CM T27 furnace interlock to Broan A2A heat exchanger
Last Post 01 Jun 2012 09:54 AM by steve_mn. 3 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
steve_mnUser is Offline
New Member
New Member
Send Private Message
Posts:18

--
01 Jun 2012 09:20 AM
Hello,

 The furnace is up and running, no problems.
I have a Broan air to air heat exchanger and would like to include the furnace interlock feature.
Ideally the A2A would run when the blower at the furnace is running and the other inputs to the A2A are met.

I see in the manual there is an interlock to the compressor but I see nothing for the blower.

 Am I off base here? Should I interlock to the compressor or is there another way.

Thanks for you help

Steve

steve_mnUser is Offline
New Member
New Member
Send Private Message
Posts:18

--
01 Jun 2012 09:32 AM
Wondering if I can use G- Fan and C - 24v common at the furnace?
I know the terminals at the A2A unit.
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
01 Jun 2012 09:39 AM
I would do the opposite. Have the thermostat and geo tell the broan when to come on. I don't like to subordinate the heat to the air exchange.
A stat with ventilation control is a good fit (i.e. honeywell IAQ).
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
steve_mnUser is Offline
New Member
New Member
Send Private Message
Posts:18

--
01 Jun 2012 09:54 AM
Just got off the phone w/Broan - they said R and G, looks like I'm good.

thanks