ClimateMaster water-to-water unit TMW 036. Closed loop. I cut JW3-FP1
wire. It worked beautifully for 18 months, then it tripped out - LED and
alarm: Cycling Code 4. FP1 fault. Check water flows, both ok. I ordered
a new FP1 thermistor, and installed it. Still failing, Cycling Code 4.
Then I took the FP1 sensor off the refrigerant line. I left the gray
wires undisturbed, still plugged in to their socket. It worked
beautifully! While it was running, I checked the temperature where the
sensor for FP1 is supposed to be. The temperature measured + 20 F. What
is the matter, control board failure? Source water in: 43 F; Source
water out: 40 F; Heating water in: 90 F; Heating water out: 93 F; and
the refrigerant pressures are where they are supposed to be! |