Posted By towpro on 17 Feb 2013 04:50 PM
do I size the electric Aux heater so it can cover 100% of the load if Geo unit goes down?
Since electric resistance heat is 100% efficient, the operating cost per BTU is
independent of the aux unit's capacity -- when the compressor isn't running.
OTOH, when used as a supplemental boost to the heat pump, it would be
desirable to use as little aux heat as possible -- but that's not necessarily
the lower capacity aux heater. For example, my 10 kW (Waterfurnace) aux
heater is actually two 5 kW units, that are controlled independently by the
heat pump's internal electronics (i.e., the thermostat logic is not involved).
When the thermostat calls for an auxiliary boost, the heat pump initially
uses only 5 kW, and doesn't turn on the full 10 kW unless/until the call
for aux heat persists for a while (5 minutes, for my system, I believe).
It's probably not a big difference, but time-sequencing two 5 kW units
may be marginally less expensive than a single higher-capacity element.
I also loved the fact that our aux heater could handle 100% of the load --
because our heat pump installation was completed almost a month before
the well driller finished the loop. So, we burned the last of the fuel oil and
switched over to aux heat for 2-3 weeks -- in the dead of winter.