Posted By jonr on 31 Mar 2012 12:00 PM
A restricted 1000' loop in parallel with a unrestricted 2800' loop
is less pressure drop than just a 2800' loop ...
That's barely true (and highly misleading) for the typical pressures &
flow rates encountered in residential closed loops. A centrifugal circ
pump is a nearly-constant-
pressure device. For example, the output
pressure of a Grundfos UP26-99 falls by only 12% when its flow rate
is doubled from 5 to 10 GPM, and only 25% when tripled to 15 GPM.
Thus, adding circuits in parallel increases total flow without greatly
diminishing the flow in previously existing circuits (providing that
the new circuit isn't a
ridiculous 1' direct short across a 1000' loop).
So, joe.ami is correct that "balancing-by-restriction" has little/no
benefit, unless the loops in question are
grossly mismatched.
Also be aware of the "self-equalizing" tendency of flowing
fluids.
Since dynamic head increases much more rapidly than GPM, the
flow through parallel pipes DOES NOT split in inverse proportion
to their lengths -- and thus, the shorter loop doesn't hog as much
flow as might have been expected, based on their lengths alone.
...the proof of this is left as an exercise for the student,
Looby