Posts:18

--
20 Mar 2012 05:41 AM
Not cold at all, was 60-70 degrees. Northern MN, cold water (normal) - measured temp soon after it began running.
Have left it to run, added 1 gallon of distilled water, will check in a couple weeks when we are back to the house.
Will check temps again as well as get specific gravity to determine % of poly-glycol.
Will also get supply and return air temps.
Anything else I should check?
Thanks
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
21 Mar 2012 12:52 AM
If the water in the flow center canister drops more than 1 inch when the circulation pumps start up, then there is still air in the loop.
www.buffalogeothermalheating.com