I would bet a steak you have a condensate fault but a 14 degree T.D. on the evaporator coil could mean you are low on charge as well. Typically 18 - 22 degrees is acceptable depending on E.A.T. and Humidity. These fluctuate and are sometimes difficult to diagnose as they may not be completely stopped up, just draining slowly. 1 cup of bleach is your fix. If not, you are only out a cup of bleach.
Depending on his airflow, 13F could be within specs if he has a bit too much airflow, especially with 10 degrees in the heat rejection, and the 73F of entering water loop temperature. The only way to check is to determine the capacity or the heat rejection, which commands the knowledge not only what the delta t is, but also the flow.
In any case, the problem is likely solved, given that the last post is almost a year old....