Hi,
Northern Minnesota (Grand Rapids), new CM T27, 5 ton, well loops filled this winter with food grade glycol (not my 1st choice), just applied power this past weekend. JW3-FP1 jumper is cut. This has been 'do it yourself' as much as I can. The entire loop is 8 feet below grade, the basement was at freezing temp, so the part of the loop entering the house was pretty cold.
Power on, all leds green, fan slow, 4-5 minutes later the fan speeds up twice, 7 minutes from power on the compressor and flow controller turn on, the heating coil is warm, after 3 minutes, then lockout. FP1 Fault code 4.
Found Technical Bulletin TBJ005 (2007) about bad thermistors.
Since the Technical Bulletin is from 2007, I would think I should be covered. Should I just replace the thermistor or do the test on it (mentioned in theTSB). Should I look elsewhere? I won't get a chance to work on it for a couple weeks, so would like to get my ducks in a row.
I havn't taken any measurements as far as flow or temperature.
The system was filled and purged by supposedly experienced folks (they sell Waterfurnace). Can anyone recommend a good place (on the web) to purchase p/t gauges?
Searching the website I found mention of the bad thermistor and new design, not sure what I have.
Thanks alot.
|
|
|
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 12 Mar 2012 08:43 AM |
|
had bad thermistors, bad switches etc. neeed way more info. pressure gauges are as easy as a basket ball inflation needle and a gauge. |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 12 Mar 2012 09:11 AM |
|
 Can anyone recommend a good place (on the web) to purchase p/t gauges? Geothermal Supply Company |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
geome
 Advanced Member
 Posts:987
 |
| 12 Mar 2012 10:02 AM |
|
Posted By geodean on 12 Mar 2012 09:11 AM
Can anyone recommend a good place (on the web) to purchase p/t gauges?
www.flowcenterproducts.com/accessories.php |
|
| Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon. |
|
|
steve_mn
 New Member
 Posts:18
 |
| 13 Mar 2012 05:20 AM |
|
Gauges on the way - may be fixed or will have more info on Monday. |
|
|
|
|
steve_mn
 New Member
 Posts:18
 |
| 19 Mar 2012 12:34 PM |
|
Fixed - there was air in the loop. When they initially filled the loop and purged the air, there was no power to the flow controller (Geo-Pulse - no pressure type, so pressure gauge is useless). This past Friday, the HVAC guy wired the flow controller direct to 220v and it started pushing water and air in a few minutes, displaced about 1 gallon of water/glycol. He mentioned that the 5 wells are not in series, but rather in parallel, there is a manifold for in/out under the ground. How is all the water in each well used then? How can I be sure each well is used equally, purged of air and that I am getting all the btu's out of the wells I should be? BTW - 38.3 degrees EWT and 33.3 degrees LWT - matches spec of the furnace.
|
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 19 Mar 2012 02:21 PM |
|
Glad it is working for you. I'm a little suprised installer did not properly flush system- that is the only way to know all the air is out. |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
ChrisJ
 Basic Member
 Posts:277
 |
| 19 Mar 2012 02:26 PM |
|
Posted By steve_mn on 19 Mar 2012 12:34 PM He mentioned that the 5 wells are not in series, but rather in parallel, there is a manifold for in/out under the ground. How is all the water in each well used then? How can I be sure each well is used equally, purged of air and that I am getting all the btu's out of the wells I should be?
The manifold sends equal amounts of fluid to each well provided the air has been purged from all wells. Usually the installer uses a high flow purge cart to push all the air out. EWT of 38*F after only a few days of use, may mean not all wells are purged, maybe not, I am not a pro, just a homeowner w/GSHP, and don't know what kind of load has been put on the HP (cold weather out there?) ChrisJ RI |
|
|
|
|
steve_mn
 New Member
 Posts:18
 |
| 20 Mar 2012 05:41 AM |
|
Not cold at all, was 60-70 degrees. Northern MN, cold water (normal) - measured temp soon after it began running. Have left it to run, added 1 gallon of distilled water, will check in a couple weeks when we are back to the house. Will check temps again as well as get specific gravity to determine % of poly-glycol. Will also get supply and return air temps. Anything else I should check? Thanks |
|
|
|
|
docjenser
 Veteran Member
 Posts:1400
 |
| 21 Mar 2012 12:52 AM |
|
If the water in the flow center canister drops more than 1 inch when the circulation pumps start up, then there is still air in the loop. |
|